Have a goodman GMP075-3 that won't turn on when thermostat is set to Auto. I will only turn on when set to the "ON" but will blow cold air. Status light blinks 3 times. Code notes suggest to" "check Venter Pressure Switch Vent Blockage" I think it is the pressure switch since I do not have a vent blockage. Should I replace the Pressure Switch? Your Advice?
  • Goodman Master
  • 2,345 Answers
With a meter you can can test continuity. This will tell you if the switch has failed. Always be safe and turn power off, when testing continuity through switches unhook at least one side of the wires. Best wishes.
If you need further help, reach me via phone at https://www.6ya.com/expert/thomas_092728000e6acb79
Posted on Nov 24, 2017
    Novelist:
  • 90 Answers
The t-state set to fan "ON" will only cycle the fan to turn on only nothing else. "Auto" is where you always want the t-state on when you want to have heat and have the fan cycle off automatically after the t-stat has reached set point.
As for the press switch, there can be two things that will cause the pressure switch not to close. 1: obviously the switch itself and 2: the inducer fan, this has the rubber tubing that connects to the pressure switch.
When you call for heat, the inducer fan ( small fan with black plastic piece that spins ) is the first to turn on, this fan makes sure any left over exhaust air/gases are vented out before the burners turn on, it also stays on the entire heat cycle to exhaust the gases. The pressure switch needs proof of air so the pressure switch closes with the vacuum that is being created by the inducer fan in that rubber hose that is connected to the pressure switch. This allows the furnace to know " my induce fan is working, lets proceed".
So,
I would make sure your inducer fan is working. if you don't see it working then I recommend using a multi-meter ( VAC setting) and checking that you have 120volts supplied to the inducer fan. if you don't, then you need to work backward from there and see why you don't. If you do verify 120volts at your inducer motor, then more than likely it failed and will need a new one. Witch out this, your pressure switch wont close.
If your inducer fan is working fine then make sure you have 24vdc across you pressure switch (again with a multi meter but with VDC setting not VAC). 24vdc in and 24vdc out. If you only have 24VDC in but not out, then you pressure switch may be stuck open. ( This is if your inducer fan is working properly).
I hope this helps. Sorry for the long response. I just don't like people changing parts and wasting money.
Posted on Nov 23, 2017
3 Suggested Answers
SOURCE:
  • 6 Answers
SOURCE: I have a 1993 Goodman,
venter is the inducer motor.
Posted on Dec 31, 2008
SOURCE: goodman furnace wont come on
If this is a High Eff furnace:
1) Remove the compartment that has the igniter and burners, turn the
power back on, if the furnace lites then you have a problem with the
intake air vent, probably iced over if you live where its cold.
2)Make sure the exhaust vent is not getting backpressure from the
wind.
3) you could cut the pipes on the inside of the house to disconnect them from the furnace, test run the furnace with no pipes.If the furnace
runs then you have a problem with the installation of the vent pipes.
4) Do not run the furnace without the exhaust pipe disconnected,
go to the hardware store and get a couple of rubber clamped
couplings and hook-up the exhaust pipe!
Good Luck
Posted on Jan 09, 2010
Do Goodman Split System fans turn off when the compressor shuts off? Is there a setting so the fan stops when the room reaches the desired temperature?
That is the job of the thermostat, but only if the "Fan-on/auto switch is set to auto. Look on your thermostat for the switch.
Aug 22, 2013 | Goodman Heating & Cooling
Furnace problems
On - OK
1 Blink - Ignition failure. Check Gas flow, gas pressure, gas valve, flame sensor.
2 Blinks - Closed pressure switch. Check pressure switch (stuck in closed position).
3 Blinks - Pressure switch - failre to close. Check venter, pressure switch, vent blockage.
4 Blinks - Open limit switch. Main limit or aux limit are open. (My comment - Means overheating in chamber. Often result of blocked intake air. Bad filter. In my case, plastic wrap had been sucked into the intake. )
6 Blinks - False flame sensed. Check sticking gas valve.
Rapid continuous blinking - Incorrect twinning, incorrect primary polarity. Reverse transformer secondary leads, reverse primary wires.
Closed pressure switch can be from dirty combustion vents, bad chamber pressure - like missing screws, maladjusted gas pressure, failing pressure switch, loose hoses, moisture in the hoses or fan blades The switch need to be closed to ge the unit to work
Jan 23, 2008 | Goodman GMS90703BXA Heater
Won't run when set to auto
This can either be a bad thermostat or faulty control board. If the unit kicks on after jumpimg the wires at thermostat then the thermostat is defective, if it does not turn on the control board is faulty and must be replaced.
Jun 06, 2012 | Goodman Heating & Cooling
I have a Goodman GMP 125-5 furnace. It had a 3 light code i replaced the presure switch now it is giving me a 1 light code please help
A sampling of various failure codes on a furnace:
Read one LED flash that stays on continuously to mean your furnace has no signal coming from the thermostat and will not operate. Turn the power off and check the thermostat for improper settings or connections.
Interpret one LED flash that blinks on and off to mean your furnace has locked out because it could not ignite after three tries, and must be reset. Interrupt power to your furnace for 20 seconds or lower the thermostat so your furnace does not try to heat, then reset the thermostat to the previous setting. After one hour of lockout, your furnace will automatically reset itself and try to operate as usual.
Decipher two LED flashes to mean the draft blower is not working, or your furnace has a short in the pressure switch circuit. Turn off the furnace power and repair a short or replace the pressure switch.
Read three LED flashes to mean your furnace has an open pressure switch circuit or it has an induced draft blower operating. Check the pressure switch hose of your furnace for blocks or an improper connection. Also, look for blockages in the flue, and tighten any loose wiring.
Translate four LED flashes to mean your furnace has a primary limit circuit open, possibly from loose wiring or blocked filters. Check and clean filters, tighten wiring and check the flue for blockages.
Interpret five LED flashes to mean your furnace senses a flame without a call for heat. This could be from a gas valve closing slowly or a burner flame lingering.
Read seven LED flashes as a warning of a low flame sense microamp signal. This could happen with a coated flame sensor or a lazy flame from poor gas pressure. Turn off the power and adjust the gas pressure according to the information on the rating plate.
See eight LED flashes as meaning an igniter circuit problem due to a bad igniter or an igniter connected improperly. Replace the bad igniter or check the ground wiring, making necessary corrections.
Decipher nine LED flashes to mean the high-stage pressure switch circuit will not close during a high-stage-induced draft blower operation. Your furnace may have a pinched or blocked pressure switch hose, a blocked flue or loose wiring.
Read continuous flashing on the LED to mean your furnace has a reversed polarity of 115 volts. Turn off the power and correct the wiring polarity after reviewing the wiring diagram.
If you need further help, reach me via phone at https://www.6ya.com/expert/dan_73bbd84fe1d95b61
Oct 28, 2011 | Goodman Heating & Cooling
I have goodman GMP series furance the furnance and gas comes on and fires up then goes out flame sensor is good what else could be wrong
Improper ground from control to burner.
Incorrect electrical wiring, check polarity.
Tubing partially clogged between inducer and proving switch.
Oct 18, 2011 | Goodman GMS90703BXA Heater
Suddenly not working im not sure if there even is a pilot to be lit
Goodman have troubleshooting idiot lights on the board. Look for flashes and count em.
The flash explanations are printed on the backside of the blower cover on most models.
Feb 03, 2011 | Goodman Heating & Cooling
Goodman: My Power Venter (aka Heat and Draft Inducer) won't start
The power ventor most likely needs to be replaced. But be advised. Goodman normally will not sell parts to anyone but a certified technician. I had to show my masters certificate to buy parts from their outlet. This is a part that has a high rate of failure.
Ray
Dec 01, 2008 | Goodman Heating & Cooling
Furnace won't stay running
1 FLASH
Furnace fails to operate.
• Integrated control module
diagnostic LED is
flashing ONE (1) flash.
• Furnace lockout due
to an excessive
number of ignition
“retries” (3 total)1.
• Failure to establish flame.
Cause may be no gas to
burners, front cover
pressure switch stuck open,
bad igniter or igniter
alignment, improper orifices,
or coated/oxidized or
improperly connected flame
sensor.
• Loss of flame after establishment.
Cause may be
interrupted gas supply, lazy
burner flames (improper gas
pressure or restriction in flue
and/or combustion air
piping), front cover pressure
switch opening, or improper
performance.
• Locate and correct gas
interruption.
• Check front cover
pressure switch
operation (hose, wiring,
contact operation).
Correct if necessary.
• Replace or realign
igniter.
• Check flame sense
signal. Sand sensor if
coated and/or oxidized.
• Check flue piping for
blockage, proper
length, elbows, and
termination.
• Verify proper induced
draft blower performance.
Nov 23, 2008 | Goodman GMS90703BXA Heater
Goodman GMS90904CXA Wont ignite, light blinks 3 times
I had the same problem, I had to remove the lower black rubber stopper right next to the exaust fan and hook up a drain to the unit, as soon as the water drained out the furnace fired right up.
Nov 19, 2008 | Heating & Cooling
Ok, you either have a inducer fan issue or a pressure switch issue or a plugged vent pipe. The inducer turns on to establish a draft for the exhaust. If it is not working you will get this error code. If the pressure switch does not sense pressure caused by the inducer, it will give this code. If either the intake pipe or exhaust pipe is blocked (even y just a little) it will give you the same error code. If the condensate hose or receptical is plugged, again it will give you this error code. Good Luck!
Oct 20, 2008 | Goodman GMS90703BXA Heater
Goodman GMS90703BXA Heater Logo