Question about Electrical Supplies
Pole barn subpanel has suddenly dropped half of circuits
All breakers running off the red hot side of the subpanel cannot support load. the subpanel tests 120V between neutral and each hot wire and 240V across the two hot wires, but if any load is placed on the red side, the measured voltage disappears. the connection of the red feeder at the main panel was charred/corroded a little... I replaced the breaker and cleaned the connection, but this did not have any affect on the symptoms. I swapped the black and red at the main panel breaker and the symptoms are still showing up on the red side of the subpanel. I moved some of the circuits in the subpanel to the black side and they work fine over there. The only thing I can add is that I had one of several flourescent shop lights on the red side that had been flickering over the past week or so before that side of the box failed. Seems to me this is likely a fault in the red wire running from the house to the barn. How can I confirm prior to digging and replacing? Thanks.
  • Frank
    Frank May 11, 2010
    check the ground, hot side seems to be OK, but the ground is "floating" the ground is the black.
    to test it out, run a ground wire from the house panel to the subpanel.
Problem solved. I disconnected both ends of the feeder line to the barn and tested continuity by alternately hooking two wires together at a time and using an ohm meter on the other ends. The result of the testing was that the majority of the wires in the run were making contact with each other to varying degrees. We have seen a lot of rain this spring, so I assumed there was a break in the line that had gotten wet down in the ground. We had some work done last fall where they may have distrubed the line, so I dug around that area first and luckily found a splice that had been very poorly sealed against the elements. Got it dried out and everything returned to normal. I used layers of liquid electrical tape and heavy water proof tape to insulate and seal the repaired line prior to putting it back into its wet environment and back filling.
Posted on May 18, 2009
5000 watt inverter schematics circuit
If you have (90) 50w lamps = 4500 watts total. Assuming a 120/240 panel, if you put 1/2 on one "side" of the panel and the other 1/2 on the other "side" of the panel, that would be 2250 watts on each half. The generator should be rated *at least* 125% of the load; 4500w x 1.25 = 5625W. Using a 4500W generator on this load will cause it to overheat and shorten its life as it is running at 100% of capacity all the time..
One half of the panel is 120V to neutral, and the other is 120V to neutral - or 240V between both circuit breaker terminals. Ohms law for DC circuits and purely resistive AC circuits says Volts x Amps = Watts; or Watts / Volts = Amps. So, 2250W / 120V = 18.75A on each pole of a 2 pole circuit breaker that feeds the sub panel. A #12 copper wire is rated for 20 amps; but as per National Electrical Code - must be de-rated to 80% of rating which means it is good up to 16 amps maximum. A #10 copper wire is rated for 30 amps, but it too must be derated to 80%, making it good for 24 amps maximum. So, if you are going to feed a sub panel supplying (90) 50watt lamps, you will need to run a #10/3 copper cable from a two pole 30 amp circuit breaker at the generator to a 120/240 volt "main lug only" sub panel rated for at least 30 amps.
Divide your load evenly across the sub panel - (4) 15 amps circuits via (2) two pole 15 amp circuit breakers on each "side" of the panel if you run (2) 14/3 cables out to the lights - or (4) single pole 15 amp circuit breakers if you run (4) 14/2 cables out to the lights. No circuit breaker terminal should have more than 23 lamps that means you have (2) w/ 22 lamps and (2) with 23 lamps. The circuit w/ 23 lamps will draw 23 lamps x 50w = 1150W. 1150W / 120V = 9.6A. The 22 lamp load will be 22 x 50w = 1100W. 110W / 120V = 9.2A. Which is well within the 12A maximum allowed (after derating as required by code) by a #14 copper wire rated for 15A.
Mar 10, 2014 | Electrical Supplies
I have a 125 FPE box currently the combined total of all breakers presently in the box is 190 amps. I am wanting to replace a single pole 20 with a single pole 40. Am I already maxed out or do I have room...
You can add the breaker.
The key is total electric use.
As long as total consumption does not exceed amps shown on main breaker, then the new 40A breaker installation is ok.
If total consumption exceeds main breaker, then the main breaker will start to get hot and then trip.
http://waterheatertimer.org/How-to-install-a-subpanel.html
Put hand on main breaker and feel for warmth.
The main should not feel warm.
Consider upgrading to 150A or 200A service.
Aug 22, 2011 | Connecticut Electric UBIF040N FPE...
Hello can i get the instuctions for tork timer model 1191 please?
According to Intermatic conversion chart, Tork 1191 is same as Tork 1101.
Link to 1101 .pdf
Link to Tork manuals
Tork 1101 is dial-type mechanical timer. Dark pins turn OFF. Light pins turn ON.
Clock motor is 120V
Hot black wire from breaker connects to pole L
Neutral white wire from breaker connects to pole X
Removable bridge connects poles L &1 together
If bridge is gone, Hot from breaker must also connect to pole 1
Black wire to Load connects to pole 2
White wire to Load connects to pole X
Timer can control 240V Load if removable bridge between poles L and 1 is taken out.
Timer clock is still 120V: so 120V Hot still connects to pole L and neutral from breaker connect to poles X
240 V circuit has two hot lines: Hot line 1 and Hot line 2
240 volt Hot line 1 from breaker connects to pole 1
240 volt Hot line 1 to load connects to pole 2
240V Hot line 2 goes directly to Load and does not connect to any pole
Oct 04, 2010 | Hardware & Accessories
How do I run from a 100 amp main panel to a 60 amp subpanel, 125 from my house to the garage
See 60 Amp sub-panel image
Above image shows drawing of 60Amp sub-panel located next to main panel. Drawing shows #6 wire... 125' distance to garage calls for #4 wire. I ran #4 to my barn and have no problems.
Give thought to how many new breakers you want at garage.
See photo of subpanel that holds three 240V breakers
Using drawing as a guide. Replace existing 240Volt breaker with new 60 Amp breaker. Two hot wires connect to new 60 Amp breaker. Neutral connects to neutral busbar.
More space: You can free up space in main breaker box using a tandem breaker. Or by doubling up 2 lightly used 120V circuits onto one breaker. Do not double-up on 240 Breakers
Conduit: You want PVC conduit large enough to fit three #4 wires. Bigger conduit is easier to pull wires ... and maybe later ethernet wire, or alarm wire etc.
Ground wire: You can put a ground rod at garage and run #6 bare copper between sub-panel neutral-busbar and ground rod. Attach ground wire firmly with grounding clamp.
I want you to check with local electrical supply for exact code in your area concerning conduit requirements, grounding, and wire size. Tighten all lugs very tight against wire.
Oct 03, 2010 | Siemens 100 Amp Main Breaker Renovation...
HOW TO WIRE
A single pole ground fault breaker has a screw terminal on one side for the black wire to the ciorcuit, a white curly pigtail that goes to the panel neutral/ground bar, and a screw terminal near the white wire for the white neutral wire from the circuit.
A 2 pole GFI breaker is similar, But it has another screw terminal for the other hot wire in the circuit.
For a 220 volt, 2 pole, GFI protected circuit, you need to run a 4 wire cable. black, red, white, green.
Please Vote !!
Apr 13, 2010 | Siemens 50 Amp Ground Fault Circuit...
I have a 2hp compressor motor that keeps tripping the breaker after about 5 minutes of use. i have changed the caps but it keeps popping the starter cap. is the motor just bad?
Our 2 HP Speedaire horizontal tank compressor is rated 115 / 230 volts at 24 / 12 amps, respectively. This means at 115 volts, a 30 amp circuit breaker is the bare minimum. That also means that the wiring should be #10 copper wires for short runs, but the next size up; #8 copper wires would be better connected to a 40 amp circuit breaker. Running at 230 drops the amperage requirement by half, to 12. A #14 copper wire is minimum for short runs with a double pole 15 amp circuit breaker, but #12 copper wires connected to a double pole 20 amp circuit breaker would be better choice.
If the compressor is cord connected (or even directly wired) with the minimum sized wires, it will likely a voltage drop problem unless very close to the panel. This problem is more pronounced as the distance between the circuit breaker and motor increases, or when smaller wires are in the circuit. All the voltage at the circuit breaker does not reach the motor, as it is lost as heat; so the compressor only sees 90 to 105 volts instead of the 115 volts it expects.
If the cords, connections, etc are getting hot, it is a tell tale sign of under-sized wires and /or poor connections. Once you solve these problems, the compressor should run "as advertised " because motors usually don't "go bad" but fail all at once. Unless you have a bearing problem - or there is a problem with the load itself (compressor).
I hope this helped.
Nov 12, 2009 | AO Smith 2 Hp Spl 3450rpm M56 Frame...
Hooking up a Hot tub
Everything above tells me this is 120V unit...if thats the case a single pole breaker is sufficient. Also by what you have written, a 15 amp breaker should suffice.
Jun 22, 2009 | Spa Parts Plus GFCI, Circuit Breaker, 30...
Properly installed electric baseboard heater won't work.
I am an electrician. You must measure the voltage across the black and red wires. Measuring each wire to the neutral will not cut it. If both your red and black wire are on the same phase the heater will not work.
To double check your wiring, measure the voltage across the two screws feeding your subpanel, they should be 240v or 208v depending on your power company. Then do the same at the breaker feeding your thermostat. Again it should read 240v.
If you have no potential across the screws it is possible that you installed an incorrect breaker. Not all breakers with two screws on them are 240v breakers. There is what is called a twin or split breaker that has two screws that are on the same phase. These are for wiring two 110v circuits, when you run out of spaces in the panel.
Double check everything. This is a relatively easy circuit to wire, even for homeowners. If the heater does not work them something is wrong so do not leave the circuit energized.
Nov 22, 2008 | Fahrenheat Electric Convector Baseboard...
Generator electrical
On a 230 volt std hook up here's the way it is supposed to work. From black to white you should get 115 volts. From Red to white you shoudl get 115 volts. From red to black you should get 230 volts.
Concentrate on getting the correct output from the generator with the load to the house disconnected
This should be 115v (black to white, 115 volts red to white and 230 volts red to black.
On the load side (ie, the house connected) what are you using? 115 volt lights, etc on one side of the
230 volts, and some other 115 volt loads on the other side.. Are there any 230 volt loads. It could be
that one side of the 230 volts (ie, a 115 volt side is drawing a lot more current than the 2nd 115 volt leg.
Get back with me on just what the loads are botth 115 volt and 230 volt . also what are the rating on the circuit breakers.
Loringh
Oct 28, 2008 | Electrical Supplies
Subpanel
YOU WILL NEED A 2 POLE @ THE HOME PANEL AND ANOTHER @ THE BARN PLUG THE ONE @ THE HOUSE AS YOU NORMALLY. WOULD PLUG THE ONE @ THE BARN ONTO THE BUSS IN THE MLO PANEL AS IF IT WERE TO BE A FEEDER BUT INSTEAD PUT THE 2 PHASE WIRES ON IT , THIS WAY YOU WILL HAVE A MEANS OF DIS-CONNECT AT THE BARN AS WELL, YOU WILL STILL NEED A GROUND ROD @ THE BARN TO GND THE MLO PANEL AND ALL RECPT SHOULD BE GFCI RATED FOR SAFETY AS FAR AS THE WIRE SIZE DONT KNOW LOAD , BUT A GUESS WOULD BE A # 4 COPPER TRI OR A # 2 ALUM SHOULD HANDLE WHAT YOUR GOING TO DO , JUST A GUESS .
Oct 22, 2008 | Electrical Supplies
Electrical Supplies Logo
137 people viewed this question
Top Electrical Supplies Experts
Steve
Gene Haynes
Are you an Electrical Supply Expert? Answer questions, earn points and help others