Furnace lockout The problem I have been experiencing is the furnace will enter a lockout mode. That is, if the furnace attempts to start as a result of the thermostat command (below set temp), it will fail to start properly. I can immediately reset the furnace (wall switch off and on) and it will start without any issues. I have cleaned the flame sensor several times with no luck. Is there anything else I can do before I call the technician? Thanks
  • Heating & Co... Master
  • 3,250 Answers
Change the flame sensor, check the connections on the sensor are tight , check pressure switch , check air filter is clean .
Posted on Jul 05, 2017
22yooper
  • 828 Answers
SOURCE: Carrier Weathermaker gas 8000 will not ignite
Your hot surface igniter may be bad. It may be cracked which would prevent it from starting the burner flame.
Posted on May 22, 2008
Therinnaiguy
  • 1420 Answers
SOURCE: Goodman GMS90904CXA Wont ignite, light blinks 3 times
Ok, you either have a inducer fan issue or a pressure switch issue or a plugged vent pipe. The inducer turns on to establish a draft for the exhaust. If it is not working you will get this error code. If the pressure switch does not sense pressure caused by the inducer, it will give this code. If either the intake pipe or exhaust pipe is blocked (even y just a little) it will give you the same error code. If the condensate hose or receptical is plugged, again it will give you this error code. Good Luck!
Posted on Oct 21, 2008
rayname
  • 70 Answers
SOURCE: Goodman GMNT furnace goes into 'lock-out'.
check to see if your intake pipe or vent is clear this could cause a flame jump and make it look like a bad flame sensor let me know if this helps
Posted on Jan 08, 2009
SOURCE: Thermostat seems to be working, furnace does not always turn on
i need help rplce thrmostat with a digital braueburn my furnance wont turn on no flashing lights cant reset the burner though has power what do i do shoul i reset the circut breaker that was never tripped though
Posted on Jan 26, 2009
mrgrzz
  • 88 Answers
SOURCE: Where is flame sensor on my old oil furnace?
Thanks for your question,
The flame sensor eye is located just under the transformer, it is looking straight down the burner assembly to where the burner chamber is at, you will have to remove the entire assembly to get to it, first make sure the power is off, remove the transformer, then remove the entire burner assembly from the furnace cabinet, once removed you can see the flame sensor window, use a clean oil free cloth to clean it, it would probably be a good idea while you have it out to replace the burner nozzle, as over time they will clog, I hope this helps you fix your oil burner, let us know and rate this please, thanks again,
mr.grzz
Posted on Jan 27, 2009
Error code= two red flashes, lockout/ no flame
Trane XV80 hard lockout, 2 flashes, Can't be reset - DoItYourself ...
www.doityourself.com > ... > Gas and Oil Home Heating Furnaces
Jan 10, 2013 - The only way I can get diagnostic Red LED light to reset is to switch ... a2 flash with absolutely no operation from the furnace does seem to ..... inducer gets a demand you should get a pressure switch error code 3. ... the flame sensor wire and giving the furnace a heating demand after resetting power twice. Luxaire Furnace Blowing Cold - 8 Red LED Flashes
Mar 1, 2010
Winchester furnace diagnostics
Feb 14, 2010
American Standard Freedom 80 - Cold Air - Getting Error Code 9 ...
Nov 20, 2009
York ignition lockout due to retries
Dec 29, 2008
More results from www.doityourself.com
7 Tips and Tricks to repair your Furnace DIY - YouTube
? 13:25
https://www.youtube.com/watch?v=rAtcvPqUsBA
Dec 18, 2012 - Uploaded by JRESHOW .
cause this fault. 2 RED FLASHES: This indicates that thenormally open pressure ... The furnace will lock out for one hour and then restart. 7 RED FLASHES: This fault code indicates that the flame could not be established. This no-light ... problem. Bothheating and cooling operations will be affected. Check
Jan 23, 2016 | Heating & Cooling
I have a Carrier model # 58MXA080-F-15112. I think my furnace is 30 plus years old. it isn't heating properly. The blower turns on and sometimes the flames come on, but sometimes they don't. As...
A 13 code means the furnace cycled on limit more than three times consecutively and is in a lockout for 3 hours. A 14 is ignition lockout. An ignitor does not intermittently quit working. I'm the service mgr at our shop, and I know that particular furnace model has a service bulletin out on bad secondary heat exchangers. If your lucky the filter is dirty, or the furnace condensate trap or drain is clogged. Most likely the secondary heat exchanger is plugged up and isn't allowing the pressure switch to make. Or the furnace is overheating due to it not being able to properly vent hot gas. Which would explain the high limit lockouts. Call an authorized carrier dealer so you can take advantage of the free heat exchangers and the $300 labor credit. You can also call an authorized Bryant dealer to perform the work for you. Only an authorized dealer can rectify this problem because the Bryant corp requires testing and paperwork in order to get your free parts and labor credit.
Good luck.
Dec 23, 2012 | Heating & Cooling
Furnace gas valve is not opening
YOUR FURNACE IS IN LOCKOUT MODE DUE TO A SAFETY FEATURE OF UNIT. USUALLY THE HIGH LIMIT HAS BEEN TRIPPED, OR YOU PRESSURE SWITCH FROM DRAFT INDUCER MOTOR FAULTY OR PLUGGED. IT WILL CONTINUE LOCKOUT MODE UNTIL THIS IS FIXED.
Dec 23, 2012 | Carrier Weathermaker 8000 Gas Furnace 125k...
I have a Ruud Achiever 90 Plus furnace that will not ignite and is showing a 'soft lockout' code on the LED panel. I've tried restting the furnace as per the manual and still no results. Am I missing...
Hello. a soft lockout typically happens when
1) the flame sensor is not detecting the flame
2) pressure switch fails to close
Since your burners are not igniting I would check the pressure switch, make sure there is no obstruction in the flue pipe, the hose going from inducer to pressure switch is not kinked, loose, obstructed, or have water in it. If that all checks out good then your pressure switch is bad and must be replaced. If you need any further assisatnce let me know
Mar 09, 2011 | Heating & Cooling
Air suspension out (inactive ) code
1. The automatic suspension system on a Land Rover must be placed in a service mode (High Lock) prior to raising the vehicle on a frame-contact hoist. This can only be accomplished by using a Land Rover Test Book Scan tool or an aftermarket equivalent.
2. If the suspension is allowed to hang freely at maximum extension, the suspension controller will enter a fault lockout mode and disable the compressor and height sensors
3. In addition, the suspension system will vent the suspension in an attempt to bring the vehicle to a correct ride height.
4. Since the suspension is hanging free at maximum extension, all the air will be vented, causing the vehicle to sit at maximum low when taken off the frame-contact hoist. A Land Rover Test Book Scan Tool or an equivalent is required to reset the suspension once it has entered the lockout mode.
Sep 23, 2009 | 2003 Land Rover Range Rover
Monsoon radio error LOC
Means someone has attempted to enter the unlock security code too mant times and radio is now in theft lockout mode. Car must be left running for an hour to exit this mode, then proper code must be entered.
Jun 13, 2009 | 2006 Pontiac G6
Main Fan won't turn off even with thermostat removed. Burner not
There is a chart with the wiring diagram and othere charts that will tell you what the 6 blinks are for. That should tell you what is wrong and what part you need. Sounds to me like the board has an issue or the gas valve is locked out.
Jan 10, 2009 | Goodman GDS81155CNA Open Flame Mid-Size...
GMP050-3 heater, gas turns on and lights for 5-7 seconds and just as thr igniter goes dim the gas shuts off. after 3 cycles the erd LED flashes on/off at a 1.5 seconds on and 1.5 sec off Gary
After the gas turns on, it is the flame sensor's job to see that ignition took place and send 24v to the gas valve. If it does not do this, the gas valve shuts down as a safety precaution. After 3 tries, the furnace will go into "lockout" and will not let it attempt to start again. The lockout can be resolved by turning off the power to the furnace for a couple minutes and then turning it back on. Sounds like the real problem is a faulty flame sensor not sending 24v to the gas valve. Sometimes they can be cleaned with a piece of sandcloth. This will cure failure to recognize the flame due to carbon build up on the sensor. Otherwise, the sensor will need to be replaced. Hope this helps!
Dec 16, 2008 | Goodman Heating & Cooling
Ignition failure after three attempts then sits for an hour.
try cleaning the burners and or adjust the distance the igniter is from the actual burner .
Oct 01, 2008 | Goodman GDS80904BNA Open Flame Heater