When I set tstat to call for a/c, compressor outside comes on. Blower on furnace does not. When I manually rotate fan limit switch on furnace wall, blower comes on, blows cold air, and then goes off when I release the fan limit switch. I have a Honeywell 83251008a low and high voltage transformer, and Honeywell (I think) limit on off switch. I also noticed the 2 wires coming from the Honeywell Gas regulator are off. They were connected at the onset of the problem. I am not sure where to reconnect them.
  • 23 Answers
Sorry, you mean gas valve control? when you have only 2 wires, usually it doesnt matter which terminal as there,s no polarity differentiation at that locationYou should never rotate this dial by hand, you will bend the helix inside and fan will not operaTE properly.Now , with your problem, was this unit working properly at first, or was this a ndew install ? That honeywell control is only for the heating mode. For a/c operation, its take a relay of some sort, depending of your model.was is there present that you can indicate to me or us? Do you have a control or box or terminal strip with the letters rwgcy, in any order?
Posted on Nov 11, 2011
  • 116 Answers
Blower relay bad or no call from stat on green wire to run fan jump red on stat to green if fan comes on stat bad if no look for fan relay turning the well switch bypasses the relay hope this helps
Posted on May 25, 2009
Coleman Evcon furnace blower runs w/ no call for heat. Temp is 5+ degrees above thermostat setting. (Programmable tstat)
When you say door are you referring to the front door or the furnace door? If the unit kicks on AND off by itself I would say it's in the tstat or the tstat wire. If it were internal I would think the blower relay or heat contactor/relay were getting stuck AND THE FAN WOULD NOT TURN OFF until you flipped the breaker. Good luck
Mar 21, 2017 | Coleman Heating & Cooling
Furnace keeps tripping off on limit switch. replaced limit switch still trips, blower motor seems to work fine.
It's always possible that the limit "dial" switch is sticking leading you to believe that it's only at 150º.
How old is the furnace and when was it last cleaned.
Dec 12, 2007 | Heating & Cooling
I have new blower motor. it dosen't stop running
Could be a bad blower motor resistor,mounted by the blower.
Sep 28, 2016 | 2002 Dodge Ram Pickup 1500
Replaced Thermostat and now Blower Motor will not run
Sounds like a set up issue on the tstat. You say this is a packaged unit, inside the machine you should find where the tstat wires hook up. Typically red is power yellow is compressor orange is reversing valve white is emergency heat green is blower. Put red and green together, test blower. Then red green and yellow, make sure blower works again. If blower runs both ways it's either the tstat wire or tstat itself. Make sure you are landing wires on dedicated heat pump terminals, make sure in settings you are set up for heat pump with back up electric heat and TSTAT CONTROLS THE FAN. Good Luck. Also if there is a switch on the tstat for gas or electric on the back you want electric.
May 12, 2017 | Heating & Cooling
Reset switch on furnace to make air contitioner start
I know what you mean. Not a lot of companies around here care to work on mobile homes. There is a safety on that unit that may or may not be a reset. Normally it will have a small red peg in the center to push and reset. Some don't have a reset though. Look for a small, flat safety, it should have 2 wires. And it may be hidden. As if 2 wires just disappear behind the blower assembly. Check for voltage to it, and across it. You can find volt/ohm meters for $10. Chase or follow the signal from the tstat. R comes from the tformer and powers the tstat. Tstat closes and sends a 24v signal through Y and G in cooling. Y should go from tstat to indoor unit, and to a terminal block or wire but, then directly outside to outdoor unit. G comes from the tstat to a terminal block's (g), then to the auto,off,on, then to a switching relay's coil. This coil closes and allows line voltage to pass through powering up the fan. So at the indoor, with 1 lead connected to common with your voltmeter set to AC volts, use the other lead to follow these paths. Or keep calling companies to find someone who will work on them. Electricians will not work on HVAC equipment. Even though it's all the same principal, source/line/load. Be safe!
Mar 17, 2017 | Heating & Cooling
Blower fan running constant after new fan and limit switch installed.more info.Honeywell-tradeline.L4064B 2210, combination fan and limit control, adjustable fan differential with manual fan switch, flush...
Here's my best shot.
Check the temperature settings for the fan switch.
The low OFF setting should be about 100 degrees.
The ON setting should be around 150 degrees and this is the setting that "makes" the ON contacts.
The HIGH LIMIT setting should be about 180 degrees.
If these are set, can you use a meter to see if the FAN ON contacts are closed?
Lastly, it appears that one hot line should go to one side of the blower and the other hot line should go to the bottom FAN terminal with the other side of the blower being fed by wiring from the top FAN terminal.
Good Luck. Gary
Feb 21, 2011 | Honeywell Heating & Cooling
Goodman furnace\ blower comes on,unasked
Sounds like the fan switch on the furnace is set to low. Turn power off to furnace, take door off of furnace look for a fan switch, it may be a fan - limit together. The limit settings should be approximately 160° to 200°, and the fan settings should be about 100° to 140° set it to 120° it it's already set there then you probably need to replace it.
Aug 03, 2009 | Heating & Cooling
AC unit turns on blower doesn't come on
The thermostat is the controller.
Jun 19, 2009 | Heating & Cooling
Blower will not turn on when a/c compressor comes on - tstat ok fuses ok
You should have a fan relay on your furnace that would control your fan in air conditioning and that sounds like you are needing
May 24, 2009 | Honeywell L4064B2236 Fan/Limit Control...
Ruud heat pump high pressure cut off problem
That's going to be in your installer configuration. Check and make sure the G terminal has a wire connected to it at the tstat , and that connection it tight. In the configuration menu, make sure it is set for a heat pump, elected heat. It seems to me that the tstat doesn't know its connected to a heat pump. Should be able to locate aodel # for tstat on the back of it. And ask Mr. Google for a manual, if you don't have 1. Hope this helps!
Mar 18, 2017 | Heating & Cooling
Heating & Cooling Logo
103 people viewed this question
Top Heating & Cooling Experts
paulcarew
Dan Webster
Dan Webster
Donni Steen