Payne gas furnace inducer motor wont start hear a siziling sound pryor the code read 3.1 furnace wont turn on just a siziling sound
    Master:
  • 571 Answers
Make sure there is power to the inducer motor...if it is a PSC motor, check the capacitor
Posted on Jan 06, 2014
  • 744 Answers
SOURCE: Central Heating - Ignitor starts but no gas
Check the flame sensor near the ignitor....it could just be dirty. Check that first. Check the electrical connections to it. Also, check the flame sensor's position. It must be within the correct proximity of the ignitor to tell the gas valve to open. Make sure the gas is on to the unit.
Posted on Mar 15, 2009
  • 189 Answers
SOURCE: just relpace a seized up inducer motor/flu vent. 3 red blinks
the diagnostic codes should be listed next to the wiring schematic on the inside of the blower compartment door. if the inducer motor was bad I bet you have a tripped flame rollout switch around the burners. look for a very small red button between two wires on a disk around the burners. push on the red button to reset the switck. this should turn your furnace back on.
Posted on Mar 28, 2009
  • 582 Answers
SOURCE: I have a Ruud 90 Plus Model UGRA furnace and blower starts immedi
NO BECAUSE THE BOARD IS TELLING THE FANS TO STARTARE THE CONTACTS FUSED TOGETHER OR STUCK IN THE CLOSED POSISTION CHECK THIS FIRST
Posted on Aug 10, 2009
Therinnaiguy
  • 1420 Answers
SOURCE: furnace wont start. heil gas furnace. on initial
Yes, inspect the air intake, exhaust pipe, filter and condensate piping for blockage or moisture. Also check for a hole in the hose that goes from the small exhaust blower to the pressure switch or a bad connection on the switch or control board. You may be able to temporalily jump the switch for diagnostic purposes only.
Posted on Oct 17, 2009
milten1
  • 1304 Answers
SOURCE: goodman gmpn100-4 ignitor lights, burners don't ignite
1 blink is ignition failure
without being able to do voltage checks
i would reccomend checking your igniotor, if you can put an amp meter on it, it should read 2.6-3.4 amps
if you cannot do that, Or check voltages I woudl repalce the igniotor, gas valves do go bad but very few and far between....
at the risk of a bad rating you deserve at least an answer...
if i were called to your house with this complaint I woul not bother comming with out the ignitor
just because the igniotr looks likes its hot,, it may not be hot enough to safely open the gas valve
Posted on Oct 25, 2009
The furnace i have is blinking 3 times with a pause. i have checked the vent pressure switch with an ohm meter. reading is 0. blew into the hose and could hear the click of the limit switch also watch the...
Check your furnace door. Sometimes there is a legend to how many blinking lights means what. I had an issue with mine, read the code and it turns out it was hitting the high heat limit. Turns out my blower motor wasn't turning on. Replaced it with a spare and it was fixed. Find out what type of furnace, and google the name, model, and the words, 3 blinking lights. Does your furnace turn on at all? Does it start to go through the cycle then stop? This is the proper cycle of a furnace and what should happen.
Inducer motor kicks on, it runs for a little bit, about 3-5 seconds, then you should see a bright yellow glow, this is the igniter, shortly after, you should hear a click and the gas should start to flow, almost immediately it turns to a blue flame. Then your igniter should turn off and the blower motor start up.
Mar 02, 2011 | Heating & Cooling
Heater unit will not ignite, will note fire up
Check your furnace by the electrical panel, there should be a blinking error light. Sometimes there is a legend to how many blinking lights means what. I had an issue with mine, read the code and it turns out it was hitting the high heat limit. Turns out my blower motor wasn't turning on. Replaced it with a spare and it was fixed. Find out what type of furnace, and google the name, model, and the words, 3 blinking lights. Does your furnace turn on at all? Does it start to go through the cycle then stop? This is the proper cycle of a furnace and what should happen.
Mar 02, 2011 | Goodman GMS90703BXA Heater
Hi, I have a vokera 726 combi boiler that will not ignite... when I switch on I can hear the fan but I cannot hear the ignition sparking then error code 01 shows up....hope you can help....many thanks
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution:You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem
Dec 28, 2010 | Heating & Cooling
It does not fire at all times igniter works, I can hear the gas valve when opens, some times it fires for a minute and some times does not fire at all
Problem: Your furnace will not ignite the gas to produce heat for your home. When a furnace has a bad ignitor what I see most of the time is the following sequence of operation:
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution:You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Dec 07, 2010 | Heating & Cooling
My furnace wont lite
Problem: Your furnace will not ignite the gas to produce heat for your home.The following is the sequence of operation and probable cause:
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch (or circuit breaker ) back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution:You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands (use gloves). If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Nov 29, 2010 | Heating & Cooling
I have a newer tappan heater and get 4 blinks on led for error code the unit starts up fine and has flame but flame goes off when blower kicks on
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution: You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Nov 26, 2010 | Heating & Cooling
Induction fan motor cycles on and off , with no call for heat
Carrier 58sxc120 won't ignite and I get a fault code blinking light of short long short don't know what it means.
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution: You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. Please see "limits, rollout switches & furnace control boards" further down on this page. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Nov 24, 2010 | General Heating & Cooling
York furnace model p2mpd12h06401f flashes 4 times for trouble code does'nt have code list inductor motor comes on but ignitor does'nt come on
Check pressure switch for inducer motor. If switch closes, check for crack in ignitor. If gas valve opens and you can hear/smell gas, the ignitor is bad probably. If pressure switch isn't closed you need to check for blocked vent/chimney/heatexchangers.
Dec 18, 2009 | York Furnace Draft Inducer Blower Fasco #...
Gas Furnace is not heating anymore.
the fan you hear come on at a call for heat is most likely just the inducer motor. the click you hear is probably the relay for the hot surface ignitor which should glow red, then in turn ignite the main burners. your going to have to determine if the ignitor is coming on. if it isnt the ignitor is bad and will need to be replaced. if it comes on and than shuts off after a few seconds the ifc board is probably at fault
Apr 09, 2009 | Heating & Cooling
Heating & Cooling Logo
103 people viewed this question