Reason of the three-phase UPS system stoped by cross current
One of the thee-phase UPS stoped by cross current. Someone put up the UPS breaker (before the time, other UPS did bypass driving). Then the UPS condender exploded. After that, other UPS was stop by overload.
We have to make a explanation report to our custmer this month.
Please tell us our problem, especially the reason that UPS stoopped by the cross current.
    Problem Solver:
  • 14 Answers
The APC 1400 is a single phase device...I'm not sure what it is that transpired can you explain a little more in detail please
Posted on Jun 01, 2009
How i can change input configuration of APC SURT15KRMXLI from single phase to three phase
http://www.apcmedia.com/salestools/KCHY-94P5CN/KCHY-94P5CN_R0_EN.pdf?sdirect=true Try page 6 of this document. It shows the connections and jumpers required. Make sure changes are made by a qualified electrician/technician who knows what they are doing so as not to damage UPS and not receive electric shock
Oct 14, 2015 | APC SMARTUPS RT 15KVA RM 230V...
Wells deep fryer 208 volt 3 element. 1 element works other two don't working left to right. Continuity good resistance good. Relay problem?
Sounds like this maybe a three phase unit and you are powering it off on single phase power. Most can be converted to single phase but will draw three times the current and requires some wiring changes. It needs to be on a three section breaker for 3 phase.
Jul 21, 2014 | Kitchen Appliances - Others
Www eemaxinc com support
My limited research indicates this heater is designed for USA electrical systems. That would mean single phase, 240/208 volts, 60 Hz. The drawings I reviewed shows a 2 pole, 240 volt breaker feeding each heating circuit. That means no "neutral wire" goes to the heater and therefore no 120 volts is needed. This is good. Kenya's system is single phase, 240 volts, 50 Hz. The heater should work reasonably well on the African system. Connect the power just like you would in the US.
Jan 17, 2014 | Water Heaters
How can i get single phase power from my 3 phase generator
I have not wire this myself
Wiki says under heading of single-phase:
http://en.wikipedia.org/wiki/Three-phase_electric_power
Single-phase loads may be connected to a three-phase system in two ways. A load may be connected across two of the three phase conductors or a load can be connected from a live phase conductor to the system neutral. Single-phase loads should be distributed evenly between the phases of the three-phase system for efficient use of the supply transformer and supply conductors. Where the line-to-neutral voltage is a standard utilization voltage (for example in a 230 V/400 V system), individual single-phase utility customers or loads may each be connected to a different phase of the supply. Where the line-to-neutral voltage is not a common utilization voltage, for example in a 347/600 V system, single-phase loads must be supplied by individual step-down transformers.
So it sounds like you take 2 legs of the 3-phase.
or
Take one leg of the 3-phase and connect to neutral ... neutral could be a ground rod.
I would put a meter on that circuit before hooking up my power saw.
Nov 17, 2010 | Electrical Supplies
What is the use of wye delta?
I don't know why your question is bound to this special breaker.
If your question is common, the wye/delta is a way to reduce the starting current of a large three phase asinchronous motor.
When a three phase motor is first connected in wye (star), the starting (peak) current is about 3 times less than this in delta. When already in motion the electromotive force will make the peak current when turned in delta much less, than that with a stopped motor.
Aug 08, 2010 | RTO Telemecanique Gv2 Ls22 Magnetic...
How do you calculate low phase voltage of a three phase four wire system without useing voltmeter?
u can take three incadescent bulbs of same rating, connect them in 3 phase star connection, means 3 phase 4 wire connection..connect it across supply..the bulb connected across low voltage phase will glow dimmer than other two
Jun 19, 2010 | Zenith ZTG Nema-3R, 400 Amps Three Phase,...
How to solve single phase lost in UPS at input end
What size UPS and make and model?
First make sure your utility is reaching the UPS and it's not on that end, sounds like the problem might be with your input power not the UPS.
If power is getting to the unit, you may have a failed power component internally, such as a fuse or transistor.
Nov 05, 2009 | Zenith ZTG Nema-3R, 400 Amps Three Phase,...
Batteries
If you go to www.batteryinternational.com they can help you locate the correct battery for your UPS system. Hope that helps
Feb 11, 2009 | Powerware Best Power Unity/I Three-Phase...
Zenith ZTX transfer switch, three phase 150 amp
if the s2 and load are flashing every couple of seconds that means your exerciser is set.
Oct 03, 2008 | Zenith ZTG Nema-3R, 400 Amps Three Phase,...
FAULTY MGE UPS
a 3 ph ups normally can work upto 450 volts because the normally its the transmisson range of voltage
220 to 250 is the voltage range of normal 1 ph line so check for proper line voltage or load voltage
Nov 06, 2007 | Computers & Internet
NEC APC Smart-UPS 1400 (050-01803-000) UPS System Logo
170 people viewed this question
Top NEC Computers & Internet Experts
Steven Wander
Steven Wander
Martin Murray
Are you a NEC Computer and Internet Expert? Answer questions, earn points and help others