Question about Electrical Supplies
I have a 21b20m 20kw electric furnace when weather is cold the 100 amp breaker trips two or three times a day can you help please
If you have a heat pump you usually have 1st & 2nd stage emergency heat . Your 2nd set of elements may be bad. You can test this with a meter by ohming across each element and it should read a ohm value. Then ohm from the element to ground and it should read OL if it does not it is shorted. Also 100 amp breakers for some reason always fail I have changed more 100 a breakers than any other size. You can also get an amp probe and turn your thermostat up and read the amp draw to see if it is close to 100a. Hope this helps
Posted on Dec 30, 2013
kcmetal9901
  • 102 Answers
SOURCE: 3 combination arc fault breakers tripping under load
What is happening is the white wire that comes off the breaker is probably too close to another neutral or too close to a hot wire that is on one of the other circuits that will make it trip when you use a drill etc... Check to see if the coiled up white wire off of the breaker is not near a hot in the panel. I have had lots of arc fault breakers trip for that reason.
Posted on Nov 28, 2008
freetek
  • 5568 Answers
SOURCE: 15 amp Gould breaker trips every 24 to 48 hours
As seemingly with everything else, these devices were once very reliable but now fail early in life.
Assuming that this is no GFI (Ground Fault Interrupter) equipped breaker, you must  have a bad one. If it is, you may have some stray currents tripping the breaker.
While finishing up on our new home and putting breakers in the main box for the first time, one brand new breaker refused to stay set even though the circuit was OK and no loads on that branch connected at all. In the two years we have been here, we had to replace a second one acting just as you describe.
Posted on Dec 15, 2008
muttandjeff
  • 359 Answers
SOURCE: electric furnace wire heating up
you should have a 3- conductor # 6-3 copper wire running to this 60 amp breaker @ the furnace to the panel if this is not the case you should replace this with a # 6 as of now as it is a fire hazard as it is and needs to be fixed at once , # 10 -2 wire is only good for 30 amps and a 60 amp breaker will not trip under fault condition and you could have a fire , if you need further assistance on this let me know and i will try to help
Posted on Jan 10, 2009
  • 653 Answers
SOURCE: Ground Fault circuit Breaker trips each time a load is applied
The most likely causes in their order of probability are: 1) water somewhere in the circuit causing the hot wire to ground; 2) a legitimate trip caused by a defect in a device plugged into the circuit; and 3) a defective GFCI breaker. In the first case, wait until it has been dry for about a week and see if it trips. In the second case, make sure there is nothing plugged into the circuit and try resetting. In the third case go ahead and put the regular breaker in, then put a GFCI outlet into the first box downstream from the breaker. If installed according to the directions, that outlet should protect all of the outlets downstream.
Posted on Feb 27, 2009
  • 132 Answers
SOURCE: two 15 amp arc fault breakers installed on two
It's possible that the first breaker that you said does not trip - it could be that breaker is failing to trip on a bad circuit. That is, it could be you have a bad circuit but that first breaker is not detecting it and pretends everything is OK. If your new breaker trips on the first breaker's circuit, the curcuit it probably bad and the breaker in not working properly. The most common problem for failed circuits is a stray ground wire in a box somewhere in the curcuit resting against a hot or neutral wire. You'll have to take apart every connection on that curcuit to find it. Not fun.
Posted on Jun 27, 2009
What makes the condenser fan shut off but the compressor keeps running but not every time
Condenser fans cycle on and off to control the temperature/pressure of the refrigerant in the condenser. This is normal operation.
As to cooler weather start up and tripping the breaker; how cold is it when you are running it? If it is too cold you could be pumping liquid refrigerant back to the compressor, slugging it and causing it to trip a breaker. However, many things can cause an air conditioner to over-amp and trip a breaker but this tends to be more problematic as the weather is hotter.
Feb 20, 2015 | Heating & Cooling
Outside main 100 amp breaker is tripping but none of the inside breakers, supposedly when dryer and tv on together but not all the time
Am I to assume your dryer is electrical? If so, I'll guarentee it will draw MORE than 14 Amps if heating. Sorry, can't analyze your problem from here.
May 01, 2014 | Cutler Hammer 100 Amp Main Breaker...
Heater not heating enough
Electric furnaces have strip heat inside of them. Depending on the model, size, etc, is how much heat the system can provide. Many times, if the system has worked in the past and started to have problems later, it's because you have lost half or more of your heat strips. They come in different sizes, 10kw, 15kw, 20kw, but ran on different contactors. So if you have a tripped breaker, faulty heat sequencer, etc, you can still have heat, but not the full amount. I strongly suggest any electrical related problems be look at by a qualified technician when dealing with air handlers. Hope this helps!
Dec 08, 2013 | Heating & Cooling
Furnace runs awhile then breaker trips
Electric furnace I assume- check with amp meter, if amps are below listed on breaker, replace the breaker, [check both the breakers in the furnace and in the house pannel, even if only one is tripping right now, the other(s) may start doing the same thing after you eliminate the weakest link- don't be surprised!] electric furnaces are notorius for "eating" breakers- they overheat the breakers for years then the breakers get weak and trip too easilly... if gas, post more info and I'll try to help further.
Feb 20, 2013 | Heating & Cooling
I have an electric furnace, it worked fine since it was last repaired, had a bad heat sequencer in it.. but now (3weeks later), it is tripping the 30 amp breaker after a few min of operation ????,...
I ran across a similar problem with electric furnaces years ago. One of the heating elements had failed and the coil was actually making contact with the frame in which it was held. This may be the problem but must be checked with the power off as the chassis may be live. Something is definitely amiss if your unit is tripping a 30 amp breaker and probably will show up on a utility bill next month.
Feb 17, 2011 | Heating & Cooling
Have Challenger Type C 2100 circuit breaker in residential home electrical panel. Manually turned to off position and now cannot turn back on. Pops back to off position. Also says HACR type and common trip...
First HACR is heating, air conditioning,refrigeration. So in other words you could use it on an electric furnace or air conditioning.
IS this the main breaker for the panel? or for and electric furnace. I'm assuming its for the furnace, perhaps back up heat for heat pump. See if there is another disconenct on the furnace, turn it off and see if the breaker resets. IF so you have a short or overload in the furnace.
If' it IS the main for the panel, turn off all the other breakers in the panel, and try to reset the breaker. If that works, turn the other breakers back on one at a time. IF it "POPS" then it is tripping. Don't keep resetting, find the problem.
Jul 19, 2010 | Challenger Connecticut Electric UBITB-A230...
Breaker keeps getting flipped off
20kw heat should have 2 separate 60 amp circuits on number 6 wire.
Mar 03, 2009 | Ducane Grilling
Electric Furnace Trips Breakers
it is normal for a breaker that is run right on the edge (50 amp and your furnance to use 45) to get weak after a while . the first thing you should do is change the breaker with the same type and amp rateing . it should take care if it
Jan 16, 2009 | Heating & Cooling
Electric furnace wire heating up
Jan 09, 2009 | Electric Circuit Breaker Kit for Furnace
My 200 amp Siemens main electric box is heating
This is a dangerous situation! There is a short in the furnace. It is NOT a breaker problem! You need to check the current draw in the furnace circuit, This requires an Amprobe meter. If you don't have one, contact a technician at once! You have a fire hazard!
Ray
Dec 15, 2008 | Fahrenheat LFP6152 Halogen Baseboard...
Electrical Supplies Logo
51 people viewed this question
Top Electrical Supplies Experts
ken skalski
Gene Haynes
Are you an Electrical Supply Expert? Answer questions, earn points and help others