Question about Carrier Heating & Cooling
Have 20 year old split carrier system, tried to turn a/c on today nothing, no fan, blower, do have power to a/c both in and out. Any help
  • garjan6002 May 28, 2009
    Thx to the both of you. The door switch worked itself loose, reinstalled and now have air.
    Thx again
    Sergeant:
  • 293 Answers
I assumed that when you say AC power is both in and out, you mean both the indoor and condensing unit has AC power. Check if the unit is equipped with in-line fuse. If not, and you have a rotary switch, try to check the terminal continuities. If it is an electronic switch, try to replace the card.
Posted on May 28, 2009
  • 24 Answers
First thing is that if u in fact have voltage to the furnace and condensing unit check the primary and secondary sides of the transformer on the furnace. if you dont have 120 on the xfrmr test the door switch and 120 v connection to outlet. if you are good there check the secondary side of the transformer and see if u have 24 volts leaving the trans. if you have 24 v leaving the trans. you should have 24 to the stat if there is not a blown fuse on the control board. check the transformer for power. if there is power there see if theres a fuse on the control board at the furnace. if thats not blown check stat operation pull stat off and jump r to y which should engage cooling. jump r to g which should engage fan. this is all of course if u have a standard a/c and not a heat pump unit. if u can jump cooling or fan replace the stat. let me know more when u get there.
  • shizznat May 28, 2009
    damn door switches.
My carrier split ac trip after some time and green light blinking contsly
If this is a ductless split call a tech! The ductless split systems can be a troublesome unit to diagnose. A few things to try. Clean air filters and ensure coil behind is clean. And build up or debris on blower wheel (indoor fan blades) will cause unit to fault. Turn off power at breaker or disconnect and clean (with water hose and medium pressure) the outdoor coil. Be sure you will not damage outdoor coils fins with too much water pressure. Turn power on. If this simple service don't do it again, call a tech! Be sure to ask if they have someone who is experienced with mini split systems and be patient. Even the best technician will need to call carrier for tech support.
Jun 04, 2015 | Carrier Heating & Cooling
Dear sir i have a problem with my carrier split fan.and the fan is ok.i think the problem is the electronic board.i'm an electronic enginner.i tested the components and al is ok.i dont undrestand what's...
if it is a standard split a/c system the board controls the voltage to the fan motor on a closure of the thermost on the low voltage side. Jumper the r-g terminals on the board, listen for the relay to "click" and verify voltage to the blower motor from common and the terminals that are usually labeled "heat" and " Cool" if the relay energizes and no power is present at these terminals the boead will need to be repalced
Hope this helps
Dan
Mar 03, 2010 | Heating & Cooling
I have a Carrier 58SX060 Furnace with air. I turned the thermostat to heat and the exhaust comes on and runs and the pilot comes on but the burner never light s and the blower never comes on. If I turn the...
carrier gas furnaces will try to light three times then will usually go on a lockout for one hour you can bypass the lock out by resetting the power, turn furnace on, remove wires from gas valve, you will need a multi meter to check for voltage to valve, if control board sends a call to the gas valve the valve is bad, if voltage is never present during the lighting cycle your control board is bad
Sep 30, 2009 | Heating & Cooling
Blower won't kick on
My guess is the FAN RELAY has loose contacts in it Trace the wires from the motor to where they tie in 1 will go to the power cord (this in L2 or Nut) The other 1 or 2 wires will go to a fan swich/relay or a rotary hi limit fan acutator sw. This rotary fan sw has a lot of cousins. On some Carrier Bryant Paynes and or Day Night furnaces that are over 20 years old the fan switch is a small rectangular cube with a seperate heater inclosed in the rectangular box. This fan sw could also be your problem but Im betting on the fan relay. It usually Click when you turn the Fan from auto to on. And the wire G goes to it (eventually)from the thermostat. CHeck this when its acting up. You could jump around the relay going from the L1 feed on the relay to the Closed motor speed.
I doubt you have a bad fan motor. But I could be wrong. Usually they have a smell associated with a bad one and you dont mention this.
Mar 01, 2009 | Heating & Cooling
I have a 5 year old Dell Dimension 8300. Lately I have been having problems getting it to come on and stay on. Once running, it stays running great. Today it wont stay on. I hit the power and sometimes it...
It is likely your power supply is failing. When you press your power button a signal goes through the motherboard to the power supply, then the PS comes on. I would try a replacement power supply first, you can get a used one for less than $20.
Dec 31, 2008 | Computers & Internet
Air conditioner
Turn off unit supply and check the blower wheel inside the indoor unit by rotating it manually by your finger if the blower wheel rotates freely then there is something wrong with your fan motor or fan motor capacitor. But if the blower wheel is not rotating freely try to check the fan motor for lubrication or some bushing dried of and no oil
Dec 10, 2007 | Heating & Cooling
Heating & Cooling Logo
166 people viewed this question
Top Carrier Heating & Cooling Experts
Dan Webster
Dan Webster
Donni Steen
Bill Long
Are you a Carrier Heating and Cooling Expert? Answer questions, earn points and help others