Reznor ft60 Fan not coming and limit shuts off burners
shastalaker7
  • 1515 Answers
SOURCE: burner lights but limit switch will not turn fan
Hi, Yes, you have the answer to you're problem. Now, I don't no if you have just a high limit, or a combination Limit control? I will go with the combination fan control as when they go bad, they stick in the closed position and they have normally open contacts. When the heat exchanger starts to heat on a call for heat, there is a dial on the fan control with temp. settings on it , and it will start to rotate as the heat gets higher. When it reaches its set fan on temp, it with start the fan.We no the fan works so the blower is good, so it shuts the burners down on you're high limit temp. which is factory set to about 250*F. When you turn The t-stat from auto to on in the fan side, that solves the problem temp, only. You will need to R & R the Fan control. If you need some direction on doing this please let me know and if it is a Honeywell auto/on type that is rectangular in looks, and if you remove the cover you will see the temp. dial with arrows on it. Thank you.
Best of Luck, and Sincerely,
Shastalaker7
Posted on Nov 21, 2009
  • 79 Answers
SOURCE: main blower stays on, burner fan on intermitantly,
All gas furnaces have a fan control of some sort. Either a mechanical fan control where there is a temperature probe that reaches into the heat exchanger compartment thru a hole in the panel that separates the control part of the furnace(this would be the front of the furnace where all the controls are) from the heat exchanger. This type of control is either a small black plastic control about 4 inches by 2 inches and about 1 1/2 inches thick secured to the panel with 2 screws. Or it is a slightly larger silver colored control that should have a pull off cover. It may say Honeywell on it. Either way the control will need replacing.
The other type of fan control is a solid state control board. This will most likely be located in the indoor fan compartment. It should be located under a covered control box. The box with all the wires going into it. This board will also need to be replaced if your furnace uses this type of fan control. You will need to bring your furnace model and serial number to a dealer that sells your brand of furnace or go online to a parts dealer that carries parts for your furnace. Hope I was of help to you! Good luck!
Posted on Nov 28, 2009
Therinnaiguy
  • 1420 Answers
SOURCE: t-stat turns gas valve on,burner lightsburns long
Probable causes include crack in heat exchanger, dirty pilot, bad high limit switch or bad gas valve. A crack can allow the fan to blow the flame off of the thermocouple or flame sensor. A dirty pilot will cause the same effect. The bad limit switch could cycle the system and a bad gas valve could be shutting off gas supply to unit.
Posted on Dec 03, 2009
  • 59 Answers
SOURCE: My cozy counterflow wall furnace burner comes on,
by pass the wall thermostat twist the wires together if unit runs and fan comes on the stat is the problem.
Posted on Oct 22, 2010
heatman101
  • 43501 Answers
SOURCE: main burner comes on and
There could be a couple of different things happening...
The most likely is that the high limit switch is bad and the flame causes it to bring on the blower and then shuts the flame down also...this could be because the high limit is bad or because the vent is blocked and the flue gases are not venting...
Could also be a bad/dirty flame sensor, but that is not as likely...
I would checkout the high limit and find out what is going on there...
heatman101
Posted on Feb 02, 2011
My good man furnace model gmh80903bnca will not get to temp fan shuts off and burners keep burning then kicks off on high limit then starts process over but never gets to temp set at 655
If you have a switch that can manually turn on the fan, try it to verify the fan works. This is what I think is happening. The normal operation should be thermostat calls for heat, inducer fan comes on, pressure switch closes, igniter glows, main burner ignites and then in 30 or so seconds the fan comes on and stays on until the thermostat is satisfied. Once the thermostat is satisfied the burner shuts off and the fan runs for approx 120 seconds then shuts off. I think the control board that automatically turns your fan on is faulty. On most modern furnaces if the auto fan control fails and the furnace gets to hot and limits, when the limit opens and shuts off the burner it also energizes the fan motor to cool the heat exchanger.
Jan 13, 2018 | Heating & Cooling
I have a reznor heater in my garage I have to keep lighting the pilot it wont stay lit.
i have an ole reznor in my garage been workiing for ten + years no problems , mine is gas , the pilot light does go out after it switches to main burner like ten seconds later , but does light back up when thermostat shuts main off ( i had to go look to make sure) not a real big flame maybe like an inch or so , has a spoon shaped air shield around it , maybe yoours is missing ?
Mar 02, 2015 | Heating & Cooling
My Ruud furnace used to regulate 1 deg +\- the set temp. Now it regulates right at the set temp and the fan cuts off while the burner continues to fire for a minute or so then the fan kicks back on for...
It appears to be the fan limiter switch. It comes on at a certain temp when heating up and shuts off on the high end of its setting. Once the burners are shut down, the fan continues for a few minutes to cool down the burners. The limiter switch is adjustable but it sounds to me to be defective and should be replaced. Good luck and stay warm, :-)
Mar 15, 2011 | Ruud Heating & Cooling
I have a reznor heater in my garage, it is flashing the code for open limit switch or open flame roll out switch, it will ignite but not put out any heat, and stay lit for a minute or two then go out. ...
I have the same issue, Appears that the fan does not start thus the high temp limit switch operates and the unit shuts down and the green light flashed three times. The open flame roll out switch is resettable manually in the top upper left of my unit. Were the manual shows the high temp limit switch, there is nothing visually located in the panel there.
Dec 11, 2010 | Heating & Cooling
My coleman 7900 furnace blower cycles on and off while burner continues to operate
I would look at fan limit switch. They are normally located in electrical cotrol compartment. If your are lucky you will have one thats adjustable. It would helpful if I knew is your home a mobile or modular home as they usually use a button type limit on fan and hi limit. It sounds to me like you may be having problems with fan limit which controls temp. that fan comes on . Often what happens is that switch scenses temp to turn on and then draws cold enough air on return air to shut back down until temp.rises again.If this occurs when unit first comes on or continues after burner shuts off you can get a limit switch with a higher temperature rating or one that has adjustable temperature range. Hope this helps you.Thanks.
Nov 06, 2010 | Coleman Heating & Cooling
Question on a day and night gas forced air heater
it very well sounds like your fan switch , does your fan work at all, like in ac mode on by turning the fan on/auto switch on the thermostat to ON. If the fan does come on its the more and likely the limit switch. if it doesnt come on it could be the motor or the run capacitor. the limit switch has a dial on it that as it heats up it spins clicking on at a desired set temp ussually about 120 to 150 degrees F. turning on the fan if the fan doen't come in the the next setting clicks off the gas valve turning off the burners ussually set at about 220 degrees F. now if the fan is working when the heater is satisfied there is a setting at about 90 deegrees F. that shuts the fan off hope this helps
Jan 05, 2009 | Honeywell L4064B2236 Fan/Limit Control...
Furnace come on then fan stops while burner still is on, then fan comes on for 1 min. and goes off over and over
This could be a couple of things, first is the fan limit switch. Make sure your fan limit is set at the correct settings, there is a fan on setting and a flame shut off setting located on the front of air handler inside the front cover. Usaully set at 140 fan on 200 gas shut off. You do not say what unit you have so this could be a pc board or module. Second this could be the blower it's self over heating and shutting down, feel if motor is gettig hot. This could be a run cap. or motor it's self. But it is more than likely the limit switch.