Question about Xantrex Technology Xantrex LinkLITE Battery Monitor
With all DC systems on no negative Ah readings
I have connected the xantrex XBM system with 500 A/50mV current shunt according to installation guide. Neg side contains wire only going to battery side of shunt. All displays read according to Functional overview and General operations Guide. Fully charged battery bank system show 100%. I have 4 deep cycle 240 Ah batteries connected in series/parallel. F01 isset to 480 Ah. However, when I turn all DC systems on in the boat (Refrigerator, lights, electronics ) I don't get any current flow showing.
    President:
  • 1,714 Answers
The shunt needs two (2) wires coming from it to your amp meter. If the meter reads backwards polarity, reverse the shunt leads.
Posted on Jul 02, 2009
My gilera seems to have voltage drop and cause my engine to cut off when i press my brake.
Hi, Herman the following is a comprehensive charging system test that is guaranteed to the find issue with your system.
1. Battery Test: The battery needs to be a fully charged and load tested to ensure proper readings, connections need to be clean and tight. If you are not working with a fully charged and functional battery, all other voltage tests will be incorrect. Standing battery Voltage should be 12.5-13.2 DCV.
2. Charging System Voltage Test: Start motorcycle, measure DC volts across the battery terminals you should have a reading of approximately 13.2-15 DC Volts.
3. Check Connections/Wires: Inspect the regulator/stator plug, and check the battery terminals for connection/corrosion. If everything seems to be in order, move on to number 4 below to determine if there's a failed component.
4. Stator Checks/Rotor Check: Each of the following tests isolates the Stator & Rotor. If AC Output test Fails and Resistance Check, and Stator IB Test Pass then Rotor is at fault (Pull Primary covers and inspect rotor for damage).
5. AC Output Check:
Unplug the regulator plug from the stator
Start motorcycle and change Voltmeter to AC volts.
Probe both stator wires with your meter lead.
The motorcycle should be putting out approximately 18-20 ACV per 1,000 rpm. Reading will vary depending on system, check service manual specification
Generic Specs:
22 amp system produces about 19-26 VAC per 1,000 rpm
32 amp system produces about 16-20 VAC per 1,000 rpm
45 amp system produces about 19-26 VAC per 1,000 rpm
Stator Resistance Check:
Switch your multimeter to Ohm x 1 scale.
Probe each stator wires with meter leads and check resistance on the meter.
Resistance should be in the range of 0.1-0.5 Ohms. Reading will vary depending on system, check service manual for specification
Generic Specs:
22 amp system produces about 0.2 to 0.4 ohms
32 amp system produces about 0.1 to 0.2 ohms
45 amp system produces about 0.1 to 0.2 ohms
Stator IB test or Ground Check:
Probe each stator wire with your positive lead on the multimeter and the negative to ground.
There should be no continuity to ground on either wire.
If there is continuity to ground your stator is shorted to ground.
5. Regulator Test: Each of the following tests isolates the regulator only, so if any of these tests fail, the regulator is at fault.
Identifying Wires:
Battery Charge Lead- Wire going from regulator to battery positive.
AC output leads- Wires coming from the Stator to the regulator.
Ground- Wire from Regulator to ground or regulator may be grounded via the physical bolting to chassis.
Regulator Ground Test: Ensure the regulator body is grounded or grounding wire is fastened tightly to a good ground (you should verify this by checking continuity from regulator body to chassis ground).
Fwd/Reverse Bias Test/Diode Test: This check is testing the Diode function to ensure it is regulating the AC current for the stator into DC Current.
Switch multimeter to Diode Scale.
Place your Multimeter positive lead on each AC output wire.
Place your multimeter negative lead on the battery Charge wire.
The meter should read voltage typically around .5 volts.
Next, switch your multimeter leads putting the negative lead on the AC output wires and the Positive lead on the Battery Charge Wire.
The reading should be Infinite.
With your meter on the same setting, place your multimeter positive lead on the regulator ground wire or to the regulator directly, and then place your meter negative lead on the AC output leads.
Next, switch your multimeter leads putting the negative lead on the regulator ground and the Positive lead on the AC output wires.
Note: Below is a table to show the readings:
Positive Lead Negative Lead Reading
AC output 1 Battery charge lead Voltage
AC output 2 Battery Charge Lead Voltage
Battery charge lead AC output 1 ?
Battery charge lead AC output 2 ?
Ground AC output 1 Voltage
Ground AC output 2 Voltage
AC output 1 Ground ?
AC output 2 Ground ?
For more information about your issue and valuable "FREE" downloads that you will need please click on the blue links below. Good luck and have a wonderful day.
http://www.jetav8r.com/Vision/Stator/fault_finding_by_www.electrosport.com.pdf
Feb 21, 2017 | Gilera Motorcycles
2005 vl 1500 charging system system not charging checked generator 3 wires giving pluss 80v at 5000rpm instaled new rectifier voltage across battery under 13 volts could faulty battery be problem
Hi, Anonymous the following is a comprehensive charging system test that I found on a Rider Groups website
1. Battery Test: The battery needs to be a fully charged battery that has been load tested to ensure proper readings. If you are not working with a fully charged and functional battery, all other voltage tests will be incorrect. Most places like Auto Zone, Advance Auto, and Pep Boys will charge and test motorcycle batteries for free. Standing battery Voltage should be 12.5-13.2 DCV.
2. Charging System Voltage Test: Start motorcycle, Measure DC Volts across the battery terminals (you should have a reading of approximately 13.2-15 DC Volts).
4. Stator Checks/Rotor Check: Each of the following tests isolate the stator & Rotor, If AC Output test Fails and Resistance Check, and Stator IB Test Pass then Rotor is at fault (Pull Primary covers and inspect rotor for damage).
AC Output Check:
Probe both stator wires with your meter leads.
The motorcycle should be putting out approximately 18-20 ACV per 1,000 rpm. (Reading will vary depending on system, check service manual specification)
Generic Specs:
Resistance should be in the range of 0.1-0.5 Ohms. (Reading will vary depending on system, check service manual for specification)
Generic Specs:
Identifying Wires:
For more information about your issue and valuable "FREE" downloads that you will need please click on the links below. Good luck and have a nice day.
http://www.crowitis.com/images/VL1500_Charging_System_Wiring_Upgrades.pdf
stator output voltage
Suzuki VL1500 Service Manual
OEM parts for Suzuki
Suzuki VZ1500 Owner Manual
Jan 16, 2017 | Motorcycles
I need to know the POLARITY of the AC adaptor to provide the correct setting using a universal adapter.
there is no polarity in ac current as ac means alternating current and that means alternating between positive to negative back to positive back to negative and so on
only dc ( direct current ) and the center pin of the plug is designated as the positive pole has polarity, the outer case being the negative
OR Are you asking the voltage of the ac adapter and the voltage of the dc output side of the adapter
Nov 26, 2015 | Office Equipment & Supplies
2005 Toyota RAV4 Is the electrical system 12V/24V DC Negative Ground system?
Your vehicle, like nearly all modern cars and trucks for consumers - should have a standard, 12 Volt Negative Ground electrical system.
Apr 10, 2015 | 2005 Toyota RAV4
2000 Yamaha V-Max charging system
Hi, Anonymous before testing any electrical component in the Charging System it is "IMPERATIVE" that you have a fully charged battery of 12.5 volts or more and be able to pass a proper "LOAD" test if necessary, you may have a preliminary reading of 12.5 volts or more but little or zero amperage, the battery is faulty and must be replaced. AGM type batteries fall into this scenario more so than lead-acid batteries.
1. Battery Test:
3. Connections and wires:
Inspect the regulator stator plug, and check the battery terminals for connection corrosion. If everything seems to be in order, move on to number 4 below to determine if there's a failed component.
4. Stator Checks/Rotor Check: Each of the following tests isolates the Stator & Rotor. If AC output and resistance test fail and stator test passes then the rotor is at fault (Pull Primary covers and inspect rotor for damage).
5. AC Output Check:
Unplug the regulator plug from the stator start motorcycle and change Voltmeter to AC volts. Probe both stator wires with your meter lead. The motorcycle should be putting out approximately 18-20 ACV per 1,000 rpm. Reading will vary depending on system, check service manual specification
Generic Specs:
Switch your multimeter to Ohm x 1 scale. Probe each stator wires with meter leads and check resistance on the meter.
Resistance should be in the range of 0.1-0.5 Ohms. Reading will vary depending on the system, check the service manual for specifications.
Generic Specs:
5. Stator Ground Check:
If there is continuity your stator is shorted to ground and must be replaced.
6. Regulator Test:
Identifying Wires:
Battery Charge Lead- Wire going from the regulator to battery positive.
Regulator Ground Test: Ensure the regulator body is grounded or grounding wire is fastened tightly to a good ground (you should verify this by checking continuity from the regulator body to chassis ground).
Next, switch your multimeter leads putting the negative lead on the AC output wires and the Positive lead on the Battery Charge Wire. The reading should be Infinite. With your meter on the same setting, place your multimeter positive lead on the regulator ground wire or to the regulator directly, and then place your meter negative lead on the AC output leads.
Next, switch your multimeter leads putting the negative lead on the regulator ground and the Positive lead on the AC output wires. The reading should be Infinite.
For more information about your issue and valuable "FREE" downloads for viewing or printing that you will need please click on the blue links below. Good luck and have a wonderful day.
Vmax Charging System TroubleShooting Guide
Charging voltage VMaxForum net http://www.vmaxoutlaw.com/tech/VMX12-Service-Manual.pdf
OEM parts for Yamaha
YAMAHA VMX12 Owner Manual
Aug 18, 2012 | 2000 Yamaha V-Max
My yamaha virago 1100 will not charge battery while running
Hi, Anonymous the following is a comprehensive charging system test that is guaranteed to the find issue with your system.
5. AC Output Check:
Generic Specs:
Generic Specs:
Identifying Wires:
ViragoTechForum com
http://www.sloneservices.com/SilverBack/Other-Stuff/VS-1100-chagre-syst.pdf
Yamaha Virago XV535 1100 1981 1994 Service Manual
Yamaha Virago XV1100K Owner Manual
Jun 16, 2012 | Yamaha Motorcycles
I have a Xantrex 2400-12 two years old, installed off grid in a vacation home in Mexico, a service call is not an option. The inverter quit working, flashes "888" and shuts off. I have a trace...
First off I am not in this for the money. If your not satisfied with the information below simply reject the solution so that you can hear from other experts.
The 888 flashing is telling you that the inverter has lost DC power momentarily. This can be from broken strands in the battery cables or an internal wiring problem in the inverter. Check the battery cables for corrosion. Remove the terminals check for battery post corrosion and visually inspect each bable to terminal connection from the battery connector to the inverter DC Power connections.
Here is something to keep in mind. A DC power cable only needs one tiny strand of wire to indicate voltage on a meter. However, if there is any load on the AC side that tiny strand of wire that is giving you the proper DC reading may in fact drop well below 10.5 V DC and simply cause the unit to automatically shut off even with no load.
Explain your situation to Xantrex using the link below and they may be able to help you due to the fact that you do not have a local "post warranty service provider" in Mexico:
If your product requires troubleshooting or warranty service, contact your
dealer.
If you are unable to contact your dealer, or the dealer is unable to provide
service, contact Xantrex directly at:
Direct returns may be performed according to the Xantrex Return Material
Authorization Policy described in your product manual. For some products,
Xantrex maintains a network of regional Authorized Service Centers. Call
Xantrex or check our website to see if your product can be repaired at one of
these facilities.
What proof of purchase is required? In any warranty claim, dated proof of
purchase must accompany the product and the product must not have been
disassembled or modified without prior written authorization by Xantrex.
Proof of purchase may be in any one of the following forms:
• The dated purchase receipt from the original purchase of the product at
point of sale to the end user, or
• The dated dealer invoice or purchase receipt showing original equipment
manufacturer (OEM) status, or
• The dated invoice or purchase receipt showing the product exchanged
under warranty
Telephone: 1 360-925-5097
Fax: 1 360-925-5143
Web: www.xantrex.com/support
customerservice@xantrex.com
The owner's guide is here:
http://www.xantrex.com/documents/Power-Inverters/Xantrex-Inverters-Digital/XPower_200-400-800_Digital(975-0176-01-01_Rev-B).pdf
Thanks for choosing FixYa,
Kelly
Jan 16, 2011 | Xantrex Technology Trace Series Inverter /...
Xantrex Inverter/Charger has no AC output
HI
Checking AC Output
1. After the battery voltage and connections have been checked, disconnect the inverter.s AC output wires from
the power distribution system and connect a light to the AC output of the inverter/charger.
2. Disconnect the remote panel to eliminate it as a possible problem.
3. Turn the inverter ON using the power switch on the front panel of the inverter. The 100-watt light should
illuminate. Measure the voltage at the AC output wires using the multimeter. The reading should be 114.126
VAC or approximately 230 VAC if the unit is an international model. If the light does not illuminate, there is
a problem with the inverter. Contact Xantrex technical support.
May 21, 2010 | Kitchen Ranges
I have a #20 charger inverter on my sailboat. It has worked fine for several years. This winter, I replaced the battery bank with 4 Trojan T-105. Batteries are fully charged, new battery wiring and...
Without more information, it could be a number of things. For starters, you might try disconnecting the ground wire to see if that makes any difference. The Xantrex Owner's/Installation Manual says specifically not to connect the inverter's negative *battery cable* to the vessel ground, but if the unit's housing and the negative cable share a common ground somewhere inside the unit, that would be the same thing. The T-105s are great batteries, but since they are 6V, make sure you rewired them correctly, i.e. a pair in series (12V) wired in parallel with the other pair for 450 AH total. Recheck all your battery connections and make sure you didn't blow the inline battery fuse in case you inadvertently made a momentary wrong connection during the new battery installation.
Apr 27, 2010 | Xantrex Technology Heart Freedom 30...
Burnt out
internal failure possibly on power side, lower than 300A fault current so unit could not trip i/p protection and as fault was post ac section, continued to burn internally.
it just broke
no breakers tripped out so it kept drawing current until the fault burnt away.
maybe this is what happened, need to know a lot more info to change hypothisis
Jun 01, 2009 | Vector VEC056D 2500 Watt Power Inverter...
Open Questions:
Xantrex Technology Xantrex LinkLITE Battery Monitor Logo
167 people viewed this question
Top Xantrex Technology Electrical Supplies Experts
ken skalski
Gene Haynes
Are you a Xantrex Technology Electrical Supply Expert? Answer questions, earn points and help others