Question about Lochinvar ERN-252 250 BTU Heater Natural Gas
Soft lockout ignition failure - Lochinvar ERN-252 250 BTU Heater Natural Gas
What do I try when my lochinvar spa heater says lockout ignition failure
turn off then try again means that it tried 3 times check gas if ok see if ignitor is lighting
Feb 05, 2015 | Lochinvar ENERGYRITE 250K BTU NATURAL GAS...
What is a 1F code on the hayward pool heater
The code you are referring to is actually IF, not 1F. It stands for ignition failure.
If the control exceeds the maximum number of ignition retries or recycles the heater will shut down and go into lockout. Automatic reset is 60 minutes.
Aug 09, 2014 | Hayward Pool & Spa
Why does my hayward heater have a if error code
the code is IF. it stands for ignition failure.
Aug 08, 2014 | Hayward Pool & Spa
Heil gas furnace soft lockout how to fix it
bad pressure switch, or control board
Dec 13, 2011 | Heating & Cooling
Furnance problem
Not knowing exactly the brand or model, it sounds like a pressure switch problem. The pressure switch has a hose attached to it and the draft induced blower assembly. Check the vacuum port on the inducer housing and hose for restriction, clean the port with a paper clip or what ever available that will fit into the port the clean out. Reconnect hose and see if the ignition energizes. The igniter may also be bad and would need replaced.
Note: To reset control disconnect power to unit and reconnect.
Nov 29, 2011 | Heating & Cooling
Model minimax nt std w/ddtc. will not fire up. code E04= fan failure. I can see and hear the fan running. It tries to fire twice then ignition lockout led flashes 3 times=ignition lockout. is there a...
FIRST ... CHECK YOUR FILTER !! IT MUST BE CLEAN ! THERE IS A PRESSURE SWITCH ON THE HEATER WATER INPUT LINE . IT MAY NEED TO BE REPLACED .. JAY.. THE POOL PUMP REPAIR GUY IN LONGWOOD FLORIDA
Jun 20, 2011 | Pentair Pool & Spa
I have a Ruud Achiever 90 Plus furnace that will not ignite and is showing a 'soft lockout' code on the LED panel. I've tried restting the furnace as per the manual and still no results. Am I missing...
Hello. a soft lockout typically happens when
1) the flame sensor is not detecting the flame
2) pressure switch fails to close
Since your burners are not igniting I would check the pressure switch, make sure there is no obstruction in the flue pipe, the hose going from inducer to pressure switch is not kinked, loose, obstructed, or have water in it. If that all checks out good then your pressure switch is bad and must be replaced. If you need any further assisatnce let me know
Mar 09, 2011 | Heating & Cooling
What are the carrier 8000ts led error codes?
They are listed inside the front panel of the main unit.
LED CODE
EACH OF THE FOLLOWING STATUS CODES IS A TWO DIGIT NUMBER WITH THE FIRST
DIGIT DETERMINED BY THE NUMBER OF SHORT FLASHES AND THE SECOND DIGIT BY
THE NUMBER OF LONG FLASHES.
STATUS
11 NO PREVIOUS CODE - Stored status code is erased automatically after 72
hours. On RED LED boards stored status codes can also be erased when power
(115 VAC or 24 VAC) to control is interrupted.
12 BLOWER ON AFTER POWER UP (115 VAC or 24 VAC) -Blower runs for 90
seconds, if unit is powered up during a call for heat (R-W closed) or R-W opens
during blower on-delay.
13 LIMIT CIRCUIT LOCKOUT - Lockout occurs if the limit or flame rollout switch is
open longer than 3 minutes.
- Control will auto reset after three hours. - Refer to #33.
14 IGNITION LOCKOUT - Control will auto-reset after three hours. Refer to #34.
21 GAS HEATING LOCKOUT - Control will NOT auto reset.
Check for: - Mis-wired gas valve -Defective control (valve relay)
22 ABNORMAL FLAME-PROVING SIGNAL - Flame is proved while gas valve is
de-energized. Inducer will run until fault is cleared. Check for:
- Leaky gas valve - Stuck-open gas valve
23 PRESSURE SWITCH DID NOT OPEN Check for:
- Obstructed pressure tubing. - Pressure switch stuck closed.
24 SECONDARY VOLTAGE FUSE IS OPEN Check for:
- Short circuit in secondary voltage (24VAC) wiring.
31 PRESSURE SWITCH DID NOT CLOSE OR REOPENED - If open longer than
five minutes, inducer shuts off for 15 minutes before retry. Check for:
- Excessive wind - Proper vent sizing - Defective inducer motor
- Low inducer voltage (115VAC) - Defective pressure switch
- Inadequate combustion air supply - Restricted vent
- Disconnected or obstructed pressure tubing
- Low inlet gas pressure (if LGPS used)
If it opens during blower on-delay period, blower will come on for the selected
blower off-delay.
33 LIMIT CIRCUIT FAULT - Indicates a limit, or flame rollout is open. Blower will
run for 4 minutes or until open switch remakes whichever is longer. If open
longer than 3 minutes, code changes to lockout #13. If open less than 3 minutes
status code #33 continues to flash until blower shuts off. Flame rollout switch
requires manual reset. Check for: - Restricted vent
- Proper vent sizing - Loose blower wheel - Excessive wind
- Dirty filter or restricted duct system.
- Defective blower motor or capacitor. - Defective switch or connections.
- Inadequate combustion air supply (Flame Roll-out Switch open).
34 IGNITION PROVING FAILURE - Control will try three more times before lockout
#14 occurs. If flame signal lost during blower on-delay period, blower will come
on for the selected blower off-delay. Check for: - Control ground continuity
- Flame sensor must not be grounded
- Oxide buildup on flame sensor (clean with fine steel wool).
- Proper flame sense microamps (.5 microamps D.C. min., 4.0 - 6.0 nominal).
- Gas valve defective or gas valve turned off - Manual valve shut-off
- Defective Hot Surface Ignitor
- Inadequate flame carryover or rough ignition
- Green/Yellow wire MUST be connected to furnace sheet metal
45 CONTROL CIRCUITRY LOCKOUT Auto-reset after one hour lockout due to;
- Gas valve relay stuck open - Flame sense circuit failure
- Software check error
Reset power to clear lockout. Replace control if status code repeats.
If status code recall is needed, briefly remove then reconnect one main limit wire to display
stored status code. On RED LED boards do not remove power or blower door before initiating
status code recall. After one status code recall is completed component test will occur.
Thanks for Choosing FixYa.
Kelly
Oct 05, 2010 | Heating & Cooling
Armstrong upflow,unit works intermittent problem,call for heat nothing happens,error code of 5 blinks then 6 blinks. i have no manuel, and the panels dont have the codes on them. anyone have access to the...
Armstrong
FAILURE CODES
LED Status Fault Description
Off
No Power to the System Control
Steady Flash (11 or more flashes with no pause)
Normal Operation (Standby or call for heat)
2 Flashes
Pressure Switch Closed When It Should Be Open
3 Flashes
Pressure Switch Stuck Open 30 Seconds or Longer After Call for Heat (System in 5-minute delay mode before next call for heat). On/off switch in "off" position during a call for heat will generate this code.
4 Flashes
Open Limit Switch or Limit Switch Circuit
5 Flashes
Flame Sense Signal Sensed Out of Proper Sequence
6 Flashes - pause - 1 Flash (see Note 1)*
Soft Lockout Type 1 (Failure to light within 4 trials for ignition)
6 Flashes - pause - 2 Flashes (see Notes 1 & 2)*
Soft Lockout Type 2 (Flame sense lost during run)
6 Flashes - pause - 3 Flashes (see Notes 1 & 2)*
Soft Lockout Type 3 (Pressure switch opened during run)
6 Flashes - pause - 4 Flashes (see Notes 1 & 2)*
Soft Lockout Type 4 (Limit or limit circuit opened during run)
6 Flashes - pause - 5 Flashes (see Note 1)*
Soft Lockout Type 5 (Flame has gone away after Error Code 5)
6 Flashes - pause - 7 Flashes (see Note 1)*
Soft Lockout Type 7 (Self-check failure)
10 Flashes* - SV9520H8034 only
Line Input Voltage Polarity Reversed
Dec 12, 2009 | Coleman Heating & Cooling
Lochinvar ERN-252 250 BTU Heater Natural Gas Logo
241 people viewed this question
Top Lochinvar Pool & Spa Experts
Paul Carew
rogerpaul3
Level 1 Expert
David Spradling
David Spradling
Are you a Lochinvar Pool and Spa Expert? Answer questions, earn points and help others