Furnace will not light
3 lights blinking It means according to codes that there is a pressure switch error. How do I reset this ? Randy
  • 468 Answers
Most furnaces can be reset by turning the power off and back on.
The pressure switch senses pressures in the furnace to make sure the exhaust fan or draft inducer is operating properly. if not the furnace shuts down. check the inlet and exhaust terminals outside for obstructions (I.E: leaves,frost or snow) check the drains to make sure they are not clogged . Hope this helps.
Posted on Dec 30, 2013
  • 54 Answers
SOURCE: Ruud achiever 90 plus wouldn't start
Thanks for the carefull description of the fault, The vent system is designed so that if a leak occurs fresh air from the living space will be pulled into the vent rather than dangerous combustion gases pushed out to insure this there is a carefully calibrated -pressure switch that will not allow the unit to fire unless a negative pressure on the vent is proven this can be prevented by many things, here are a a few :a sticky micro switch, a leaking hose from the vent to the pressure sensor, cold stacking in the flu(either a down draft or extremely cold air in vent that restricts warm combustion air from being pushed out), a problem with the power exhaust fan(debris has gotten in the housing preventing an easy start), i usually find the cause to either be a bad pressure sensor hose or debris in ths exhaust fan housing either blocking blade movement or obstructing the pressure sensor hose port.
To clear the fault turn of the breaker to the unit then restart the unit and fallow the sequence of operation to see where the fault occurs the fan should come on first then the exhaust blower should come on when negative pressure is achieved it start the lighting sequence if the lighting sequence doesn't start and you get the same fault take the neg pressure hose loose from the exhaust fan housing and start the sequence again while pulling a slight negative pressure on the pressure sensor with a hand held pump continue this process until you find the fault.
Posted on Mar 11, 2008
SOURCE: The led indicator blinks 3
Pressure switch open. Remove the small hose at the blower assy and gently **** on it. You should hear the switch on the other end of that hose change states. If not then it's the hose (cheap) or the switch (100 bucks but tough to find 2 years ago) or the wiring to/from or the control module. If it does do you have a bunch of white **** (the gasket) coming out of the black blower mount? I had to remove broken gasket and Permatex the seal to create the proper pressure; that's probably your problem as well.
Posted on Oct 03, 2008
tborn6
  • 700 Answers
SOURCE: Trane Furnace xv-80
check the pressue switch and make sure that nothing is in the fan that would cause it to not draw. I have seen water inside of them at times due to the high efficentcy of the units. let me know if this does not solve it please.
Posted on Jan 01, 2009
  • 5 Answers
SOURCE: High limit switch open on armstrong furnace
If you know where the high limit switch is you can always cut the two wires and wire them together causing the limit to close. But what you have to watch out for is why the high limit is not closing. That means in your return air either you have a dirty return air duct, dirty filter, or you don't have all your registors open to allow the heat to escape the heat exchanger. Just watch over riding the system. The high limit switch should either be on or behind the blower, in the middle of the system right under the heat exchanger. any other questions about hvac just ask.
David
Posted on Jan 17, 2009
Therinnaiguy
  • 1420 Answers
SOURCE: Ruud Achiever 90 Plus - furnace won't ignite.
Jump out the switch as it first starts then take the jumper off as it ignites. If it starts, its the switch. If not, its the circuit board.
Posted on Feb 13, 2010
Testimonial: "furnace stayed on when the switch was jumped - must be the switch then. Thanks!!"
Error code= two red flashes, lockout/ no flame
Trane XV80 hard lockout, 2 flashes, Can't be reset - DoItYourself ...
www.doityourself.com > ... > Gas and Oil Home Heating Furnaces
Jan 10, 2013 - The only way I can get diagnostic Red LED light to reset is to switch ... a2 flash with absolutely no operation from the furnace does seem to ..... inducer gets a demand you should get a pressure switch error code 3. ... the flame sensor wire and giving the furnace a heating demand after resetting power twice. Luxaire Furnace Blowing Cold - 8 Red LED Flashes
Mar 1, 2010
Winchester furnace diagnostics
Feb 14, 2010
American Standard Freedom 80 - Cold Air - Getting Error Code 9 ...
Nov 20, 2009
York ignition lockout due to retries
Dec 29, 2008
More results from www.doityourself.com
7 Tips and Tricks to repair your Furnace DIY - YouTube
? 13:25
https://www.youtube.com/watch?v=rAtcvPqUsBA
Dec 18, 2012 - Uploaded by JRESHOW .
cause this fault. 2 RED FLASHES: This indicates that thenormally open pressure ... The furnace will lock out for one hour and then restart. 7 RED FLASHES: This fault code indicates that the flame could not be established. This no-light ... problem. Bothheating and cooling operations will be affected. Check
Jan 23, 2016 | Heating & Cooling
My Xenon high efficiency furnace has a red blinking led light that blinks 4 times and my furnace will not light. What could be the problem?
Gas furnace fault or error codes for common furnaces - Gray ...
www.grayfurnaceman.com/-ifc-failure-codes.html
Each color will also flash a specific number of times to signify a specific error. ... 4 redcolored flashes may be signaling that the "high-limit" switch might be open. ... 3 green colored flashes on your furnace has the same meaning as 2 green colored flashes. ....If a system problem occurs, a blinking LED shows a fault code.Missing: xenon
? 13:25
Flash sequence codes 1 through 11 are as follows: LED will turn "on" ... 4 RED FLASHES: This indicates that the main limit switchhas opened ... This no-light condition occurred 3 times (2 retries) during .... My furnace trane xe80 is only flashing once my manual says something about flame being locked out ...Missing: xenon ‎efficiency
Nov 21, 2015 | Heating & Cooling
I have an Olsen furnace. It's not running and there is a red light blinking. What's wrong?
Count the blinks in between pauses. On the door of the furnace will be a legend that tells you what that number of blinks mean. For instance 3 blinks may mean open limit switch or pressure switch failed to close, something like that. Post here what it tells you then we can help.
Mar 23, 2015 | Heating & Cooling
Amana Air Command 90 furnace LED light blinks 3 times pause 3 times
TRI-COLOR (DSI LED) DIAGNOSTIC TABLE
No. of Red BLINKS
1 Flame sensed when no flame should be present
Verify the gas valve is operating and shutting down properly. Flame in burner assemble should extinguish promptly at the end of the cycle. Check orifices and gas pressure.
2 BLINKS Pressure switch stuck closed/ inducer error
Pressure switch stuck closed. Check switch function, verify inducer is turning off.
3 BLINKS 1st-stage pressure switch stuck open/inducer error
Check pressure switch function and tubing. Verify inducer is turning on the pulling sufficient vacuum to engage switch.
4 BLINKS Open limit switch Verify continuity through rollout switch circuit.
5 BLINKS Open rollout/open fuse detect Verify continuity through rollout switch circuit, check fuse.
6 BLINKS 1st-stage pressure switch cycle lockout If the first stage pressure switch cycles 5 times (open, closed) during one call for heat from the thermostat the control will lockout.Check pressure switch for fluttering, inconsistent closure or poor vacuum pressure.
7 BLINKS External lockout (retries exceeded) Failure to sense flame is often caused by carbon deposits on the
flame sensor, a disconnected or shorted flame sensor lead or a
poorly grounded furnace. Carbon deposits can be cleaned with
emery cloth. Verify sensor is not contacting the burner and is locatedin a good position to sense flame. Check sensor lead for shortingand verify furnace is grounded properly.
8 BLINKS External lockout (ignition recycles
exceeded where flame is established and then lost)Check items for exceeded retries listed above and verify valve is not dropping out allowing flame to be established and then lost.
9 BLINKS Grounding or Reversed polarity Verify the control and furnace are properly grounded. Check and reverse polarity (primary) if incorrect.
10 BLINKS Module gas valve contacts energized
with no call for heat Verify valve is not receiving voltage from a short. If a valve wiring is correct and condition persists, replace module.
11 BLINKS Limit switch open - possible blower
failure overheating limit Possible blower failure, restricted air flow through appliance or duct work. Verify continuity through limit switch circuit and correct overheating cause.
12 BLINKS Module Ignitor contact failure Fault code indicates the module ignitor contacts are not functioning
properly. Replace module.Solid Module - internal fault condition Module contacts for gas valve not operating or processor fault.
Reset control. if condition persists replace module.
3 double 2nd-stage Pressure Switch Stuck Open/Inducer Error
Check pressure switch function and tubing. Verify inducer.
Nov 11, 2013 | Patton Electric Patton PUH680-U Electric...
I have a Goodman GMP 125-5 furnace. It had a 3 light code i replaced the presure switch now it is giving me a 1 light code please help
A sampling of various failure codes on a furnace:
Read one LED flash that stays on continuously to mean your furnace has no signal coming from the thermostat and will not operate. Turn the power off and check the thermostat for improper settings or connections.
Interpret one LED flash that blinks on and off to mean your furnace has locked out because it could not ignite after three tries, and must be reset. Interrupt power to your furnace for 20 seconds or lower the thermostat so your furnace does not try to heat, then reset the thermostat to the previous setting. After one hour of lockout, your furnace will automatically reset itself and try to operate as usual.
Decipher two LED flashes to mean the draft blower is not working, or your furnace has a short in the pressure switch circuit. Turn off the furnace power and repair a short or replace the pressure switch.
Read three LED flashes to mean your furnace has an open pressure switch circuit or it has an induced draft blower operating. Check the pressure switch hose of your furnace for blocks or an improper connection. Also, look for blockages in the flue, and tighten any loose wiring.
Translate four LED flashes to mean your furnace has a primary limit circuit open, possibly from loose wiring or blocked filters. Check and clean filters, tighten wiring and check the flue for blockages.
Interpret five LED flashes to mean your furnace senses a flame without a call for heat. This could be from a gas valve closing slowly or a burner flame lingering.
Read seven LED flashes as a warning of a low flame sense microamp signal. This could happen with a coated flame sensor or a lazy flame from poor gas pressure. Turn off the power and adjust the gas pressure according to the information on the rating plate.
See eight LED flashes as meaning an igniter circuit problem due to a bad igniter or an igniter connected improperly. Replace the bad igniter or check the ground wiring, making necessary corrections.
Decipher nine LED flashes to mean the high-stage pressure switch circuit will not close during a high-stage-induced draft blower operation. Your furnace may have a pinched or blocked pressure switch hose, a blocked flue or loose wiring.
Read continuous flashing on the LED to mean your furnace has a reversed polarity of 115 volts. Turn off the power and correct the wiring polarity after reviewing the wiring diagram.
If you need further help, reach me via phone at https://www.6ya.com/expert/dan_73bbd84fe1d95b61
Oct 28, 2011 | Goodman Heating & Cooling
My central heating is on lockout and the burner is with red light
A sampling of various codes on a furnace
Interpret five LED flashes to mean your Goodman furnace senses a flame without a call for heat. This could be from a gas valve closing slowly or a burner flame lingering.
Dec 02, 2010 | Heating & Cooling
I have a Goodman GMPN080-4 furnace. The light on the board blinks 3 times. The furnace won't light at all. What could be the problem?
Hi 3 blinks should mean it is the pressure switch there should be a code in the manual or inside of the door
Jan 30, 2010 | Goodman Heating & Cooling
Goodman GMS90904CXA Wont ignite, light blinks 3 times
Ok, you either have a inducer fan issue or a pressure switch issue or a plugged vent pipe. The inducer turns on to establish a draft for the exhaust. If it is not working you will get this error code. If the pressure switch does not sense pressure caused by the inducer, it will give this code. If either the intake pipe or exhaust pipe is blocked (even y just a little) it will give you the same error code. If the condensate hose or receptical is plugged, again it will give you this error code. Good Luck!
Oct 20, 2008 | Goodman GMS90703BXA Heater
Ruud Achiever 90 Plus wont start
4 blinks is "pressure switch closed" there are 2 in the system according to the wiring diagram one for the vent system  and one for the drain system ... I just wiggled them and heard one "click" the fault light quit blinking and when I pushed the safety switch back in the furnace fired right up.  That being said is there a good website for learning how to maintain your own furnace?  I'll call a pro if I have to, but shoot I can fix a jet engine... this shouldn't be much worse.
Thanks  dan
Jan 19, 2008 | Ruud UBHC Air Conditioner
Heating & Cooling Logo
Top Heating & Cooling Experts
Paul Carew
Tim Whalen