Heater won't light
The induced draft motor runs for a half second, then quits. No HSI glow or gas flow. LED on the circuit board blinks rapidly and continuously. According to the error codes on the inside of the panel, that indicates a "incorrect twinning" or "incorrect polarity".
the solution given is to reverse the transformer secondary wires or the primary wires. I have done both with no change in the operation of the heater.
  • 3 more comments
  • fstephens Oct 19, 2007
    Thanks so much for the response.
    I thought I put the make & model in the original message form, but somehow it was lost when I posted it. The heater is a Goodman MN:GMP075-3.
    The inducer motor turns very freely, and the resistance through its coils is almost nothing. The pressure switch also seems to be working fine (and I bypassed it to test once too). The HSI appears fine and has a resistance of about 75 ohms.
    The fan will run if I connect the green and red thermostat wires, but the error code still flashes. Nothing happens when I connect the red and white thermostat wires. The inducer motor only runs for the half second when I put power to the furnace with the red & white thermo wires connected. Reconnecting them with power on does not cause the inducer motor to turn.
    Any help greatly appreciated (as well as sources for wiring diagrams, troubleshooting info or parts).
  • fstephens Oct 20, 2007
    Yes I am talking about the same blower motor. I did as you suggested and I hear a relay on the circuit board click, the voltage goes to 110 momentairily and the drops to zero again. So I guess it is the board? That was the conclusion I was leaning towards, but I wanted to be sure before I order one.
    There are also 2 ground wires I cannot account for. One is a short green one that has no apparent place on the board or anywhere else to connect it to. It has a terminal end that supports connection of a second spade connector. The other wire is a long blue one. Both are connected to the chassis near the upper left of the circuit board. I see on the wiring diagram that there is supposed to be a ground hooked to one of the transformer's secondary connections, along with 2 blue wires. I wonder if this long blue one should go there too? Seems strange to me, but since the error code mentions the secondary wiring... There is no connector on the end of this long blue wire, so I don't know if someone previously cut the end off or what. I did try connecting it as the diagram shows, but that did not change anything.
    Do you know a good source for the circuit board?
    It is B18099-13.
    This site lists it:
    Thanks for your help. Any sources for troubleshooting info or diagrams welcome too.
    Thanks allot for your help.
    Really appreciated.
  • JPScott Feb 24, 2008
    Good Morning:
    I am having a heating problem as well. I had furnance maintenance completed on my unit and had the thermastat upgraded and replaced. The problem is the vents on the first floor of my home. Heat is not blowing uniformy out of the vents.. So that level is always cold. The bedrooms are almost hot because all the heat is blowing out of those vents but on the first floor heat only blows through one out of the four vents on that floor. Any ideas on what could be causing this? Thanks so much for your help.
  • Anonymous Dec 20, 2008
    heater wont ignite every thing turns on but no light
  • 1,420 Answers
Not having a make or model number, I can only give you generic information. However if you add more info, others and myself can give you a better diagnosis.
In order for a furnace to start that has an inducer motor, the thermostat must call for heat. Then the circuit board will flash rapidly. There should be power from the board up to the inducer motor. If there is too much resistance, the blower motor or pressure switch(s) will shut down the unit. I would suggest that if you can spin the inducer motor by hand, check for resistance. It may be frozen up or there may be water in the housing not allowing the blower to turn. Check for a plugged water drain at the bottom of the blower housing and make sure it drains. If the inducer blower does not even try to start, you will need to check for voltage from the circuit board. Not knowing for what you have for a model, I am unable to tell you if you should be checking for AC or DC voltage.
Get back to us as soon as you can with more info.
Thank you for your patience.
Posted on Oct 19, 2007
  • Chandler Ede
    Chandler Ede Oct 19, 2007
    I fear you have an issue with either the inducer blower motor or the control board. For some reason the relay is dropping out on the inducer circuit and then te unit just will not operate. You will need to hook up a meter to the 2 wires from the control board going to the inducer motor. Put your meter on AC voltage of about 200. Watch the meter, see if the voltage stays or drops out. If it stays at about 110, you have a bad inducer blower motor. If it drops out, bad board. Just to make sure we are talking about the same blower motor, the inducer motor is connected to the exhaust vent pipe and is not the blower in the bottom of the furnace cabinet.
    I hope this helps.
  • Chandler Ede
    Chandler Ede Oct 20, 2007
    There are a number of places on the web to order one. As far as the green and blue wires, The green one should be attached to chassis ground. I am not sure what the blue wire is for. Chack it for voltage when you get your new board. It may not be used, your wiring diagram may help.
    Good luck to you.
Burner on Bryant 90 PLUS won't turn on and it only blows cold air. I usually can see blue flame in the inspection window when the furnace was functioning properly. Is there a switch that I can reset to...
This system will not have a pilot light, instead it will have an electronic ignition or hot surface ignitor. The problem can be a number of things. You can check to see the operation of the unit by having someone turn the thermostat on while you are at the unit and go from there. The order of operation will be:
Inducer draft motor starts (small motor in heat compartment), after the motor runs and pulls the pressure switch in, telling the furnace that its safe, it then starts the ignitor. This will either sound like a clicking noise until the pilot lights or there will be a orange glow by the burners, after a few seconds, the gas valve calls and the burners should ignite.
By doing this, you can get more information to what the problem actually is. If your unit fails to start the inducer draft motor, fails to call for ignitor, fails to call at gas valve, fails to stay on after ignition. Your system should have a control board with LED trouble lights also. If you can see blinking lights, count the number of times they blink, then look for a trouble code chart, usually on the back of a panel. Hope this helps!
Dec 08, 2013 | Heating & Cooling
How to trouble shoot trane 80 gas furnce
The 1st thing I do is go to the thermostat and put the Fan switch from Auto to the On position. If the fan operates this proves you have both high and low voltages and the breaker, fuses, transformer etc is functional, this saves one from going to the breakers and air handler often in an attic or roof or basement.
If the fan does not operate then I check for correct power.
Set the thermostat for heat mode and turn the temperature setting well above the rooms temperature. and observe the furnaces sequence of operation.
What you normally expect is upon the white circuit from the thermostat being energized with 24 volts, the induced draft motor will cycle for 30-60 seconds typically to pre purge the heat exchanger, after this purge the induced draft motor has a pressure switch that senses the induced draft operation thus proving the induced draft motors running and alloqw the ignition to begin, either a spark or a HSI, hot surface ignition type.
If you see no bright white light or hear a sparking noise by the burner area this is normal, this will be followed by a trial period for ignition, meaning the gas valve will be energized for a 30 second trial period, during this time the flame rectification proves a flame exists by a DC signal being sent back to the module by the flame sensor or the ground/burner ground.
This DC signal is very weak and easily interrupted and this is why we clean flame sensors and simply re seating wiring will often times correct a situation,
The typical issues are the induced drat pressure switch and the orifice that it's tubing connects to on the induced draft housing.
This port must be reamed to clear carbon and if not will cause a problem such as locking out requiring resetting power or a 5 hour wait for some units,
You need to insure the limits and roll outs are all closed, its all failrly simple if the LED is tellingyou the error as they do today.
Feb 19, 2013 | Heating & Cooling
Carrier 48sx gas pack. Won't turn on. No smell. No igniting sound. Blower fan works. How do I troubleshoot this?
Remove the panel from the heater section, you will need to watch what happends as there is a call for heat. There may be a light on the control board that lights up or blinks to indicate a call for heat. The inducer blower (exhaust blower) will start. INn a few seconds after the blower starts, the igniter will glow orange. After a few more seconds the gas valve should open and the burner will ignite. If the inducer does not run, you may have a bad motor or control board. If the igniter does not glow, you could have a bad pressure switch, bad pressure switch hose or a broken igniter. If the gas valve does not open, you may have a bad control board or bad gas valve. If you get no light on control board, bad fuse, bad thermostat or bad control board.
Jan 03, 2011 | Heating & Cooling
I have a newer tappan heater and get 4 blinks on led for error code the unit starts up fine and has flame but flame goes off when blower kicks on
Problem: Your furnace will not ignite the gas to produce heat for your home. When a furnace has a bad ignitor what I see most of the time is the following sequence of operation:
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution: You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Nov 26, 2010 | Heating & Cooling
Have a Goodman GPG13 single package gas-electric heating and cooling unit. Turned on the heat and the outside unit ran a short time then shut off. Smelled gas after it shut off. Is this an igniter...
There is a induced draft motor that will run first to purge the combustion chamber and induce a draft, a pressure switch closes proving an induced draft exists, thus allowing the spark and pilot gas, or hot surface ignitir and gas to pilot rsil and /or burners, a trial period for ignition about 30 seconds each for 3 attempts will be made and if not lit by the 3rd attempt it locks out, requiring a reset of power to unit to reset the module or circuit board etc. 1st see what motors running, is it the flue exhaust motor/induced draft??
Nov 02, 2010 | Goodman Heating & Cooling
Turns on but no heat
From what I saw when I googled you furnace it has a hot surface igniter. It only gets hot when it's time to light the furnace. You should be able to see it glowing red when the furnace is trying to light. The furnace has a safety feature which shuts the gas valve when it doesn't detect a flame to prevent gas build up in the furnace. There are other safety features also. If the draft inducer motor isn't running the gas valve won't open. Overheat switches some of which have to be reset manually. Adjust the thermostat until it calls for heat then observe what is or isn't happening in the furnace. It will go thru a purge cycle first. The draft inducer motor will run to do this. After the purge the hot surface igniter should get hot a glow, then the gas valve will open and the burner will light. Let me know what you find.
May 04, 2010 | Goodman GMS90703BXA Heater
Bad control board?
This is a good one! I would check for a blocked vent or intake pipe first. Also check to make sure the condensate lines are free of moisture or debris. What is the code for three blinks?
Oct 11, 2009 | Goodman GMS807034ANA Heater
Armstrong v tech 91 furnace. will not make heat. when on unit runs continuosly no matter what thermistat is set at. could mother board be bad,replaced once already. cah this be done by the home owner to...
These furnaces goes thru 4--steps for complete run time.... step-1, the small draft inducer blower motor blows and prove thru the small air tube that sucks a switch close to tell the circuit board to go to step-2......the glow plug glows for 15 seconds and step 3 the gas valve opens and dump gas in the venturi tubes and lights off the glow plug and proves thru a flame sensor (pin with 1 electrical wire connection) on the last venturi tube which tells the circuit board to go to the last step 4--, to turn on the main blower fan after 90 seconds!. Where ever it stops at then thats where your problem is!
Sep 12, 2008 | Heating & Cooling
Heating & Cooling Logo
2,027 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Tim Whalen