Have a Pentair MiniMax CH 200M Pilot lights but will only occasionally fire up all burners.
  • 3,037 Answers
First, the normal color of the pilot flame is blue. When the flame appears yellow, burners should be inspected and cleaned. Is your heater pilot blue or yellow?
If the pilot seems fine, then I would test the ignition module. The good news is that if you are electronically inclined, I have a manual with the wiring diagrams so you can see how everything is wired up in order to test the parts and I also part numbers on it. So please check the ignition module if the pilot seems fine and use the manual to further branch back from the ignition module to find out why the burners don't all light. Another possibility to look into is gas pressure to all of the burners. Here is the manual on the following link.
http://www.propools.com/instructions_owners_manuals/MiniMax-CH.pdf
Let me know of any further questions.
Benjamin
Posted on May 09, 2009
How remove a pilot generator from a minimax ch 200m
shut off gas supply. undo gas line union. remove wiring from gas valve. undo burner tray support screws. slide burner tray out. remove pilot generator leads from gas valve. pull out pilot generator from pilot assembly. then re assemble
Aug 17, 2014 | Pool & Spa
Where can I find helpful instructions for replacing (removing old and installing new) thermocouple on Pentair 250k minimax ch NG mv? Thank you.
Simple:
  • Insecure bracket holding the pilot assembly to the burner tray
  • now, remove the pilot assembly from bracketry
  • unscrew old pilot generator/thermo pile or thermocouple
  • new may have a clip instead of threaded nut
    • diameter of hole is same so it should just snap into place
  • in reverse order resecure the pilot bracket to burner tray
May 30, 2014 | Pentair 250k Minimax Ch Ng Mv Heater
Why is water dripping on burners of pentair minimax ch 200m?
bad heat exchanger or you have condensation this happens when the temperature delta is too high
May 21, 2014 | Pentair Minimax CH Heater
Pentair 250 pool heater
check gas pressure and when it goes out check voltage from transformer
May 28, 2013 | Pentair 250k Minimax Ch Ng Mv Heater
I have a Pentair Minimax CH 250M pool heater. When I opened my pool, the heater started up fine and heated the pool initially. However, since the initial heater it has not come back on, and the pool is...
Do you have 24V at the brown wire of the gas valve? If you do then it is probably a bad gas valve.
If you don't have 24V on the brown wire it is probably the ignitor.
Jun 04, 2011 | Pentair Minimax Ch 250,000 Btu Natural Gas...
I have a minimax 250 i can light the pilot but the main burner will not light. i jump the th to th/pp and the pilot goes out.
are you sure your jumping th and th/pp? the labeling on valve is a little deceptive.should use 1st and 3rd terminal on gas valve. if your using correct terminals try same thing with thermostat wires disconnected from gas valve. this will isolate valve from all controls and safties.if it fires valve is good and need to look in thermostat loop for problems. hope this helps
Jul 18, 2009 | Pentair 250k Minimax Ch Ng Mv Heater
Main burner not lighting
Could be bad coupler or pilot valve is not staying up due to bad spring. If the light does stay lit at all, then the problem is with the fuel.
You can get the entire pilot assembly for $70 at poolcenter.com
Jul 05, 2009 | Pentair 250k Minimax Ch Ng Mv Heater