Question about Weather King 10AJA3001AH Air Conditioner
I removed the blower from the furnace to clean it. After installing the blower the condenser would not come on. The furnace heating works okay The air conditioner works and cools the house if I force the contactor closed. I get no voltage across the leads from the furnace
  • 29 Answers
You don't have the t'sat wires to the outdoor unit hooked up. They should be on the y & c terminals. If they are you may have a burnt out contactor coil. It should read 24volts at the contactor coil when you are calling for cooling
Posted on Jun 03, 2009
My furnace will not reach the desired house temperature in one cycle. It will run for several minutes, shut off, and repeat. It eventually reaches the desired temp but it take a long time and I feel it...
There are a few different reasons for short cycling of a furnace.
1. Inadequate air flow. Not enough air moving through the furnace can cause it to overheat and trip the high temperature limit switch.
check to see that all registers are open and returns are not blocked.
2 Improper heat anticipator setting on thermostat. Some thermostats have a heat anticipator and too low of a setting can cause short cycling.
4 Partially blocked drain hoses. If the condensate backs up into the furnace it can shut the flame off and then when the condensate drains the furnace starts again. Check all drain hoses to make sure they are clear.
These are just some of the possible reasons for short cycling .
Hope this helps.
Dec 26, 2013 | Heating & Cooling
Cleaning instructions
Dirt is the biggest enemy of your furnace. It can waste fuel and drastically lower efficiency. Dirt affects all three basic components of your furnace, so cleaning is the most important part of regular maintenance. The three parts of the furnace should be cleaned: the filter system, the blower, and the motor.
The furnace filter should be replaced or cleaned at the beginning of the heating season and about once a month during periods of continuous use. To check the filter, take it out and hold it up to the light. If it looks clogged, replace it with a new filter of the same type and size regardless of the length of time it has been used.
Step 4: Clean blower assembly, belts and pulleys to blower, and motor housing. Cleaning blower is critical if furnace has a squirrel-cage fan, because openings in this type of blower often become clogged with dirt. To clean blower, remove panel that covers filter to gain access to blower or panel on front of furnace. This panel may be slip-fit on hooks or held by series of retaining screws. Access to inside of blower is usually gained by sliding out fan unit, which is held on track by screws.
If power cord to fan assembly is not long enough to permit fan unit to slide all the way out, disconnect cord. Mark wire connections first so you'll be able to reassemble unit correctly. With toothbrush, clean each fan blade and spaces between blades. Then, with vacuum cleaner hose, remove all dirt and debris loosened by brushing. Vacuum belts and pulleys. Wipe motor housing clean to prevent heat buildup in motor.
Feb 08, 2013 | Rinnai Toyostove Direct Vent Heater:...
Ruud achiever 90 condensation overflow
Not a furnace guy but I do know that your drain should be insulated. Gotta figure out if it's water from the drain leaking or actual condensation dripping from the outside. If sweat, it needs insulated. Good Luck.
Mar 11, 2017 | Ruud UBHC Air Conditioner
I have a Intertherm Heat Pump system in my Manufactured Home, Model # E2EB-015HB; Serial # E2E0121006692. Condensation is forming on the Coils and the water fills up the area under the coils, drips down...
There is a drip pan bit the middle is open to allow air flow through the coil and into your ducting. If the drain for the drip pan is clogged it will fill up and overflow onto your furnace and then to the floor.If that is what is happening then clean out the drain tube running down the front of the furnace and it should empty the drip pan and solve your problem.
You also need to have your furnace checked for water damage in the electrical components, if these have gotten wet then you run the risk of a fire. Please consider calling an expert in your area to inspect your furnace and make sure the drain line is clear.
Jun 13, 2011 | Intertherm Heating & Cooling
My furnace keeps shutting off after a minute i changed the thermo copler,i also changed the blower and still having the same problem,i turn the furnace on and the burners and everything seem to work okay...
Is it possible that the flame sensor has to be cleaned or replaced. I would try removing it first and then use steel wool or some sandpaper and clean it off. I have seen them get all blackened and discoloured and then they don't conduct heat the way they should so the sensor stops the flow of gas. Give that a try.
Jan 19, 2018 | Honeywell Heating & Cooling
I have an 11 year old natural gas forced air furnace--a Goodman GMPN100-4 Rev B, which is 100K BTU and 92% efficient which was working fine at the end of last winter. I went to turn it on for the first...
You are correct. If the inducer motor is warm, but not running, it has seized up. If you replace this yourself, I also suggest that when you replace the inducer fan, check to make sure the secondary heat exchanger isn't clogged, or the condensate drain(s). If you have an HVAC contractor replace it, he should do this for you. It shouldn't run more than $350, to have it replaced and he can check for clogs (The price I'm quoting is for standard hours).
You can check this yourself by running the inducer fan without it being attached to the furnace, then attaching it to the furnace. If you notice a significant reduction in airflow, then you have a clogged secondary heat exchanger. I've run across this situation before on this particular model. The owner recenly replaced the inducer motor, but couldn't figure out why he was still having problems. I suspect the clogged heat exchanger contributed to the inducer motor to failing previously, and feel It would definitely be worth checking while you have the fan removed to help eliminate any future problems that could result from this, including heat exchanger failure. The manufacturer of this unit actually recommends you clean the secondary heat exchanger every year, but this is overkill if your furnace was installed and set up properly. I'd recommend doing it every 10 years and you're at that mark now. Instructions on how to do this are in the manual for this unit if you have it. Otherwise, e-mail me at wheels38_97@yahoo.com and I can send you a copy.
Finally, check the limit and flame roll out switches after replacing, as they could have tripped when the motor failed.
Oct 22, 2010 | Heating & Cooling
Can heat hurt your appliances?
Hot weather may affect the refrigerator as the domestic regrigerators are typically not designed for hot ambient conditions, manufactures make the assumption that you are not going to let your house get to 100 degrees (I have when I lived in Tulsa) so the condensers are smaller. Make sure the condenser is clean all the time when its hot and that the fan (if equipped) is clean and running. I had a small squirrel cage blower that was a combustion fan for a furnace I sat so it would blow more air across the condenser.
Jun 30, 2010 | Refrigerators
Itseems as though the condensation trap on Lennox G26 not working
Hi!
Take of both access covers on your furnace. In the bottom compartment (where the indoor blower fan is) there is a condensate trap, It will be black, gray, or white. Disconnect the rubber tubing that is connected to it (these tubes run up to the collector box in the top compartment. Remove the condensate trap and wash it out until it is clean inside. You will have to shake it some to get all the dirt out of it. Reinstall it and you should be good to go. Hope I was of help to you!! Good Luck!!
Dec 06, 2009 | Heating & Cooling
Goodman Furnace
Inspect the venting system for sags or blockages. The added restriction could be adding to your issue.
Mar 29, 2008 | Goodman GMS90703BXA Heater
Weather King 10AJA3001AH Air Conditioner Logo
112 people viewed this question
Top Weather King Heating & Cooling Experts
Tim Whalen
John Tripp
John Tripp
Dan Webster
Dan Webster
Are you a Weather King Heating and Cooling Expert? Answer questions, earn points and help others