Question about LG Heating & Cooling
LG SPLIT SYSTEM AIR CONDITIONER INDOOR UNIT WILL NOT POWER UP
LS-D2462HS AIR CONDITIONER, OUTDOOR UNIT HAS POWER TO IT BUT INDOOR UNIT WILL NOT POWER UP. HAS APPROXIMATELY 50V DC TO RED AND BLACK TERMINALS FROM OUTDOOR UNIT TO INDOOR UNIT BUT NOTHING ON WHITE WIRE.
    New Friend:
    Cheetah:
    An expert who has answered 20 or more questions within one hour.
  • 40 Answers
As described the voltage you are seeing is fake. if there is no led lighting in the indoor unit check the small transformer in the indoor unit you should get 12V DC or 24V DC out from it
Posted on Feb 10, 2014
Therinnaiguy
  • 1420 Answers
SOURCE: Air Conditioner unit won't switch on outdoors
can you give us some model numbers and a make? Get both the inside and outdoor unit numbers please. Thanks.
Posted on Oct 10, 2007
  • 182 Answers
SOURCE: Fujitsu Split System AST24RGA-W + AOT24RZAL
with the remote.....turn the fan only on.if the fan does not run its either the board or wiring.
Posted on Aug 23, 2008
SOURCE: ac split unit indoor an ouydoor unit electrical wiring diagram
machine off
Posted on Apr 25, 2009
greenspan
  • 1734 Answers
SOURCE: LG split (3 indoor) LMU360CE
The LED #2 is only flashing while in disconnection or short in Thermistor (3 sec off / 0.5 sec on). If you want to change it, note: this is not an easy job to do! You will need to remove the top panel, then remove the control paneland then the front panel to gain access to the thermistor. The part isnot available to the public and requires an authorized service techfrom LG to take care of this problem. You will need a special tool toremove the front door seal spring clamp.
But you can call customer service @ 800 243 000 and see if theycan transfer you over to parts. Just give them the model and serial #and see if they would be willing to sell you the thermistor part. Youwill also need the door seal spring clamp removal tool to make the jobeasier.
Posted on Aug 02, 2009
SOURCE: Wiring diagram for Ramsond 18000 BTU Ductless
See link below for detailed wiring. I found it very helpful
http://www.ramsond.com/minisplit/wiring/detailedwire5170.pdf
Posted on Oct 02, 2009
Won't power on!
You may need an electrician or tech to look at this as you will probably need special tools. If you have a multimeter, check the interconnect cable - the cable that connects the indoor to the outdoor and allows it to communicate. Check that they are connected correctly and to the right terminals. Check the voltages - supply and signal. Set your meter to DC Volts, test between terminals 2 and 3, of the outdoor unit and wiring terminals. You
should see 0-65 V dc, it will be fluctuating.
If the Voltage is not present disconnect the inter unit wiring, test the Voltage on the wiring terminals again, If
No Voltage is present, the outdoor PCB must be faulty.
May 05, 2015 | LG Heating & Cooling
My LG mini split want cut off. I can cut it off on the unit but it still runs wide open it will not cut off by the remote either. any help appreciated.
This sounds like a faulty thermostat (indoor unit), or a welded (shut) set of contacts in the condensing unit (outdoor unit)
Aug 09, 2011 | LG LS-K2430HL Heat Cool Mini Split Air...
The supply is 220v going to pcb. indoor .the outdoor unit was not working due the power supply..was 110v,, prom the pcb indoor..
I assume you are in Australia? There should be a 240v feed to the indoor unit. Once the indoor unit has been switch on , there shouldbe a 240 v supply to the outdoor unit. The communications wire will fluctuate what voltage is supplied to the outdoor. Unless you are a licenced electrician, I would not suggest you attempt to check these figures as the risk of electrocution is very high. No power to the outdoor unit can be as simple as a failed air / pipe sensor on the indoor unit , or the indoor board itself is faulty. Call up an LG Agent in your area for service and to protect your welfare..
Jul 03, 2011 | LG LS-L1210CL Mini Split Air Conditioner
What happens when i use a one horsepower for the indoor and a 1.5horsepower for the outdoor of my split unit..cos i'm presently in this situation after my 1.5hp indoor unit got spolit i had to use 1hp...
maybe if you combined this unit the problem may be occuring is possible icing of your indoor unit but it can contol your thermostat but try to see what happen i think it will work.
Mar 18, 2011 | LG LS-L1210CL Mini Split Air Conditioner
I have an LG split system air conditioner model number LSZ244VN-4 it is coming up with a fault code of CS after it has been running for approx 5 minutes
There is no CS code. Please read as C5.
Fault Code 05 and 53 (CH05 is displayed at indoor unit, 53 is displayed at outdoor unit)
This fault code indicates a communication error between the indoor and outdoor units; this is usually caused
by wiring errors or condensate pumps connected to the inter-connecting cable.
The communication between the units is a fluctuating DC voltage commonly called a serial signal, it can be
easily lost if the wiring is not done correctly. If there is a communication error fault CH05 will appear within 5
mins of powering up the system.
Testing
• Check Outdoor and Indoor Power Supply Voltages ( 230V ±10% ) and correct as necessary.
• Check for any mis-wiring or loose connections and correct as required.
• Check the resistance between communication line and GND. (Normal: Over 2M).
• If one Indoor unit operates normally Outdoor PCB is generally normal.
Turn on the power and start the indoor unit in cooling, set the temperature to 18ºC; the serial communication
signal will only be present for the first 3 mins of operation.
Set your meter to DC Volts, Test between terminals 5 (Red probe) and 2 or Earth (Black probe) of the outdoor
unit, you should see a fluctuating 0-72 Vdc.
If the Voltage is not present disconnect the terminal 5 cable, test the Voltage between this wire (Red probe)
and 2 or Earth (Black probe), you should see a steady voltage in the range of -0.1 to -10.0 Vdc. If No Voltage
is present either the cable or Indoor PCB must be faulty. This can be determined by checking the voltage
output on the Comms terminal of the Indoor unit, with the Comms wire disconnected. If No Voltage is present
the Indoor PCB must be faulty, if present, cable must be at fault.
Jan 19, 2011 | Heating & Cooling
I have a LG Inverter Art cool and after about 5 minutes it stops and C5 shows on the panel Kerrie
Fault Code 05.
Testing
the Indoor PCB must be faulty, if present, cable must be at fault. Helpful?
Jan 19, 2011 | LG Art Cool LA121CNP wall/window Air...
Eee code displayed
To work out what the error code is press the orange start/stop button on the remote controller so unit operation is stopped.
Then press and hold "energy save" and "zone control" button simultaneously for at least five seconds, the error code will be along the lines of En:nn where the "En:" is the error code and the ":nn" indicates the indopor unit address if there are multiple indoor units connected to the one controller. If the upper vertical bar on the capital E is missing so it looks maybe like a 2 or something don't worry for some reasons they just do that
Some common error codes are:
E0 Communication error between indoor unit and wired remote control, check if there is 12VDC between terminal 1 + 3 at remote control and 8-9VDC pulsating between terminal 2 + 3. If DC volts out of Indoor pcb is below about 11.6VDC it will cause this error, the problem is normally dry capacitors in the 12 VDC power supply section. This model has two power supply sections on indoor pcb.
E1 Communication error between indoor unit and outdoor unit,
EF Discharge temperature abnormal
Dec 25, 2010 | Fujitsu 36CS Air Conditioner
U4 System transmission between indoor and outdoor units Daikin
Sounds like an interconnecting wiring error. Check wiring connection i.e. wires are connected in right order 1 to1 2 to 2 etc. from indoor terminal board to outdoor terminal board. Also check for slack or loose connections.
Hope this helps I take the time to answer your question so please rate me
May 28, 2010 | Cfm Daikin R410a Split System Air...
Heating & Cooling Logo
154 people viewed this question
Top LG Heating & Cooling Experts
Tim Whalen
Dan Webster
Dan Webster
Are you a LG Heating and Cooling Expert? Answer questions, earn points and help others