American standard furnace aux100R
Only two burners light the the gas valve shuts off
machtcl1
  • 61 Answers
SOURCE: how to light a American Standard furnace
If it is an old furnace with a manual pilot light there are pilot lighting instructions usually on a door or panel. If it is 15 years old or newer it probably has either a spark ignition or a hot surface ignitor. These can't be lit manually. If they fail they usually require parts to be repaired.
Posted on Jan 02, 2009
  • 1214 Answers
SOURCE: American Standard Gas furnace acting weird
I am concerned of the readings you have given. 120 volts to ground, but 168 volts to neutral? And having 10 amps of current at the "ventor", but only 1 amp for the whole furnace worries me, because power for the "ventor" comes through the furnace.
You should not have 168 volts to anything! Unless somehow 240 volts is feeding the system, and there is a medium resistance short somewhere.
The controller boards are sensitive to AC polarity (if you will). Neutral should be tied to neutral on the board. You can check that by testing for voltage between the neutral terminal and chassis ground (assuming the chassis is properly grounded.). The hot leg of incoming power, which should be 120 volts, should be connected to the terminal that says 120 VAC.
If your getting 168 volts AC somehow, then something is wrong, and you need to disconnect power from this unit until you find the cause.
As a heat-A/C tech, you should know the sequence of operation for all furnaces is pretty much the same. The boards, while manufactured by different manufacturers, all operate pretty much the same way.
Let me know your findings in reply and I will attempt to help you more.
Posted on Jan 20, 2009
james3751
  • 614 Answers
SOURCE: All burners will not light on Goodman furnace
I have had problems like this before. Most of the time it is the connection between the burners. There are small slots that the gas runs thru to lite. Clean those with a brush and then try it. Rus
Posted on Oct 04, 2009
  • 1015 Answers
SOURCE: gas furnace, main burner ignites the other 2 don't. then shutdn.
Between the burners is a small rail in the pressed steel where the flame runs across to light the other burners and it sounds like there is dirt or debris in the step over rails causing the problem. You will need to use some compressed air on those rails to clear them out. Once the rails are clear the other two burners should ignite right away.
Posted on Dec 21, 2009
Testimonial: "I did not expect such a quick response. These are hard times for us and we really appreciate your help. Thankyou for sharing your expertise."
SOURCE: I have american standard freedom
The igniter must have failed. replace the igniter.
Posted on Dec 20, 2010
My furnace won't light. American standard. About 13 years old. No pilot. I shut gas off for five minutes. Still blowing cold air. Any suggestions
The most common issue would be the gas valve has failed or the transformer is defective, I strongly suggest you call a professional service business as this can be a fire/explosion hazard.
Dec 07, 2016 | Heating & Cooling
Old anthes gas furnace with pilot light. burners will not light.blows cold air
Have to think that the thermocouple has failed if the pilot is on but the furnace main burner doesn't ignite
Apr 05, 2014 | Cozy (W352E) Heater
Ducane furnace gas burner runs one minute shuts down
If this has an Hsi Ignition its time to have a tech check it out and replace
Feb 13, 2013 | Honeywell Furnace Gas Valve Sv9501h2409
I've got a 23 yr old 30DV3 whose pilot light works, and the thermostat & heating element seem to work, but not well. With the thermostat set at full hot, it just barely throws out any heat at all. ...
As I'm sure you already know, Empire Comforts Systems, no longer makes that model heater and hasn't for some years, now. I mentioned that, because if your unit needs parts, they may be almost impossible to get. In any event, there are a several things that may be causing the problem.
  • Low Gas Pressure - Burner is not receiving enough gas. Check for obstructions and have gas pressure at the unit checked.
  • Clogged burner or air intake (venturi valve) is partially clogged. Clean burner ports and venturi valve.
  • Gas line Shut Off Valve at heater not fully open. Check Gas line Shut Off Valve.
At 23 years old, you've gotten your money's worth out of this unit and it may be time to replace it. Empire makes several Direct Vent Wall Furnaces that are rated as High Efficiency Furnaces. In the long run, the money saved in fuel cost, would be worth installing a new one.
Hope this helps you solve the problem.
Apr 11, 2011 | Empire Direct Vent Wall Furnace;...
I changed the furnace filter on my american Standard Freedom 80 filter and now my burner won't light.
does anything happen, i door that you removed might have a kill switch on it so if the door comes off or is not installed right the furnace wont light, let me know and maybe i can help. wally
Mar 10, 2011 | American Standard Heating & Cooling
Heating problems: i have an american standard freedom 78 natural gas furnace. The exhaust fan comes on, the ingiter lights up then the main fan comes on but not the burners. I have cleaned the flame...
sounds like you have a good feel for what your doing. do you have a volt meter? if so look for 24 volt at the gas valve just before the glow bar starts to cool down each time. if 24 volt shows then look first for blocked orifices into the burner and next replace the valve. no power to the valve look to the control board
Feb 05, 2011 | General Heating & Cooling
Pilot will not light
Unable to light pilot Gas supply turned off Turn on gas supply Gas **** knob dial not positioned correctly Check lighting instructions. Set control knob Defective thermocouple Check and replace thermocouple Defective safety magnet assembly Check and replace gas valve Pilot burner orifice clogged Clean or replace Pilot tube pinched or clogged Clean, repair or replace Poor thermocouple connection Check and tighten Air in gas line Purge air from gas line Thermostat's single use ECO is tripped Check ECO and replace gas valve Gas valve defective Check gas valve
Jun 06, 2010 | American Standard AMERICAN STD 100G NGAS...
FURNACE COMES ON AND SHUTS DOWN WITHIN 15 SECONDS
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control). When all else fails, check the ground connection for corrosion.
Nov 23, 2009 | Heating & Cooling
Rheem gas furnace pilot lights, but no burners or fan
If the burners do not fully ignite, the sensor will shut the furnace down. The lack of sufficient burner flame is a gas valve or gas pressure problem within the valve.
Replacing the gas valve with the original one may get you going. I surely suggest a professional service company for safety reasons and a thorough inspection. A 20 year old furnace is past it's normal life span.
Jan 06, 2009 | Heating & Cooling
Heating & Cooling Logo
Top Heating & Cooling Experts
paulcarew
Dan Webster
Dan Webster
Donni Steen