Discharge pressure reading 150 psi and suction reading 70 psi what could cause this problem on a heat pump? this is a r22 system
  • Bill Long May 11, 2010
    Are you running the unit in heating or cooling and what is the approximate outdoor temperature.
  • jdthefixer May 11, 2010
    The pressures will depend on the outdoor ambient anf indoor load condtions. Is the heat pump operating in the heating or cooling mode? The pressures you list aren't that far off for an R-22 system. What is the specific issue?
  • 3 Answers
What is the Problem?,
Can you discribe, or give more details about the Problem ?
Posted on Jul 03, 2010
  • 116 Answers
Need to know the room temp and out side temp but the expansion valve could be sticking open or the compressor could have bad valves hook up hi side hose to true high side port and shut the liquid valve off in the line set in cooling mode make call for unit to come on and as it pumps down the hi side should go up if not the comp is week but if room temp is 85 or higher and out side about same still low on charge the suction will fall when room cools and the expansion valve quits flooding the coil
Posted on May 10, 2009
  • mike bare May 10, 2009
    check the temp on lines from rev valve switch it manually from heat to cool by pulling the wire most are energized in cooling make sure low side Gage is on direct read port not on suction lie because it becomes discharge in heat mode
65 PSI TO 70 PSI IS THE SAME SUCTION PRESSURE FOR ALL TON SPLIT AC OR THERE IS DIFFERENT SUCTION PRESSURE IN ON CONDITION?
Your suction pressure will always vary depending on many variables. What type of freon??? If you find your freon type on a PT CHART(PRESSURE/TEMPERATURE), 65-70 psig will have a temp that is 38-41°f. Most evap coils should be a bit warmer but not much. BUT, again variables! Coils are clean, indoor temp, blower speed, return air opening, supply ducts. Also superheat should be a factor. If you have 65-70psig, that freon temp(per pt chart r22) is 38-41°f, then using a temp sensor/meter to measure the actual temp of the suction line. Subtract 38-41 from the actual temp and that give us a superheat reading. This # should be around 8-12°. But again variables! If the unit has an expansion valve? Seems like you are close if its r22.
Aug 05, 2015 | Heating & Cooling
WHAT IS REFRIGERANT SUCTION PRESSURE OF MY 1 TON SPLIT AC?
R22= 70-80psig
R410a=120-130psig
Depending on many variables such as blower speed, coils clean, indoor/outdoor temps.
Aug 05, 2015 | AMVENT 18000 Btu 1.5 Ton Ductless Mini...
What would cause high suction pressure 134a Freon?
to start with it will be high vacuum reading as suction is low pressure
secondly it means that the system is vacant of any gas and is well below 0 psi
if it is a high discharge pressure ( after the ac compressor) it means that the condenser is not being cooled by the fan or you have excessive gas in the system or the tx valve is blocked
I strongly suggest that you seek the services of an accredited ac specialist shop as r134a gas runs at a lot higher pressure that the r12 or r22 gas before you do serious damage to the ac compressor and system
Jul 19, 2015 | Cars & Trucks
No suction pressure at condenser test port
i would suspect the valve on suction side not open. if the other system failed on a burn out you could have a blocked dryer or orfice at coil.
Apr 20, 2014 | Goodman CLQ36AR49 Air Conditioner
Unit is freezing up
what type of gas?
if R410A it too low
if R22 check for inside air flow
Jun 23, 2012 | Gibson Nordyne/2 Ton Heat Pump Package...
The best pressure of gas in a split ac in
65 psi is the ideal pressure remember its not exceede from this pressure.
and it is valid for all season
Jun 05, 2010 | LG LSC121PMA Split System Air Conditioner
I am working on a coleman self-contained a/c which is low on charge. it is for my sisters mobile home, what should the pressures be. Any other ways to check charge? The model # is 7330D901. Thank you very...
If it uses R22, with a 70F to 75F indoor temp, and a 70F to 80F outdoor temp, I would think the suction pressure would be 65 to 70 PSI. Liquid line pressure might be 200 to 250 PSI. On a warmer day, they could be higher. Granted, those pressures are for the cooling mode. If it is a heat pump, the pressures will be higher in the heating mode.
Jul 07, 2009 | Coleman Heating & Cooling
My pump is running however it's pressure is less than 10 psi and the heater on the pool will not run.
With the Jacuzzi Magnum pool pumps, low pressure is going to likely be cause by one of the issues below. Try these troubleshooting tips.
1.Pump not primed
2.Leakage of air into suction system
3.Impeller clogged
4.Valve in suction or discharge line partly closed or suction or discharge line partly plugged or too small. 5.Plugged basket in skimmer or hair in lint strainer.
6.Dirty filter.
Jun 06, 2009 | Jacuzzi MAGNUM POOL PUMP 1-1/2 HP MAGNUM...
Two lennox heatpump 71/2 tons
check the true psi with the line psi to see if same if psi is good in cooling 225 hi and 70 low on 80'day then compressor is fine and i would start checking for temp difference on the reversing valve sometimes this will cause high suction or high discharge psi shift it manually with by energising it be cooling or heating then pull wire and see how it shifts if shifts good then txv on out door unit could be bad what is the psi in heating on the discharge line going to the indoor unit? most prv's are set at about 350 psi r22 as for suction line size its only hot gas in hp mode os no problem their shows in cooling mode as low suction psi ..hope this helps some also make sure indoor coil is clean!....thanks & rate me
Apr 19, 2009 | Ruud UBHC Air Conditioner
Normal operating pressures
Normal operating pressures will change as the freezer reaches the selected temperatures on the inside. Normals of minus 14 degrees on the inside would be around minus 4 psi on the suction and 150 pis on discharge. Now checking the pressure will require a set of guages that have been purged with the same freon before connecting with the suction line on freezer. If not purged the suction line will draw outside air into the system and cause freezing of air and moisture inside the capillary tube rendering the freezer inoperative, Hope this helps, Sea Breeze
Nov 01, 2007 | Freezers
Heating & Cooling Logo
1,332 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Donni Steen