Air handler fan not working
I have a 5 ton rheem package heat pump that has been working fine. It is 3 yrs old. Now the compressor runs but the internal air exchange fan does not come on.
  • Dan Todd May 11, 2010
    Checked ALL the breakers? Checked the dry fuses in the little box outside for continuity?
    Sometimes the fan switch on the thermostat gets stuck. Try turning it "on" and see if it runs. If it does, switch back to automatic.
  • 3,361 Answers
Check the fan relay switch in the air handler.
Check the fan motor capacitor.
Check the fan blower wheel for binding.
Posted on May 25, 2009
My fan will not turn off even if you shut system down
The fan relay is located in the air handler side of the system. Replace it and the fan will shut off normally.
Jan 16, 2016 | Rheem Packaged Gas And Electric Unit 13...
Emergency heat on, compressor not running
Unit may have have iced up and defrost timer came on which is emergency heat check pressures and refrigerant
Dec 19, 2015 | Rheem 3 Ton 14 Seer Package Heat Pump -...
Indoor blower won't shut off on heat pump
I would look to replace a relay that is not shutting off or replace the thermostat itself.
Nov 14, 2015 | Honeywell Heating & Cooling
What is problem when fan motor on outdoor unit gets very hot and compressor will not restart?
Ur compressor depends on fan motor of ur condenser. Ur compressor undergoes Hi-pressure because ur fan not working properly
Sep 06, 2014 | Rheem Air Handler 3 Ton With RBHP Series
Had 16 xi Trane heat pump installed 3 years ago. It ran well for the first couple of years. It began to stop heating and would blow cold air only. Have tried both aux heat and reg. heat to run and neither...
That's a complicated system that needs a qualified technician to service it. Lots of people can install them and they run fine, for a few years. Your indoor unit, operating on 2 heat elements, will feel like its blowing cold air even though its heating, just not so well. And not like you are accustomed to. Each element (5kw)=22.7amps, on average. So 3 elements operating should trip a breaker. Its probably been operating on 2 heat element plus the heat pump. And now you have trouble with the heat pump. If you can't TRUST the guys working on your equipment, try someone else. A second opinion. Normally a 3 or 4 ton unit will have 15kw heat installed, heatpump or not. 5 ton, 20kw. If yours is a 3-4ton, cooling, the 100amp(or normally two 60 amp) breaker should have been installed upon equipment change out. If yours is blowing cold all the time, something is wrong with your heatpump. The electric heat inside operates only when the heatpump can't keep up(real cold outside), the heatpump is in defrost(then it's actually in cooling mode), or if you have the tstat in aux/em. heat. Try a local trane dealer? Of a technician with 15-20 yrs under their belt. A trane dealer should have trane tech support also. BIG HELP!!!
Mar 01, 2017 | Haier Energy Star ESA3183 Air Conditioner
I have a Rheem heat pump/air handler; it draws 2.9amps with only the fan running, 13amps when the heat pump is running and 38amps with the heat strips on. My question is why the unit draws that many amps...
Sounds like it must be about a 2.5- 3 ton system. The 13amps has to be the compressor draw -normal. and 38 on the strips- normal. 2.9 fan -normal.
You may want to check your wiring to see where the outside unit gets its power. Theres nothing inside that can draw 13 amps. That almost has to be the compressor power wire.
Jan 27, 2011 | Heating & Cooling
My 5 ton Goodman Heat Pump won't go into heat or ac mode. Fan won't turn on. No noise from compressor. System is 1 1/2 yeras old.
Easy: Turn the "fan" switch to on at the thermostat and see if the blower starts. If no start, check breaker at breaker box. Check service disconnect at or near the air handler. With the breaker and/or service disconnect OFF check the 3 or 5 amp fuse inside the top cover in the air handler.
Not so easy: (You must know what you are doing for this part or let an HVAC Tech do it for you) Open thermostat and firmly jump the Y and R terminals to see if you get the compressor to start for no more than 30 seconds. (don't do it more than once.) Jump the G and R terminals to see if you get the blower to start. If so, u have a bad thermostat. If not, check the transformer inside the same cover in air handler for proper voltage. (24V. Make sure you also get 220 on the opposite side of the transformer)
If the blower comes on, but the heat pump doesnt start, open the side cover of the heat pump, with the thermostat on cool, and the temp. setting as low as possible for at least 10 minutes see if the contactor is pulled in. If so, check the capacitor and see if it's blown out. Be super careful these systems operate with 220v and the amperes are enough to kill you if you make a simple mistake.
May 20, 2010 | Goodman CLQ36AR49 Air Conditioner
4 ton rheem 3yrs old thermostat
It is possible that the relay in the thermostat for "cooling" has gone bad. The relay that runs the blower is different than the condenser relay. Check that you have 24v AC coming from the t-stat to the "y" terminal at the air handler. That same "y" wire should go out to the condenser, make sure then that you have 24v out there. If you have 24v at the condenser then see if the contactor is pulling in. If not then you may have a loss of charge switch that is stopping the current to the contactor. See if you have 24v to the coil of the contactor. If the contactor is pulling in and power is going to the compressor then the compressor has failed. If this is the case the condenser fan will be running but the compressor is not. If neither the condenser fan or the compressor is running then you have a problem in the 24v circuit, which could be a bad wire or a safety switch.
As you can see there are a number of possibilities for your problem. You will need to methodically go through everything to eliminate the possiblities till you isolate the problem,
I hope that this will help you to solve your problem and get you cooling again!
Thanks for using Fixya!
Heatman101
Nov 23, 2009 | Air Purifiers
Heating & Cooling Logo
675 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Tim Whalen
Mack Baxter