My Heil Heat Pump outdoor unit is short cycling
My Heil model CH5024UKB3 is running in heat mode and blowing warm air inside (no air handler issues) and colder air outside (as it should). However the condenser is clicking and shuddering every 5 second. The fan is running but stalls briefly when the click occurs and then spins back up to speed immediately. The unit was manufactured in 1993, so this may be a dead dance, but might it be something simple to repair?
  • jason Dec 31, 2013
    Hi Gordon Bingaman, Does it maybe sound like brushes going on the motor ?
watugot
  • 290 Answers
SOURCE: Ruud heat pump outside unit trips circuit breaker
Check your wiring between the contactor and compressor for a short to ground, or check the compressor windings for short to ground.
With the Tstat off, the contactor should be open so the only way for the compressor to be trying to do anything is if the 110 volts from the unbroken side are traveling through the compressor to ground. Since 110v is not enough to run it, the overload is kicking it out, cooling off, and repeating the cycle. When you kick on the Tstat, the contactor is supplying voltage directly to ground without going through the resistence of the compressor windings and kicking the breaker.
Post back and let me know what you find.
Posted on Nov 20, 2007
hotuna
  • 288 Answers
SOURCE: ruud heat pump outside fan
You may be right in looking at the motor. It uses a different speed on heat than cool. The heat cycle uses low speed, usually red. Some manufactures use blue (medium). Cool uses black, high speed. If you are confident, switch the low speed wire with the high speed and see if this changes anything. If the fan motor isn't the problem, check the other setting (cool) if the overload trips, you may need to look into a new capacitor or compressor, if so, you can install a hard start kit. these are start boosters, and are inexpensice, sometimes they will give another year out of the comp. but I've put them on and they have lasted 5 years.
Posted on Mar 15, 2008
  • 124 Answers
SOURCE: York Air Handler trips main circuit breaker
almost has to be the electric heat strip coils. they usually come on in stages. when the damaged strip comes on it kicks breaker. turn off all power, check with a meter , gently remove strips and inspect for broken or shorted coils. usually best to buy a new heat strip module. they are usually held in place as a module with 4 screws and a snap together wire connector .good luck. i have had some success if the wires are broken and not to brittle by bending a minute loop in the end of each wire and reconnect with the tiniest screw and washer and nut you can find, i'm talking real tiny. about the size of a bb if you can find em , or you can remove the damaged strip wire entirely to get some heat from remaining.
Posted on Nov 23, 2008
drmengle
SOURCE: axu heat and outside blower fan run all the time
I can tell you exaclty whats wrong . and it sounds like multipart problems. you have an old RUUD heat pump and its reversing vavle is stuck. without that valve opening it will contantly try to run in refrigerant mode to make heat. and here its 26 degrees, het pumps are only made to be effiient in over 34 degrees and that why your electric heaters in the blower section in an in a closit of unit
continously running up you eectric bill big time. cuses for the reversing valve to stick are sitting along time when it was low on refrigernt. or ust plain shut depending on its age. that cicking is the relay trying to open or close the reversing valve swict to make pressure again. any local guy an fix that one. theyre are kits called hard start kits that they hook up to them that shoot an extra zap of jiuse in it to try to free it up if its not totally lockd up being though that you still hear the relays pulling in and out thats good you may have just caught it in time.
now here is a quick test and possible cure but only if you what your doing turn both units off take off the top cover of the old rudd and get a small hammer not a sledgehammer and rap and tap all around the reversing valve. it will be a cylindrical tube black usually have sets of copper or brass tubings going in the 2 sides of this so dont hit itthat hard it gets dents it and is ruined. look for oil spots which uually means the refrigerant leaked out , and its seized up for good. they try spinning around the big out door fan door fan some. you may have to rock it back and forth Till it braks lose but dont put super human efort int it,
than put it all bak together making sure you connected wires back up right. go in and have you wife eithe watch it or you do it and switch the breker on and off about 8 times to trying to get the cnnectors switches to stay in and if your brave take a well insulated screw driver and hold them in for 2-4 miuntes to force it to work. if that doesnt do it call your local repairman and tell him you need a hard startkit only much safer, the cost about 40$ but you labor will be high if he is sent alone so may you can help im out and lessen your bill if the valve cant be made to work again. you may want start looking for prices with that model and serial number and d shut that electric heater off some one to replace it . I hope I helped you out some no charge ( I dont have my Pay Pal acct. set up yet ) good luck tom.
Posted on Jan 12, 2009
mastatech
  • 478 Answers
SOURCE: Heat Pump Cycles On and Off and Air Handler Noisy
I am pretty sure you have a low charge and the pressure switch is kicking it off. probably just a pound or two however the accumulater will sometimes hold more.
Posted on Mar 31, 2009
Goodman gph1348m41ac unit is blowing cool air in heat mode with mid 30s ambient outdoor temp. I turn it off then on and will usually blow warm air but this cycle is becoming more repetitive. any expert...
A heat pump on the optimal heating day (about 50 degrees ambient) will only deliver approximately 85 degree air as compared to 125 degree air from a fossil fueled furnace. The colder the outdoor air is the less heat there is available to be transferred to the living space. At 30 degrees, the heat transfer capability is getting close to negligible meaning the run cycles will be approaching continuous and eventually as the heat pump along cannot maintain setpoint, the outdoor stat or stats will bring on auxilliary heat in the air handler.
If your ambient temp is below the 'balance point' of the heat pump, the house temp will drop a little lower and most times energize the heat strips through the outdoor t-stat. Your outdoor stat could be set too low for the heat pump to carry the structure all the way down to the balance point so when you turn it off and back on, the lower indoor temp automatically brings on the heat pump plus a heat strip or two, thus the warmer air. Second stage on the stat satisfies due to the heat strip, drops them out of the circuit and the heat pump is left running on first stage heat delivering the perceived cold air.
Your outdoor stat could also be not functioning correctly and not allowing the heaters to come on until the system is turned back on reestablishing the two stage call for heat.
Tons of possibilities and not enough room to list....
Jan 01, 2015 | Goodman Manufacturing Goodman GPH1348M41 4...
Hi, I have an LG artcool A09AHD aircon unit and after a while on the heat cycle, the unit stops and shows a circle with a snowflake and a waterdrop within the circle. Does anybody know what alarm tjis is?...
This may just be the defrost cycle for the outdoor unit. In the heat mode, the outdoor unit builds frost on the coil. The outdoor unit senses how much frost has built up on the coil and reverses the refrigerant cycle to allow the outdoor coil to warm up and defrost it. After a short period, the unit then restores itself to the heat cycle. This is normal operation and nothing to worry about. During the defrost cycle, you may feel some cool air inside your home.
Oct 26, 2013 | LG Heating & Cooling
My mistral reverse cycle mss25ss model does not work at all in heat mode. what would be broken?
firstly is the air comming from the outdoor unit cold or warm? if it is cold then the 3way valve is working and it has changed to heating. If it stays warm then it is still in cooling mode. The indoor fan wont come on until the coil temp gets warm enough, ( so it doesnt blow cold air on you straight up). If it is changing into heat mode then the larger of the pipes connected to the outdoor unit should get warm/ hot. If this is not happening then the unit is either out of gas or the compressor is on hollidays and wont come back to work.
May 22, 2012 | Heating & Cooling
WIRING THE THERMOSTAT TO AC UNIT THEN FROM THE UNIT TO HANDLER
Generally, you would go from the thermostat to the air handler, and then, from the air handler to the outdoor unit. I don't know if you have a heat pump or not, so I will give you a simple diagram and you can contact me if you need more.
Thermostat : Y G R W and sometimes C
Air handler: Y G R W and C
Outdoor unit: two wires connecting to the contactor ( not heat pump)
Thermostat; Y--------------Y(air handler cooling)------------------one side of contactor, outdoor unit
G-------------G (air handler, fan)
R--------------R (air handler ,hot)
W-------------W (air handler, heat)
C--------------C (air handler, common)------------other side of contactor, outdoor unit
This is a typical wiring diagram. Just contact me if you have something different. Hope this helps. Stay cool. mark
Jul 10, 2011 | Heating & Cooling
I installed 18 seer heat pump&air handler with communicating stat,i turned power on to air handler,not heat pump,stat learned air handler&heaters properly.turned power on to heat pump,stat does not...
Dont know what equipment you have but yes of course there is a fix. Turn power off to air handler. cycle power to heat pump and be sure the board is configured properly to match your outdoor unit. Then turn power on to indoor unit and likely go through system setup once again. provide model numbers of all communicating components if more problems.
Dec 10, 2017 | Goodman Heating & Cooling
Heil Max Performance 10 Heat Pump not working
First check to see if you have afloat switch inside the air handler ar underneath the air handler. Its purpose is to shut the outside ac off if the drain stops up. Very common. If this is OK take cover off unit and with screw driver push in the contactor. It is located about the middle of the panel. It has main power at the bottom. If unit comes on you cave a control voltage problem. Meaning something is not allowing 24 volts to the contactor. If your out of Refrigerant the low pressure swich will have it off. Call a service tech. Rusty
Jun 09, 2009 | Heating & Cooling
Uotside unit blowing cool air but hot on the inside
It sounds like you have a unit called a heat pump. When a heat pump unit is in cooling mode the outside unit blows hot air and the inside unit blows cold air. If the outside unit is blowing cold then the indoor unit is most likely blowing room temperature or warm air. It sounds like the thermostat could be controlling incorrectly or you could have a failed reversing valve which is the device that switches the unit from heating to cooling mode.
May 31, 2009 | Ruud UBHC Air Conditioner
My air handler comes on ,not the outside unit when my thermostat is in the off position even if i turn the thermostat down to 50 and have it turned off the air handler comes on for about 5 to 10 minutes...
If you have a standard thermostat the fan switch is for the air handler only. It completely over rides the thermostat for most settings. Now lets see this is what I'd expect:
fan switch on Indoor fan runs all time
Fan switch auto Indoor fan only runs when thermostat is set to cool or heat and the thermostat is turned up above room temp for heat or below room temp for cooling. In both of these modes the furnace blower comes on and stays on til the room temperature is satisfied. The outdoor unit only comes on for AC the out door unit will not come on for heat or the "on" setting on the thermostat. See exception 1 & 2 below...
Exception 1- (in a heat pump the out door unit runs in both heat and cool mode unless it has emergency heat turned on then it will not come on outside in the heat mode, and depending on the type of heat pump and furnace or air handler it is). A heat pump thermostat usually has "backup heat" and an "emergency heat" setting switch on the thermostat.
Exception 2 - On some thermostats they are made to cycle on the heat if the temperature reaches a preset temp (around 50'f usually but definitely by 40'f). This mode prevents freezing when if instance the homeowner is away or while the home is under construction. In this mode the fan inside can run but the heat usually comes on with it.
Exception3 - On some electric furnaces the heating strips may be individually controlled and thus not all come on at one time. This may give the feel of no heat especially if the room is cold.
Now there may be other exceptions but Ive tried to give you a heads up on some of the most common ones.
If you need more help please post more specifics about your unit/system as to for sure what switches are set to what setting and what is happening with each. My first though was that maybe your system is OK and you needed to know if the thermostat was working properly.
If this helpd you understand your problem would you please give me as hifgh a mark as you can. Thnaks for using fixya and good luck.
Mar 28, 2009 | Carrier Heating & Cooling
Ruud heat pump question
Does the air handler take a minute or two to start, this would be normal so that it doesn't blow cool air into the house before the unit is warmed up. If not could be the fan relay is weak and needs replacing. As far as the outside unit it sounds like you need to check the refrigerant. In cooling they are 70/150 psi. This should be checked in cooling mode, once you turn it to heating mode the pressures switch bring heat inside the house instead of out. I hope this helps.
Oct 23, 2008 | Ruud Heating & Cooling
Wiring connection for a Ruud air handler & seeking its wiring diagram.
we are trying to install a goodman heat pump with a rheem air handler, the orange wire is hook up and the unit is still staying in the heat mood. does anyone have a wiring diagram for the air handler, their is some white wires in the air handler one with a purple strip and one with a black strip we need help
Jan 05, 2008 | Heating & Cooling
Heating & Cooling Logo
63 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Tim Whalen