I have ups my office and the problem with that is sometimes it is working good i.e inverter is taking load but sometimes inverter is going off indicating inverter overload. If some components fails the problem has to be continuous but here it is not the case. suggest me what may be tha possible reason for this malfunctioning.

Posted by on

  • haribabualap May 17, 2009

    it is 7.5KVA UPS,what it mean refill inverter

×

2 Answers

  • Level 3:

    An expert who has achieved level 3 by getting 1000 points

    Superstar:

    An expert that got 20 achievements.

    All-Star:

    An expert that got 10 achievements.

    MVP:

    An expert that got 5 achievements.

  • Master
  • 1,056 Answers

Make sure the connection that supply the inverter its power is tight. A major cause of overload light coming on is a low voltage on the battery if it is getting supply from a battery, and loose connection on the power supply. All in all if the voltage that power it is lower than what it operates on it would do that.

Posted on Jun 28, 2009

  • Level 2:

    An expert who has achieved level 2 by getting 100 points

    MVP:

    An expert that got 5 achievements.

    Governor:

    An expert whose answer got voted for 20 times.

    Hot-Shot:

    An expert who has answered 20 questions.

  • Expert
  • 102 Answers

Did u refill ur inverter

its happens too me too sometimes

"can u rate me, for my work... please"
thanks

Posted on May 17, 2009

1 Suggested Answer

6ya6ya
  • 2 Answers

SOURCE: I have freestanding Series 8 dishwasher. Lately during the filling cycle water hammer is occurring. How can this be resolved

Hi,
a 6ya expert can help you resolve that issue over the phone in a minute or two.
best thing about this new service is that you are never placed on hold and get to talk to real repairmen in the US.
the service is completely free and covers almost anything you can think of (from cars to computers, handyman, and even drones).
click here to download the app (for users in the US for now) and get all the help you need.
goodluck!

Posted on Jan 02, 2017

Add Your Answer

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

1 Answer

Our ups apc back-ups 1500 is making beeb sound with red led blinking (overload option)


remove the load fom the ups and restart the ups. if the ups alarms again then the problem is in the inverter.

Apr 19, 2011 | APC Back-UPS RS Battery Backup (apw...

1 Answer

Upc 900 why my overload alarme with no charge on it?


The overload circuit normally collects the current information from the inverter leg. At times when there is an actual overload, the protective circuit picked up the excess current as compared to the calculated value and thus gives an alarm. However at times when the inverter leg is short circuit or a leakage it also gives the same overload current. Is the inverter on when it gives the overload alarm? Please let us know.

Mar 13, 2011 | APC Back-UPS XS900 (BX900) UPS System

3 Answers

Overload Red button is on even after pressing reset button @ back


Try unplugging some equipment from the UPS. The total load should be less than 865 W. Printers and scanners often are culprits.Some gaming desktop computers can have a power supply that will be too much for this UPS. (I've found that even having the printer on the surge only part of the UPS can be a problem. I have the printer on a separate surge protector.)

Since the overload is new, did you add any equipment to the UPS recently or upgrade components?

If you reduce the load, and the problem continues, the UPS may have a fault in the circuitry. If it is under warranty, contact APC.

I hope this helps.

Cindy Wells
(I have replaced APC units after 3+ years when they can't properly recharge the battery - with a new battery. The symptoms are 1) getting a overload when a small load is on the UPS. Small load - desk lamp, 13" TV or 2) not keeping the item on when the power goes off.)

May 17, 2010 | APC 1500VA BX1500 8 Outlet UPS UPS System

1 Answer

Ups temprature fault


From what info you gave me. It sounds to me like it is either too small for the load, or it is in a confined space where heat is building up (UPS has to be outside of a desk office, etc.) or the rectifier is going bad and heating up. I would check to see if it does it by hooking up a small load to it like a radio or something, and if it is in the open, not overloaded then rectifier is bad,I see it alot. I am a Master Electrician and have worked on many UPSs'. Remember that if you keep a UPS loaded to it's full potential (which you shouldn't do) it will get hot. The rule is to only load it up to 80% of it's rating and you will be fine. To find out how many amps it will handle you simply devide the VA of the UPS by the supply voltage. Example: 1200va UPS supplied by 120v. is good for 10 amps. 1200/120 = 12 amps, then it is wise to add 25% more to the watts or amps when sizing them. Also, if it has a cooling fan make sure it isn't blocked by lint and is working, if it isn't working it will get hot fast. Good luck!

Nov 10, 2009 | MGE UPS Galaxy 3000 UPS System

1 Answer

I have an inverter, then a UPS, as the inverter does not always keep the PC on. The inverter does not power the UPS so it cuts out after a few mins, I then have to take the UPS out of the system until the...


Hello,

As I understand your statement, Your inverter (Powerline 200watt) has the UPS plugged into it, but it is not able to keep the UPS powered on. You didn't mention the size of the load (PC), nor the wattage rating of the UPS, or the batter bank size that supplies the inverter.

It sounds like you are trying to create an electrical system with double redundancy. If this is the case, you are going about it wrong. Most inexpensive inverters will have a Modified Sine Wave output, that the UPS will detect as a poor AC signal, and revert to backup mode, rather than pass the inverter power to the load.

200 watts isn't going to be very much for anything. 200watts / 120 volts (assuming 120vac system) is only 1.6amps or so. The charger on the UPS will likely use this much just to keep the internal battery topped off. As the PC is turned on, and the battery charger is doing its thing, there now exists an overload at the inverter. The inverter will respond by trying to increase its output by lengthening the pulses in the MSW waveform. The UPS then sees this, interprets it as bad power, and kicks into backup mode.

Since the powerline inverter is obviously a 12volt unit (cig. lighter plug), then check the battery configuration of the UPS itself. If it is 12volts as well, then you may be able to connect the UPS directly to the batteries that were powering the inverter. Note that some modification to the UPS will be needed if there external battery connections are not already present. Even then, there is no guarantee that the charger in the UPS will be able to charge the internal plus an external battery bank.

Since the battery that powers the inverter is likely larger than that of the UPS, why not run the PC directly off the inverter itself and forgo the use of the UPS altogether?

Nov 02, 2009 | Powerline 200Watt DC to AC inverter...

2 Answers

Overload LED lit, constant warning tone, no load


you may have to many things plugged into the ups, it is not good to plug a power bar into one of the outlets of one of these as you are OVERLOADING the device with more power than it can produce

Oct 21, 2009 | APC Back-UPS XS900 (BX900) UPS System

1 Answer

I have a APC BX900R. i HAVE REPLACED THE


Your UPS is having an internal problem, it should be an inverter problem. if you know how to troubleshoot up to component level try to open the UPS and check the power mosfets. if not bring your UPS to the service center.

Aug 12, 2009 | APC BACK-UPS 900VA (BR900) UPS System

1 Answer

APC 650 Pro not working properly.


My question is how long is the battery inside your UPS? 5years ? coz sometimes you cannot just base on the voltage you measure on the batteries. dont forget about the current that is being supplied by the batteries maybe the battery current is too weak to handle your load. but if you are really sure that your battery is good. try to check the inverter circuit of your UPS. or send it to UPS service center if you dont know how to check electronics component.

Jul 02, 2009 | APC Smart-UPS 1400VA UPS System

1 Answer

Overload light in APC RS 800 UPS


it seems that the inverter circuit of your UPS is dying. the solution here is you have to open up the UPS and check the inverter circuit. to make easier, check the power mosfet if its leaking.

Jun 11, 2009 | APC (br800) UPS System

Not finding what you are looking for?
Powerline 200Watt DC to AC inverter (0900-35) Power Supply Logo

Related Topics:

1,168 people viewed this question

Ask a Question

Usually answered in minutes!

Top Powerline Computers & Internet Experts

Doctor PC
Doctor PC

Level 3 Expert

7733 Answers

kakima

Level 3 Expert

102366 Answers

David Payne
David Payne

Level 3 Expert

14161 Answers

Are you a Powerline Computer and Internet Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...