Question about Amana Heating & Cooling
Amana PHD42CO2E1 heatpump and A/C
3 amp fuse on the thermostat control board keeps blowing. Have checked wires to thermostat .didnt find a short.
oscarn
  • 110 Answers
SOURCE: ptac fan keeps blowing
Try setting the fan control to "AUTO" this will cause it to cut out with the compressor.
Posted on Sep 07, 2007
kstfas
  • 75 Answers
SOURCE: Air Conditioner malfunction
Hi, Sounds like you have a short in the control circuit to me. Turn off all power going to the unit. Write down or otherwise mark the wires leaving the control board going to the thermostat. Remove them from the control board. Replace the fuse. Turn power back on and see if the fan still runs. If it does, check and or replace the heat limit switch that brings the fan on during the heat cycle. It may just need adjusted. If the fuse blows, I would think that the control board is probably bad. If it doesn't blow, Remove the thermostat. Leaving all thermostat wires open check them with an Ohm meter. There should be no continuity between them. Twist all the wires together at one end and ohm them again at the other end. You should have complete continuity on all wires. If the wiring checks out, down power the unit. Double check your wire colors and rewire the control board. With all wires open at the thermostat, turn the power back on. Touch the RED wire to the YELLOW wire. The Condensing unit should come on. Touch the RED wire to the GREEN wire. The fan should come on. Touch the RED wire to the WHITE wire. The heat should come on. Down power the unit. Replace the thermostat. Test unit. If the fuse has lasted ok but blows now it is either wired wrong at the Thermostat or the thermostat is bad. I hope I have helped. NOTE: If you can not understand these instructions. Call a licensed Heating / Air conditioning company. kstfas
Posted on Sep 23, 2007
motor1258
  • 6674 Answers
SOURCE: analog thermo.stat control kit
Have you tried removing the RH wire connected to the thermostat and try it ? This might rule out furnace as short in system. If it does the same, put RH- (heat) back on and try removing RC-(cool) , if it doesn't pop the fuse, you may have isolated the problem.?
Posted on Aug 23, 2008
vanni7
  • 163 Answers
SOURCE: 3 amp fuse blows on a carrier 58mcb furnace board
Hi!!! Does your ac unit work fine?If not check your low voltage problem..You have a low voltage problem check the wire going out to your condensor make sure that they are not touching..Good luck..Check low voltage wires..short in progress..
Posted on Jan 04, 2009
  • 127 Answers
SOURCE: Dometic 57915.531 Air Conditioner Blows 3 amp fuse in control box
Steve,
The three amp fuse is installed in the board to protect from shorts or overloads created by disconnecting or reconnecting components when DC power is still connected to the system. If the fuse is blowing, then you more than likely have a short in the 12VDC system between the control unit and the thermostat.
1. Pull the cover off of thermostat and remove the +12 (or +7.5 depending on the model) wire. Access the other end of the wire in the AC compartment. Using an ohmmeter, touch the end of the wire at the AC with one lead and touch the control box with the other (or any ground source). If you get a reading other than OL or Infinity, then that wire is shorted out in the wall somewhere. If not, repeat the steps for the rest of wires except the ground of course. If all of these wires appear to be fine, you may need to take it in for some more extensive troubleshooting.
Hope this helps,
Jeff
Please rate me!!
Posted on Jul 04, 2009
3 amp fuse keeps blowing when heat is on. Took advice of repair person and purchased and installed a Honeywell 5000 Still blowing fuses. Super frustrating We have 4 year old Goodman heatpump a unit Any...
the reversing valve has an electric solenoid, if it is energyzed for heat mode, then try replacing or testing the solenoid coil. the coil may be going out drawing more amps than it should.
Dec 24, 2017 | Honeywell Heating & Cooling
Coleman furnace dgaa077bdta
The control fuses keep blowing tells me one or more of the control that operate the control on 24 volts is malfuctioning. Most controls operate at about 5 watts and on a clamp on amp meter normally pull about 0.2 amp (p = current x voltage, 5 watts = 0.2 amps x 25 volts) I install 75 watt 24 volt transformer with a resettable overload to save on fuses. I reset the transformer and quickly go to the controls and determine the amp draw. When I find the one >0.2 amps I found the problem. The things to check is the emergency heat sequencer, fan control sequencer, reversing valve for heat pumps, main contactor on the condensing unit and any other 24 volt control loads. I have had to replace the themostat wire because the increase current for the thermostat wire can cause the entire length of wire to form a long heater and cause insulation degradationa and cause the thermostat wire to short out and blow the fuses.
Hope this helps
Aug 30, 2014 | Coleman Mobile Modular Home Gas Furnace...
Control transformer keeps shorting out
One or more of the solenoids operated switches is your most probable cause. If you have a clamp on amp meter, measure the amps pulled by each component with a solenoid. The reversing valve solenoid and the main contactor solenoid. Each one of the these components are typically rated at 6watts. If your control voltage is around 25 volts, your amp draw should be about .24 amps max. If your transformer cannot be reset without blowing, install a 3 amp inline fuse so when the overload occurs the only thing that blow is an inexpensive fuse costing about 25 cents instead of a several dollar transformer. If your fuse/transformer immediately blows, try looking for a direct ground in the control wiring. If problems has persisted for a while, you may even have to look into replacing your thermostat wire. The control wire travels over the thermostat wire throught the thermostat and excess amps through the thermostat wire can break down the insulation jacket and short to the common wire causing the control transformer to blow. Another thing to check is the condition of your thermostat wire to check if the insulation is shredding off. Old thermostat wire, especially thermostat wire exposed to sunlight deteriorates quicker. Hope this helps.
Jan 10, 2014 | Rheem 14AJM49A01-RHSLHM4821 4 Ton 14.50...
Amana AMH95 Blown control fuse
Control fuses only blow with a 24 volt problem. Make sure that you replace it with a fuse NO LARGER than 5 amps.You could have a thermostat wire pinched or some wire touching the cabinet inside the unit, but it is a 24 volt problem.
Jan 22, 2013 | Amana GMH950453BX Gas Furnace
1993 Goodman gas furnace keeps blowing fuse when first turned on
You can take each thermostat wire off the control board and use a ohm meter and test to ground, should not have any resistance. Another way is turn off power take each wire off the board, then place one wire at back on the control board terminals ome at a time, untill the one you get to the one that blows the fuse. If the wires check out good sometimes the thermostat itself can have a internal short and cause the fuse to blow.
Nov 27, 2012 | Heating & Cooling
Bryant 650a furnace keeps blowing 3 amp fuse
If you keep blowing the 3 amp fuse it usually means you have a short somewhere in your low voltage control wiring or maybe within the wiring of your control box. I would ecommend using your ohm meter or continuity tester and start tracing each circuit unit you find where it is grounded at. It usually is in the thermostat wire where a rat or just an exposed piece of wire is touching metal somewhere. Just keep in mind that it could be a very small part of a wire touching the metal. Also check your low voltage wiring and make sure you have everything wired correctly if any of that has changed. At least you have a 3 amp fuse to blow instead of something else more costly to repair! Hope this helps.
Feb 28, 2012 | Heating & Cooling
3 amp control power fuse blowing
You have a shorted control wire problem with either the thermostat, wiring to the thermostat and or the wiring to the outdoor unit if used. Disconnect all the thermostat wiring at the unit and thermostat use a meter to check for a short.
Jul 16, 2011 | Goodman CKL36AR36 Air Conditioner
The fuse on the control board keeps blowing and cannot find the problem
CHECK FOR A SHORT SUCH AS A WIRE TOUCHING ANOTHER WIRE OR THE BOARD TOUCHING METAL. MAKE SURE FUSE IS CORRECT AMP. ALSO TURN POWER OFF AT THE OUTDOOR UNIT AND CHECK TO MAKE SURE THERMOSTAT WIRES ARE NOT TOUCHING. IF NONE OF THESE SUGGESTIONS WORK THEN CHANGE YOUR THERMOSTAT. THIS SHOULD SOLVE YOUR PROBLEM.
Apr 13, 2010 | Heating & Cooling
Steve,
Hope this helps,
Jeff
Please rate me!!
Jul 04, 2009 | Dometic 57915531 Air Conditioner
Rf top ac on rv keeps blownig the 3 amp fuse
The 3 amp is 12 Volt protection for the control board. If that fuse is blowing instantly, then you have a short in the 12 Volt system somewhere. More than likely it is somewhere between the Thermostat and the control unit. Check to see if you have 12V at the thermostat. If so, then disconnect the red wire from the thermostat and the red wire at the control unit. At the control unit side, use an Ohmmeter to see if you have continuity with ground. If so, that wire is the culprit. If not, reconnect the red wire and continue to the next wire. Do this until you find the wire that is shorted to ground. Of course, the ground wire will not be checked.
Hope this helps,
Jeff
Jun 29, 2009 | Dometic Rooftop RV Air Conditioner
Heating & Cooling Logo
55 people viewed this question
Top Amana Heating & Cooling Experts
Bill Long
Pete Norton
Are you an Amana Heating and Cooling Expert? Answer questions, earn points and help others