When unit cuts on, gas ignites in chamber and heats for a minute or two, then burner and pilot light shots off, then fan turns on. I have to relight pilot light. This never seems to happen when I have the access door open to watch the pilot and ignition. I have changed the thermocouple and clean around the pilot, blew heavy dust off the fan sensors, and clean the blow. I do not have manual for this unit and I believe it is a 2002 model. It also has a small open ended copper tube that runs from the gas valve to next to pilot assymbly, not sure what it is for?
    Sergeant:
    Champion:
  • 234 Answers
The tube is gas supply for pilot. You have to make sure the thermocouple is in the flame at least half way and make sure its tight in the gas valve. There should be a small silver plug on the gas valve near the pilot supply tube. You can pop the cap and adjust the height of the pilot flame a little. Can you tell if it has a flame rod in or above the flame? If it does You can remove it and clean it with steel wool.
Posted on Nov 26, 2014
22yooper
  • 828 Answers
SOURCE: My gas furnace that came
Try lighting all other gas appliances first. On a new setup air in the lines between the tank and the furnace takes time to bleed out before the gas reaches the pilot light.
Posted on Nov 21, 2008
  • 89 Answers
SOURCE: Intertherm MGH-056ABFC-91 won't kick on. Just
There is probably more than one limit switch. I'll have to get a wiring diagram of this unit. See if you can follow the wires from the wires from the limit switch and see if they go to another limit switch. Also you can put a jumper wire on the red wire and white wire on the unit outside and see if ti comes on.
Posted on Nov 03, 2009
SOURCE: 1990 Triple E mobile home
I've a similar problem and a new thermocouple solved it
J. N. Millet, Alberta
Posted on Jan 14, 2011
Therinnaiguy
  • 1420 Answers
SOURCE: my furnace the burners light
The manual selection on the thermostat bypasses the fan relay. When in Auto, the fan relay turns on the blower. You are probably looking at replacing the circuit board. As far as the three blinks, on the reverse side of the front panel there is a wiring diagram and error code chart. It will give you a starting point where to look for a problem. The three blinks could indicate an open limit because the blower is not operating. Keep the blower on manual and let the furnace run normally until you can figure out what the problem is.
Posted on Feb 23, 2011
  • 571 Answers
SOURCE: intertherm furnace M1BG wont fire
Make sure the gas valve is turned to the ON position after you had it in PILOT position. Also check the thermostat low voltage wiring @ furnace...jumper the Red & White wires to bypass the thermostat temporarily. Make sure there is 24 volts on you low voltage circuit.
Posted on Dec 16, 2013
Pilot light lit but not igniting to heat water
pilot lit on gas furnace, but the burners won't light (Home ...
answers.angieslist.com > Home > HVAC
Oct 26, 2013 - i have a gas furnace with a lit pilot, but the burners won't light. ... if the thermocouple does not sense the heat of the pilot it prevents the gas controller fromturning on the burners. ... clamped onto the outgoing hot water pipe, if huydronic system) that is telling the furnace it is too hot, whether or not that is true.
Nov 18, 2015 | Water Water Heaters
When I try to use my Thermolaire model SU402E, the pilot lights( and stays lit), but the main burner will NOT ignite.. any suggestions as to what could cause this if the pilot stays lit?
Bad igniter? When you 1st try it the gas valve will give enough gas that you would get the burner lit if the igniter was glowing red. If you're desperate you can light the igniter area w/ an aim n flame, but you definitely want to do that w/ caution and crank up your t-stat so the furnace stays on awhile Cuz you'll have to do it again for heat or buy an igniter($40 or so)
Jan 14, 2015 | Heating & Cooling
Why is gas furnace in igntion lockout due to recycles (8 blinks). likely causes?
Check the thermocouple (heat sensor) on the pilot light...it tells the control unit that there is a lit flame...otherwise, the control unit won't let the gas valve open...does the pilot light stay lit after you've held the button down 30 seconds?...
Jan 01, 2015 | Dryers
Lennox furnace model G11Q3-110 v.2 burners light but go out before fan comes on
Troubleshoot an ignition problem on a Lennox gas furnace ...
? 2:44
https://www.youtube.com/watch?v=yXIxgzwMkPs
Nov 17, 2012 - Uploaded by grayfurnaceman
This furnace should light its pilot with a spark then the pilot proves its on ... Troubleshoot an ignition problem on a Lennox gasfurnace .... Pilot and no inducer but is the same model as that great video! ... You probably have dirty burners. ... How do you know spark module is not sending 24 volts to mv and pv ...
Lennox Furnace Model G11Q3-82-2 - RepairClinic.com
Nov 19, 2012 | Heating & Cooling
Janitrol GUPS075-3 Furnace burners will not stay lit
The first thing I would do is make sure the flame sensor is clean, this is a metal rod immersed in the burner flame on the opposite side of the igniter. If too much oxidation builds up on it, it will not allow the burner to stay lit. To clean, just turn off furnace and remove flame sensor and clean with steel wool and then reinstall. If this does not solve the problem there may be a problem with the gas valve.
Nov 08, 2012 | Heating & Cooling
Reliance 606 natural gas water heater - model #640YORT - water does not stay hot. pilot has to be clicked to heat and then u can use hot water til tank empty and it will not continue to heat water.
If I understand correctly, the pilot light is not staying lit.
You light the pilot and water in the tank reaches temperature.
Once hot water is gone, then pilot light has to be lit again.
Gas pressure is good, and gas is flowing.
Thermostat is working at high end because it cuts off heating.
Vent is working because tank heats up.
Air intake is working.
Gas control thermostat might not be reading low temperature. Replace gas control valve.
Pilot tube might be dirty. Clean burner parts and combustion chamber, and air intake, and vent.
Backdraft might be blowing out pilot. Check for constant updraft by running water heater 5 minutes, and then light match under vent hood and see if smoke goes up.
Very hot air can put out pilot, especially when water heater located in attic. Add ventilation.
Improper vent might have water dripping back down into combustion chamber and putting out pilot light and rusting out the parts. Inspect for rusted parts and water.
http://waterheatertimer.org/How-to-install-gas-water-heater.html#troubleshoot
http://waterheatertimer.org/pdf/Pilot-light-will-not-stay-lit.pdf
Aug 09, 2011 | Reliance Natural Gas Water Heater Control
Williams 3003622 Wall Mounted 30,000 BTU The pilot light goes out when the main flame shuts down. The pilot light will stay lit for days when heat is not called for but when heat is called for the furnace...
I'm having the same exact problem... At first we thought was the vent... but the way the flames goes out... it seems that there is "not enough oxygen" more than "blown out by the wind"... right after both main & pilot goes out, I can't even light any external flame inside the chamber... and it doesn't feel like the outside cold air coming in... it just feel like there is some sort of gas in the chamber that's so strong, it prevents flame... and the only thing I can think of is that it doesn't have enough oxygen, but too much natural gas, and flame can't sustain.
Nov 02, 2010 | Williams 3003622 Ceramic Wall Mounted...
Furnace runs about 1 minute, then total shutdown
What type of gas supply line do you have? Is it black pipe or copper? If it is copper, there can be a film like substance that builds up on the inside of the copper. The debris will the get caught in a pre screen where the supply enters the valve thus cutting the supply of gas to the unit. Also, the thermocouple may be bad. You didn't say that you replaced it. Try replacing it as well. Also, you could have a limit switch turning the system off and thus cutting the gas off completely but it is highly unusual for the pilot to be cut off as well unless the pilot is being blown out when the gas is shut off. Also, turn the unit to fan only without calling for heat. Using a flame of some sort, put it into each baffle of the heat exchanger. If your flame is being blown around in one of the baffles, then you have a hole in the heat exchanger and what is happening is that the roll out switch is cutting the unit off and the air still moving through the heat exchanger is blowing the pilot out. I have seen this actually happen. If your furnace is in excess of 15 years old, it does need to be checked for possible holes. If it is in excess of 25 years old, it is a huge possibility that the unit has already developed a hole. If you feel hair coming out of one of the baffles, then shut the unit down immediately and have it replaced!
Apr 05, 2009 | Heating & Cooling
Lighting the pilot light
The steps involved can vary slightly depending on your furnace model and pilot valve type, so if possible try and find the instructions inside the furnace door cover or in the instruction manual. This is for a gas fired furnace, but applies to any gas-fueled appliance including water heater. Two of the most common types of pilot valve body assemblies either have a red reset button and a gas valve or no reset button and a valve knob that can be depressed. But whichever type you've got, if you have an older model furnace with a standing pilot (flame is lit all the time) then this is the basic procedure.
  • Turn you thermostat to 80 degrees or to a setting that will demand heat. Make sure the thermostat is in "Heat" mode.
  • Go to the furnace and find the pilot valve. The pilot valve body is a box shaped device into which the main gas line will run and is located near the gas burners. It will usually have a gas **** or valve knob that reads "On, "Pilot" and "Off." Locate this gas **** or knob.
  • Turn the knob or gas **** to the "Off" position and wait about 3 minutes for any residual gas to clear away.
  • Find the pilot. It's located near the gas burner tube assembly in the furnace.
  • Get your match or lighter ready. Sometimes the pilot is hard to reach. If possible, try and use a long fireplace match when you light it. If you don't have a fireplace match then a butane BBQ grill lighter works well too. If you don't have that, then you can fasten a match to the end of a stick when you light the pilot
  • If you have a pilot with a red Reset button, turn the gas valve from "Off," to "Pilot."
  • If you have a pilot with no red button, turn the knob from "Off" to "Pilot."
  • Place the lit match or ignited lighter tip at the pilot and depress and hold the button or depress the knob as appropriate. Depress the button or knob for about 30 seconds. This maintains gas flow to the pilot until the thermocouple gets hot enough to open the main gas valve.
  • Once the pilot stays lit, slowly release the button or knob and turn the gas **** or knob from the "Pilot" position to the "On" position. This will ignite the burners and keep the flow of gas supplied as required for the burners as called for by the thermostat.
  • If the burners fail to ignite then it may be because the thermocouple did not get hot enough to open the gas valve. Wait a few minutes and then repeat the above procedure. This time hold the red reset button or depress the knob for about 45-60 seconds.
  • Once the main furnace burners ignite, adjust the thermostat to the desired setting.
  • If you've followed the previous steps on lighting the pilot and it still does not light after, or will not stay lit, then you probably have a problem with the thermocouple or an adjustment needs to be made to the pilot. You'll need a furnace service technician to replace or repair these parts. You may find that the pilot lights, but it is an anemic looking flame. That's a different problem we'll look at in the next section.
  • If the pilot lights but the flame is a weak yellow flame, it will not get hot enough to heat the thermocouple to its set point allowing the gas valve to open.
    A natural gas flame should be a bright blue with the tip of the flame having just a tinge of yellow. A propane flame should have a bluish green flame with a tinge of yellow at the tip. The flame should be strong enough to hit the thermocouple tip about 1/2 inch from the tip end. If the flame is weak or shaky looking, check to see that a breeze or draft is not blowing on it. Adjusting the Flame
    There is usually a small screw on the pilot valve body that will adjust the flame. You may have to refer to the manufacturer's instructions to find the screw. Turn the screw as needed to adjust the flame throw. Yellow Flame
    A yellow flame is caused by lack of air and incomplete combustion. It can be caused by a dirty pilot tube tip. Split Flame
    This is caused by dirt in the pilot tube. Take a needle or small nail and gently clean the tube. Flickering or Wavering Flame
    A flame that flickers is usually caused by a draft.
Thanks for using FixYa - a FixYa rating is appreciated!!
Feb 18, 2009 | Water Heaters
Rheem gas furnace pilot lights, but no burners or fan
If the burners do not fully ignite, the sensor will shut the furnace down. The lack of sufficient burner flame is a gas valve or gas pressure problem within the valve.
Replacing the gas valve with the original one may get you going. I surely suggest a professional service company for safety reasons and a thorough inspection. A 20 year old furnace is past it's normal life span.