Furnace doesn't start up sometimes
I have a question; We have a Bryant 80Plus furnace in the new house we just bought. Problem is that it sometimes locks out after 3 'misfires' - meaning it goes through the cycles to start up but then shuts off. Sometimes it starts right up, sometimes it needs 2 tries and sometimes it locks out after 3 failed tries. After 3 failed tries I usually turn the power on the furnace off and on. After that it fires right up without any problems. Guys on a HVAC message board told me it could be a faulty flame sensor. I cleaned the flame sensor with sandpaper and it seemed to run better for a while. Now the problem is resurfacing. I measured the flame sensor and it measured 5.2 microamps In the furnace manual it says that value should be 5.0 minimum. Since the measurement is so close over the minimum I wonder if sometimes the value is lower than the 5.0 and it doesn't start because of that. What do you think? Is it a faulty flame sensor or do the burners need a cleaning, or something else you can think of? In general, do flame sensors ever go bad or can they always be cleaned? I also heard that cleaning them with sandpaper is not good and can result in problems. Thanks for your time. I appreciate it very much.
  • 230 Answers
SOURCE: My furnace shuts off sometimes after the first 20-30 seconds.
The two most common reasons I have found for this are listed below. You have already addressed the third one.
1) Grounding issue. This can be difficult to find but easy to diagnose. Try using a volt meter or even just a piece of wire. Touch one end to an unpainted surface of the interior furnace cabinet and the other end to the sheet metal plenum or other ground. If the symptoms go away then you have diagnosed the problem and need to find the faulty ground.
2) Pressure in the flu. Check to make sure that the flu vent pipe is not clogged or even partially filled with debris. The small rubber hose that connects to the switch from the inducer blower motor may be clogged. Also check the orifice on the inducer motor side. You can clear this with a paper clip. Water (condensation) in the inducer motor housing or pressure switch can cause a failure too. Rarely is the pressure switch itself bad. This usually will only happen if it has been physically damaged or soaked. Best of luck.
Posted on Jan 29, 2009
Therinnaiguy
  • 1420 Answers
SOURCE: my burner goes on but shuts off early
First when it goes out again, locate the furnace and look thru a small viewing port to see if there is a light blinking, count the number of blinks. Then look at the wiring diagram for a diagnostic code chart. This will give you a strart of where to look.
Posted on Oct 17, 2009
Therinnaiguy
  • 1420 Answers
SOURCE: FURNACE COMES ON AND SHUTS DOWN WITHIN 15 SECONDS
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control). When all else fails, check the ground connection for corrosion.
Posted on Nov 23, 2009
Therinnaiguy
  • 1420 Answers
SOURCE: Won't ignite
There is a diagnostic light on this model that will bling an error code on the circuit board. Without removing a panel, look for a small viewing port and a blinking light. Once you have found it, look on the wiring diagram for a error code chart. This will give you a starting point. If you are getting glow from the igniter but the gas valve is not opening, you could have a bad igniter (not producing enough heat to trigger the sensor). There may be an issue with gas getting to the gas valve as moyerboy2 mentioned. The gas valve could be turned off or restriction in the gas line. Check all shut-offs and your tank if propane. Check all electrical connections at the gas valve and follow the wires back to the circuit board. Tap on the gas valve when the igniter glows, maybe something is blocking the flow of gas. Hope this helps.
Posted on Dec 21, 2009
  • 111 Answers
SOURCE: Furnace Short Cycling when cold ----- again.
I take it this is a forced air heater,if so, ther is a relay and thermal switchs involved plus possible a sail switch in the fan housing, check circuits, oil fan motor bearings
Posted on Jan 31, 2010
Model 393 Bryant furnace fan or motor makes noise when first starting. Then it's quiet.
https://www.repairclinic.com/PartDetail/Bryant-Furnace-Dual-Run-Capacitor/P2914553RS/2386586?ss=a36b380&mr=0
That part is probably going bad. The motor uses it to get moving and when it fails then the motor wont start, makes buzzing or humming noise due to phase loss.
Jan 28, 2017 | Bryant Heating & Cooling
Bryant 330JAV won't restart after power outage. Very tight space. Need to know what to do before we try to get in. Happened before. Believe tech flipped a switch. Any suggestions appreciated.
Sometimes killing the power to the furnace by flipping the breaker off for 30 minutes and then back on will let them reset and start. don-ohio
Jan 21, 2017 | Bryant Heating & Cooling
New Bryant. Why isn't it heating home well?
The furnace capacity could be inadequate
Your home could have a serious cold air infiltration problem
Your home could have inadequate insulation
If the new furnace was installed and the old thermostat was not replaced, it may be the source of the slow heating
If the new furnace was connected to existing ducts, they may be inadequate. This could account for the loud fan
Dec 25, 2015 | Heating & Cooling
How much water gal/hr is reasonable to expect from the furnace humidifier overflow in "0 degree" farenheit outside to heat a 1500 square foot normal midwestern house to 72 degrees inside having a norm
There is no flow rating because it would depend on too many factors. What you do need to check is the float valve. The water valve is opening and closing like it should be but the reservoir is filling too much.
Jan 23, 2015 | Humidifiers
Bryant Plus 90 furnace
possible your supply duct leak or break
Feb 11, 2014 | Heating & Cooling
I have a Carrier model # 58MXA080-F-15112. I think my furnace is 30 plus years old. it isn't heating properly. The blower turns on and sometimes the flames come on, but sometimes they don't. As...
A 13 code means the furnace cycled on limit more than three times consecutively and is in a lockout for 3 hours. A 14 is ignition lockout. An ignitor does not intermittently quit working. I'm the service mgr at our shop, and I know that particular furnace model has a service bulletin out on bad secondary heat exchangers. If your lucky the filter is dirty, or the furnace condensate trap or drain is clogged. Most likely the secondary heat exchanger is plugged up and isn't allowing the pressure switch to make. Or the furnace is overheating due to it not being able to properly vent hot gas. Which would explain the high limit lockouts. Call an authorized carrier dealer so you can take advantage of the free heat exchangers and the $300 labor credit. You can also call an authorized Bryant dealer to perform the work for you. Only an authorized dealer can rectify this problem because the Bryant corp requires testing and paperwork in order to get your free parts and labor credit.
Good luck.
Dec 23, 2012 | Heating & Cooling
I am trouble shooting a Bryant Hi-bred system that uses an air cooled heat pump with high efficiency gas furnace for backup and low ambient operation. How does the system decide whether to use the air...
Your t-stat should be set up so that the furnace is the second stage heat and also emergency heat. First stage (heat Pump comes on) sometimes they use Time to start 2nd stage, sometimes they use outdoor temp and this all bepends how bryant has set it up, without a model # I cannot tell you but send it and i will look in somebooks i have to tell you.
Mar 01, 2011 | Bryant Heating & Cooling
Filter for Bryant plus 90i
Bryant Furnace Filters www.iaqsource.com Every Bryant filter in stock For every Bryant furnace and AC
may want to check on the filter itself and the housing for numbers that could assist its type and size
this site may help you
Jul 04, 2009 | Goodman CLJ30AR32 Air Conditioner
Code #33 on Bryant 355MAV 90i Furnace
'Limit or flame rollout switch is open'. In my case, the flame rollout switch had tripped due to an overheating? I had to push the button between the wire leads to reset the switch. Then when I turned the power back on, the furnace started up like normal.
Why did the switch overheat and trip? My current theory is that there was a rubber grommet around a pipe near the switch that had slid down and was no longer sealing the furnace?
Mar 01, 2009 | Goodman CLJ30AR32 Air Conditioner