Outdoor unit does not start. indoor unit fan does run.
Fujitsu split system compressor does not switch on. the indoor unit fan is running and the green light is flashing.the outdoor unit PCB does have 240vac going to it and the fuse is not blown. The red LED on the PCB is not on. Can anyone help ?thank you
  • 1 more comment
  • andrefourie May 31, 2009
    Thanks . is the relay on the main PCB. there are 4 pcb's in this machine. a large pcb with your l c filter networks, your main PCB and 2 smaller pcb's with your inverter electronics ?the main PCB does have 240vac comming into it. should it have a dc voltage commin into it ?
  • hfdgjdfg Sep 10, 2013
    add comment
  • mike ison
    mike ison Dec 28, 2013
    thank you it worked
    Problem Solver:
  • 10 Answers
By the sound of it the relay in the outdoor section is bad
Posted on May 31, 2009
3 split units run from one compressor one is not cooling
If there is 3 indoor units from one condensing unit
(6 pipes at outdoor unit) this is classed as a multi unit
All units will run correctly as long as they all require same mode, cooling or heating, if one unit decides to heat it will shut down until master unit decides to heat then it will start, for each unit to individually heat and cool there would have to be 3 pipes to each indoor,
Dec 19, 2015 | Fujitsu 9RLS 9000 BTU Split System Air...
Indoor fan slow to rotate in heat mode and no heat/compressor
The indoor fan will not run at normal fan speed untill the indoor coil reaches 32oC. This is done so that a cold draught is not felt when outdoor unit is not running. Check to make sure the outdoor unit is operating. If the outdoor fan is running but there is no indoor fan after 5 mins then you must likely have a gas issue or a fault compressor circuit.
May 31, 2010 | Fujitsu 24R1 Air Conditioner
Indoor unit freezing up
THE OUTDOOR UNIT HAS A CONTACTOR WITH THE CONTACTS WELDED TOGETHER THE CONTACTOR CONNECTS TO THE COMPRESSOR AS IT TYPICALLY PULLS A SURGE OF 20 -30 AMPS OR MORE..WITH THE INDOOR UNIT IN FAN ONLY THE COMPRESSOR SHOULD NOT BE RUNNING. THE CONTROL WIRES GOING TO THE UNIT HAVE 24 VOLTS TO THE CONTACTOR TO PULL IN THE CONTACTS TO SUPPLY 220 TO COMPRESSOR.
Mar 09, 2010 | Heating & Cooling
Fujitsu mini split outdoor unit not running, but indoor unit is running after turnning on
Check the disconnect switch and make sure that both the fuses are good and not shot. If one is shot then the system wont work. There are two fuse. Also be careful due to you will be working around 210 volts
Jun 01, 2009 | Fujitsu Heating & Cooling
Does not heat - compressor switches on/off repeatedly
check outdoor fan if running. the outdoor coil will freeze up on heat cycle. or outdoor board if there is one is defective.it could be reversing valve as well
May 18, 2009 | Heating & Cooling
Split unit, I get heat but no cold
I have run into this with the LG brand systems. try shutting power off to the outdoor unit to reset all units. If problem persists, it could have to do with a charge level of refrigerant (freon) or possibly a failed control board.
May 16, 2009 | Fujitsu 24R1 Air Conditioner
Will Not Heat
On the outdoor unit the fan should not be running, on the indoor unit the fan should be running. If you then check the outdoor unit with fan not running, you should be able to hear clearly that the compressor is actually working. If this is all correct, it is possible that your fourway reverse valve is seeping and needs to be replaced.
Apr 15, 2009 | Fujitsu 18R1 Air Conditioner
Fujitsu Split System AST24RGA-W + AOT24RZAL
with the remote.....turn the fan only on.if the fan does not run its either the board or wiring.
Aug 23, 2008 | Heating & Cooling
Mitshubishi split muh-18nvand inside msh-18nv
-Start the unit.
-Press EMERGENCY OPERATION switch.3-minute time delay works.Test run operation operates for 30 minutes.
-Check voltage to terminal block of outdoor unit.Is there 12V DC between 2-1?
-If voltage is presenet check the wiring, compressor contactor outdoor fan motor and compressor.
-If no voltage check voltage to terminal block of indoor unit.Is there 12V DC between 2-1?
-If if voltage is present re-connect the continuity of indoor and outdoor unit connection.
-If no voltage replace the indoor electronic control P.C.
board.
-But also check the coil thermistor sensor and room air thermistor if this two is out of range it can cause the tripping of out door unit. It has the resistance of 8 to 10 k ohms at 25 deg c temp.
Jan 04, 2008 | Heating & Cooling