Question about True Refrigeration True T-49 2 Door Bottom Mounted Reach-In Refrigerator
True freezer not cold enough
Were is the thermostat located
Posted on Mar 13, 2015
    Sergeant:
  • 236 Answers
Things to check are:
Is the thermostat set to the correct temperature (Low, Med, High)?
Are the door seals in good repair and making a good seal with the freezer cabinet frame?
Is the door warped or distorted in any way, will lead to leaks.
Can you hear the compressor/motor running?
Posted on Jan 08, 2014
Fan not working
Generally I would check for power at the fan wiring because there are several components that can keep it from running. If the fan does have power change the motor. But if it doesn't is the coil frosted and cold enough to let the fan thermostat switch close?
Is the door switch good? Hope this helps good luck.
Aug 06, 2014 | True T19F Commercial Freezer
True GDM-72f freezer Fans don't start
Thermo fuse has failed on the core plate, tells the freezer its cold enough to start blowing air, you can bypass it but not recommended. hope that helps, Russ
Jun 11, 2011 | True 72 cu. ft. / 2039 liter Commercial...
The compressor is running but the fans are not spinning so no cold is coming out.
Coil must be cold enough for the fan delay to turn fans on. If it is and no fans replace delay
Mar 08, 2011 | True 72 cu. ft. / 2039 liter Commercial...
The fan on my true t 23f does not run. i check it is not getting power is there a fuzz or capacitor for this thanks
Are you talking about the fan inside the freezer? If yes, check the following items. The door has a switch that turns the lights off when the door closes, it also turns the fan off when you open the door. If it isn't working right the fan won't come on. There is also a round temperature senser on the coil inside the freezer called a "clickson" that keeps the fan from coming on until the coils are below 20 degrees, it may be bad. If you are low on freon, your coils may not be getting cold enough to trip the clickson. Feel of the small copper line going from the compressor to the coils on the outside of the freezer. It should be almost hot enough to burn your skin if you have enough freon. One other thing to check is the defrost timer. It is a box about 4 inches wide and 8 inches tall with a door on the front of it. Check the connections inside to be sure you are getting power through to the fan. Let me know how it turns out.
Oct 04, 2010 | True 23 cu. ft. / 651 liter Commercial...
True upright freezer. coil fan not running.
Let it run. Coil temperature has to be low enough for the fan delay switch to close.
Jul 14, 2010 | True 49 cu. ft. / 1388 liter Commercial...
Freezer is not cold enough . I cannot seem to find the mechanism that controls the temperature.
You need to check first that there is no leakage of your gas in your compressor system thats responsible for cooling the refrigerator. If you have the manual you an read it to locate the regulator
Oct 14, 2009 | True 31 cu. ft. / 878 liter Upright...
I have a True Freezer, the compressor comes on but the fans inside the box do not so there is no cold. I replaced both capacitors but still no luck.
http://www.truemfg.com/pdf/InstallManuals/T-SERIES/t_series_english.pdf
Go to this web site and look in the manual on page 15. Check "Compressor runs but will not refrigerate". Gives some suggestions.
Now, inside the evap, usually strapped or clipped to the coil "U" turn on the end of the coil, is a Klixon device. This device comes in many different configurations. There may be 1 or 2 of these. One is a defrost termination switch. When evap gets hot enough so no frost is present, it terminates the defrost cycle. The other is a fan delay. It comes on when the coil temp gets to about 20 degrees. This prevents circulating warm air from defrost cycle. Now if there is only one device, it can be 2 in 1. That is, a defrost terminator/ fan delay. Will most likely have 3 wires going to it where as the 2 separate ones will only have 2 wires to each one. Now, either this fan delay is not working correctly or the coil is not getting cold enough. When it gets cold enough, it turns on the evap fans. This is most likely where your problem lays. Check it out.
Sep 08, 2009 | True 52 cu. ft. / 1472 liter Commercial...
Not cold enough
Should be a thermostat with a black knob in the freezer. Usually they are marked 1-7 1 being the warmest and 7 the coldest. Usually clock wise + colder. Adjust by only 1 number per day. See how it responded the nest day. The set point is designated by a notch or arrow on the cover plate. ;)
Aug 07, 2009 | Freezers
True Freezer Running Too Cold
thermostat is stuck closed, if not compressor relay is stuck closed, if not then the defrost timer is stuck closed. test the components in that order.
Mar 22, 2008 | True 12 cu. ft. / 340 liter Commercial...
TRUE under counter FREEZER TU2-27F
Are both evaporator fan and condensor fan running?You stated that you topped off the charge.Assuming the charge is ok, the next thing to check would be the expansion valve.May not be metering the freon properly.A faulty expansion valve can trick you into thinking the unit is undercharged.It may be partially open and starving the evaporator.(Not freezing the water totally)You should have a even coating of frost on the evaporator coil when running.Hope this helps,let me know if i can assist you any further.
Dec 10, 2007 | True 12 cu. ft. / 340 liter Commercial...