Question about Braeburn 1220NC 2 Heat/1 Cool Non-Programmable Thermostat - Builder Series
Heat pump won't come on
Air handler runs but outside unit dosen't
Heat pump problems
Some heat pumps have high and low pressure swiches installed to keep compressor from running when unsafe conditions occur that can damage the compressor. If the outside fan is not turing on, the unit is cycling on high pressure, if you see ice forming on the big refrigerant line coming from the air handler, then the compressor is shutting down on low pressure. Low pressure can be cause by lack of air flow through air handler or from a low refrigerant charge.
Feb 13, 2014 | Intertherm Heating & Cooling
Hey, I purchased your Honeywell RTH2510 Thermostat, but I didn't even think to label the wires when I took the old thermostat off. Upon installation of the new Thermostat (2510) the Air Conditioning...
The connections that you really need to reference would be at the air handler itself. That would tell you which wires go outside to the heat pump and which wires go to the air handler. I can however give you some basics that may help.
Heat Pump Wiring
Terminals/Colors/Function
R- Red- 24v power supply. (Usually a jumper between RC/RH)
G- Green- Fan
W- White- Heat (Sometimes W1-W2, first or second stage heat)
Y- Yellow- Cooling (Same applies as above i.e. Y1-Y2)
C- Common (Most people use blue unless it is used for B terminal and sometimes cooling on older 4 wire systems.
B/O- Reversing Valve for heat pump. Either powered heating or powered cooling, depending on system installed.
Aux- Also used for heat.
Note: Considering that the installer had their own way to run all wires, use different wires, connections, etc. This is just a reference to common wiring in the field.
How the most common system is hooked up:
Thermostat:
Red wire goes to R terminal
Yellow wire goes to Y1 or Y2 terminal
Green wire goes to G terminal
White wire usually goes to W1 or W2 terminal
Orange or Black wire goes to B/O terminal
Brown wire usually goes to Aux terminal
Blue wire goes to C terminal, unless its being used as stated above.
This is without using a fossil fuel kit or zone control board.
Where do they go from the thermostat?
Red
goes to the air handler transformer or board and goes outside to heat pump to power low voltage controls.
Yellow wire goes straight outside to Y terminals on heat pump unless going to a board inside first.
Green goes to the air handler fan relay.
Common goes to the air handler and outside to heat pump.
Black or Orange will go outside to heat pump terminals for reversing valve.
White usually goes outside to heat pump,and inside to air handler. Will explain reason further down.
Brown will go to the air handler to the heat relay for the emergency heat.
On a call for heat, with a powered cooling system (more common).
The R, Y, and G terminals energize, sending a signal to start the blower and pull in the contactor outside. Note that the Y terminal is usually cooling, but since this is a powered cooling system, the reversing valve is not energized, causing the system to run in heat mode. If you have powered heating, the reversing valve terminal will energize also. Depending on thermostat, if you set the temp substantially higher than room temp, it may kick on the emergency/aux heat to quickly raise the room temp. On a call for emergency/aux heat, the R, G, and E/Aux terminals are energized, turning on the electric/gas heat instead of the heat pump. This comes in handy since the heat pump can only pull so much heat from outside before its not enough to properly warm the house, usually around 30 degrees outside temp. If you are running the heat pump and the system goes into "defrost", the outside unit will send a signal back to the air handler, through the white wire I mentioned earlier, to tell the emergency/aux heat to come on while it is in defrost mode, providing heat whenever needed.
Again, this is just a reference guide to some basic wiring, but hopefully it will tell you where the problem is or at the least, give you a good start. There are variables in which things can change the wiring like a zoning system or fossil fuel kit. Even then, you should be able to get pretty close. Hope this helps and Happy Holidays!
Dec 07, 2013 | Honeywell Programmable Thermostat Heater
HE heat pump won't talk with old air handler?
The fact is, the air handler supplies the voltage, blower, and electric heat. In order for the heat pump to work correctly, the wiring from the thermostat and heat pump need to be hooked up right to the air handler. The thermostat is what tells which component to come on. If the fan stops, but the condenser keeps going, you either have a faulty fan relay on the air handler, faulty thermostat or wiring, faulty wiring at the heat pump, or the contacts on the new unit are sticking, which is highly doubtful considering it is working now. I hope I have helped you understand this a little more. Good luck and don't let them push you around, get someone that knows what they are looking at.
Jul 18, 2012 | Goodman Heating & Cooling
What does aux mean on a honeywell Thermostat? the heat doesn't seem to be working but warm air is comming from the vents and the heat pump fan is spinning just not enough to match the temp. it's set too....
The aux switch is for electric heat banks installed in the air handler. Depending on the outside temp. it may not be efficient to run in heat pump mode but in aux. or emergency would run the electric heat in the air handler.
Dec 11, 2009 | Goodman Heating & Cooling
I have a Ruud air-conditioner/heat pump and it blows 5 amp fuse.
It sounds like the thermostat wire going to the condenser is ground, It either got pulled loose and is touching the housing or as in most cases the wire got cut or was chewed by an animal. You need to turn electric off to both devices and physically inspect the thermostat wire going from the air handler to the outside unit, also inspect where they connect inside the unit. When you find the break, cut and strip each individual wire and securely wire nut each conducter red to red white to white and so on. There you go all fixed. That's when I give you the bill for $75...except this time you write that check to yourself. Good Luck
Jul 14, 2009 | Ruud UBHC Air Conditioner
My air handler comes on ,not the outside unit when my thermostat is in the off position even if i turn the thermostat down to 50 and have it turned off the air handler comes on for about 5 to 10 minutes...
If you have a standard thermostat the fan switch is for the air handler only. It completely over rides the thermostat for most settings. Now lets see this is what I'd expect:
fan switch on Indoor fan runs all time
Fan switch auto Indoor fan only runs when thermostat is set to cool or heat and the thermostat is turned up above room temp for heat or below room temp for cooling. In both of these modes the furnace blower comes on and stays on til the room temperature is satisfied. The outdoor unit only comes on for AC the out door unit will not come on for heat or the "on" setting on the thermostat. See exception 1 & 2 below...
Exception 1- (in a heat pump the out door unit runs in both heat and cool mode unless it has emergency heat turned on then it will not come on outside in the heat mode, and depending on the type of heat pump and furnace or air handler it is). A heat pump thermostat usually has "backup heat" and an "emergency heat" setting switch on the thermostat.
Exception 2 - On some thermostats they are made to cycle on the heat if the temperature reaches a preset temp (around 50'f usually but definitely by 40'f). This mode prevents freezing when if instance the homeowner is away or while the home is under construction. In this mode the fan inside can run but the heat usually comes on with it.
Exception3 - On some electric furnaces the heating strips may be individually controlled and thus not all come on at one time. This may give the feel of no heat especially if the room is cold.
Now there may be other exceptions but Ive tried to give you a heads up on some of the most common ones.
If you need more help please post more specifics about your unit/system as to for sure what switches are set to what setting and what is happening with each. My first though was that maybe your system is OK and you needed to know if the thermostat was working properly.
If this helpd you understand your problem would you please give me as hifgh a mark as you can. Thnaks for using fixya and good luck.
Mar 28, 2009 | Carrier Heating & Cooling
Ruud heat pump question
Does the air handler take a minute or two to start, this would be normal so that it doesn't blow cool air into the house before the unit is warmed up. If not could be the fan relay is weak and needs replacing. As far as the outside unit it sounds like you need to check the refrigerant. In cooling they are 70/150 psi. This should be checked in cooling mode, once you turn it to heating mode the pressures switch bring heat inside the house instead of out. I hope this helps.
Oct 23, 2008 | Ruud Heating & Cooling
Heat pump not running
Depending on the age of the unit it could be several things, does it have a circuit board? Contactor could be bad, freon leak if it has a low pressure switch, burnt wires, connections, etc. Do a complete visual and check for 24 volts, does the indoor unit run? Transformer may be bad.... No indoor unit - no outdoor unit, most of the time the outdoor unit gets its 24 vac power from the indoor unit which runs them both, look for fuses (like car fuses)..
Apr 26, 2008 | Heating & Cooling
Wiring connection for a Ruud air handler & seeking its wiring diagram.
we are trying to install a goodman heat pump with a rheem air handler, the orange wire is hook up and the unit is still staying in the heat mood. does anyone have a wiring diagram for the air handler, their is some white wires in the air handler one with a purple strip and one with a black strip we need help
Jan 05, 2008 | Heating & Cooling
Braeburn 1220NC 2 Heat/1 Cool Non-Programmable Thermostat - Builder Series Logo
35 people viewed this question
Top Braeburn Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Donni Steen
Are you a Braeburn Heating and Cooling Expert? Answer questions, earn points and help others