We have had the electric air handler removed and replaced, enlarged return air and added a new 24x20 filter return air grill, adjusted all vents and checked in attic for a possible kink in the ductwork. Master bedroom is same size as the guest bedroom however it is 5 degrees warmer. The rest of the house is quite comfortable. We have spent almost $1000.00 with ac so called specialists and are so frustrated.
  • steve
    steve May 11, 2010
    Factors to consider are,
    distance from air handler.
    duct size to room.
    number of ducts to room.
    location of ducts in room.
    windows in room.
    southern exposure of windows.
    wall and attic insulation to room.
    return air from the room.
    cfm to room.
    partially closed damper to room.
    Can you answer these queries?
  • 420 Answers
The issue may not be confined to airflow alone. An air conditioner makes us more comfortable through two basic rules of physics.
It removes sensible heat (the temperature you feel) and removes moisture from the air. Dry air enhances the bodies own cooling system allowing perspiration to evaporate more quickly which speeds the removal of heat from the body, this is why 85 and dry feels more comfortable than 72 moist degrees.
to ensure the ducts are balanced properly one must use an anemometer which is a tool used to calculate airflow by the pro's. Being that most homeowners do not have access to one there are some good observations to make using a pocket thermometer and your own senses:
  1. Ensure the guest room vent is the same size as the master bedroom.
  2. Ensure the supply duct for the suspect vent is the same diameter and approximate distance from the main plenum (where the ducts originate) as the master bedroom.
  3. Is the air emminating from the suspect vent approximately the same in volume as the master bedroom (does it feel and sound the same).
  4. The issue exists even if the guest bedroom door is left open.
  5. The air temperature measured at the vents is within 3-5 degrees of each other.
If 1 - 4 are true check for #5, if # 5 is false make sure the suspect ducting is insulated or covered well by attic insulation.
If 1, 2, 3 or 4 are false: Ensure the following:
  • The guest room ducting does not have a damper hidden under insulation or duct wrap.
  • The duct has not been crushed or restricted.
NOTE: internaly insulated ducts can be restricted on the inside by fallen insulation while appearing normal on the outside.
If #5 is false (issue goes away if the door is left open) the door may need to be cut off a bit more at the bottom or a grill installed to allow the air coming into the room a place to go.
If none of the above reveal the culprit concider the room itelf, it may have a higher heat load than the others.
A higher heat load may be due to dislodged, compacted and or wet insulation in the walls or attic, feel the walls and ceilings with your hands, how does it compare with cooler rooms?
If the walls and ceiling feel about the same and the tests above did not expose an issue its time to call the contractor back in, make sure the static pressure is checked in each duct a foot or so downstream of the the plenum and again just upstream of the vent. A duct with air pressure higher or lower when compared with the others could mean a variety of issues with the duct or where it connects to the plenum.
Posted on May 26, 2009
Goodman AC unit recently service but don't believe the filter I am using is the issue or what the tech did actually fixed my issue. Details below.
Setting the air handler to high speed will draw more current and this will result in an increase in electricity consumption.
Jul 27, 2017 | Goodman Heating & Cooling
Pro Standard Fan mount
Since the failure of an air conditioner to turn on, loss of air conditioner cooling capacity, reduced air conditioning output temperatures, loss of cool air supply, or even loss of air flow entirely can be due to a variety of problems with one or more components of an air conditioner or air conditioning system, after reviewing the lost air conditioner cooling diagnosis procedures described in this article, be sure to also review the diagnostic procedures at each of the individual air conditioning diagnosis and repair major topics listed just below. To return to our air conditioning and refrigeration home page go to AIR CONDITIONING & HEAT PUMP SYSTEMS.
Electrical problems on HVAC systems: Keep in mind that despite the depth of technical detail you will find here about all components of air conditioners and heat pumps, most service calls for non-working air conditioners or heat pumps turn up an electrical problem. So if your A/C system is just not working at all be sure to check all of our electrical and control setting suggestions first.
Mechanical problems on HVAC systems: tend to fall into these groups: refrigerant leaks, dirty condenser coil or unit, dirty evaporator or cooling coil, or burned out (or hard-starting) compressor motors. We have also seen a number of problems with fans and fan motors in both the compressor/condenser unit and in the air handler/blower fan unit. Some of those fan problems are mechanical - like a loose fan belt or blade. MORE DETAILS
Nov 13, 2012 | Heating & Cooling
I just had 'goodman gpc1336h41ab' 13.00 seer unit installed , I have a 1250 sq. ft. home and it just doesnt seem to be cooling. The unit runs constantly. So my question is , is my unit big enough...
There are a few variables that determine the size needed to cool your home - the size of your home, type insulation, are just two. I have a 2600 sq ft home - about 1300 sq ft per floor. I choose to cool the entire second floor (bedrooms and baths) and two of the largest rooms on the first floor (kitchen & living room) via flexible ducts from an air handler installed in my attic. My house was built in 1960, and at the time had electric heat. This means it is fully insulated. I replaced all the windows with energy efficient types, and vinyl sided. I installed soffit, ridge and gable vents to keep my attic well ventilated. I can cool my house in Boston, MA to 70 degrees (when it is 85 degrees inside) with a 4 ton unit in a little over an hour with no problem (one ton of cooling is equal to about 12,000 BTUs). Your condenser should not run non-stop. If it is not cooling then it is not a thermostat problem, but could be a gas charge problem. If you haven't paid the contractor in full yet - that may be the reason why. The contractor should know how much cooling you need for the space you have and installed a properly sized unit. Make sure your air filters on the return are clean and replaced regularly. Call the contractor and explain the problem - he should be able to solve it for you very quickly.
Aug 03, 2011 | Heating & Cooling
WIRING THE THERMOSTAT TO AC UNIT THEN FROM THE UNIT TO HANDLER
Generally, you would go from the thermostat to the air handler, and then, from the air handler to the outdoor unit. I don't know if you have a heat pump or not, so I will give you a simple diagram and you can contact me if you need more.
Thermostat : Y G R W and sometimes C
Air handler: Y G R W and C
Outdoor unit: two wires connecting to the contactor ( not heat pump)
Thermostat; Y--------------Y(air handler cooling)------------------one side of contactor, outdoor unit
G-------------G (air handler, fan)
R--------------R (air handler ,hot)
W-------------W (air handler, heat)
C--------------C (air handler, common)------------other side of contactor, outdoor unit
This is a typical wiring diagram. Just contact me if you have something different. Hope this helps. Stay cool. mark
Jul 10, 2011 | Heating & Cooling
I'm looking to purchase a Rudd 2 stage model, 16 SEER, 5 ton along with a 100000 BTU 95% furnace. I have a two story home and will only be using the 1 AC. Will the Rudd cool both floors?
Assuming that there are ducts ran upstairs and downstairs, it all depends on the square footage of the living spaces, i.e. bedrooms, living room, dining room, etc. You need an average of 1 cfm per sq ft. For every 1 ton of air, you have an average of 400cfms. So your 5 ton unit will cool/heat 2000 sq ft. A 16 seer unit with a 95% furnace is a nice buy and you will notice the difference for sure. Hope this helps!
Aug 03, 2010 | Ruud Central System Air Conditioner
Just installed 5 units in my home. all four work
It sounds like the condensate from the drain pan is not draining correctly! The drain tube from your Air Handler unit may be kinked or not properly installed. The condensate water from the unit should be drained outside at least.
Jul 19, 2010 | Mitsubishi Mr. Slim MXZ30TN Air...
I have a 3 ton goodman heat pump warm air is delivered from all the vents except for two which blows cool to cold air . help me , freezing im both bedrooms
if these are the longest runs from the air handler this can sometimes happen ,about the easest solution is to install a in duct heater into the duct feeding the rooms this is basically a set of electric coils installed in duct to re-heat the air going to the bed room
Jan 08, 2010 | Goodman CLQ36AR49 Air Conditioner
AC BLOWS WARM AIR
Cooling comes from what is done outside, if air handler is blowing and you are hearing a sound , may be in the duct work. If you feel warm air in cooling mode then the outside unit is the prob, need more info
Jul 25, 2009 | Heating & Cooling
My air handler comes on ,not the outside unit when my thermostat is in the off position even if i turn the thermostat down to 50 and have it turned off the air handler comes on for about 5 to 10 minutes...
If you have a standard thermostat the fan switch is for the air handler only. It completely over rides the thermostat for most settings. Now lets see this is what I'd expect:
fan switch on Indoor fan runs all time
Fan switch auto Indoor fan only runs when thermostat is set to cool or heat and the thermostat is turned up above room temp for heat or below room temp for cooling. In both of these modes the furnace blower comes on and stays on til the room temperature is satisfied. The outdoor unit only comes on for AC the out door unit will not come on for heat or the "on" setting on the thermostat. See exception 1 & 2 below...
Exception 1- (in a heat pump the out door unit runs in both heat and cool mode unless it has emergency heat turned on then it will not come on outside in the heat mode, and depending on the type of heat pump and furnace or air handler it is). A heat pump thermostat usually has "backup heat" and an "emergency heat" setting switch on the thermostat.
Exception 2 - On some thermostats they are made to cycle on the heat if the temperature reaches a preset temp (around 50'f usually but definitely by 40'f). This mode prevents freezing when if instance the homeowner is away or while the home is under construction. In this mode the fan inside can run but the heat usually comes on with it.
Exception3 - On some electric furnaces the heating strips may be individually controlled and thus not all come on at one time. This may give the feel of no heat especially if the room is cold.
Now there may be other exceptions but Ive tried to give you a heads up on some of the most common ones.
If you need more help please post more specifics about your unit/system as to for sure what switches are set to what setting and what is happening with each. My first though was that maybe your system is OK and you needed to know if the thermostat was working properly.
If this helpd you understand your problem would you please give me as hifgh a mark as you can. Thnaks for using fixya and good luck.
Mar 28, 2009 | Carrier Heating & Cooling
My Blower Turns itself on when it is not supposed to.
If your indoor unit is located in the attic, you may be experiencing the result of a high temperature safety device (possibly too sensitive) that is responding to warm air drifting up the return air duct. The function of this device is to turn on the fan at a given set point and cool the unit back down. Have someone identify your limit rating and change the limit device with one rated the same or see if the maker of the unit has an upgrade/service bulletin on this fault.
May 03, 2008 | Ruud Handler Air Conditioner
Heating & Cooling Logo
186 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Donni Steen