Question about Carrier Heating & Cooling
Connecting replacement fan motor in HP condenser
I am replacing a fan motor on the condenser unit of a Carrier heat pump. The motor I am replacing is a GE P612S, 1/12 HP. The new motor is a Dayton 4M261J, 1/6 HP. Other than that the specs are about the same. The capacitor and wiring set-up of the motors is different and my problem is I don't know how to connect the new motor/capacitor. The old motor had three wires and the new has four wires. On the old motor, the Brown and Yellow wires went to different terminals of a three-terminal capacitor, and the black wire (marked line) clipped into a circuit board. I bought a capacitor for the new motor, and it has two terminals which are unmarked. The new motor has 2 wires marked for the capacitor, a brown and a brown-white pair. It's black wire is marked for line 2 and it has a purple marked common-line 1. So, I have some ideas on how to wire the new motor into the existing set-up, but I really don't know the right way. With electrical components, there is often only one chance to do it right. I will appreciate it if somebody can enlighten me on how to tie in the new motor.
  • Chip Walsh
    Chip Walsh Nov 29, 2013
    I am replacing the fan motor, not the compressor motor. I have only removed the three wires that were connected to the fan, so wiring for the compressor has not been disturbed.
    Burzerko, where is the fan motor in that diagram? And the thing with three terminals at bottom right is labeled "compressor," right? The diagram doesn't seem to show the three-terminal capacitor. The item on the left side with an arrow to the red dot, is it the run capacitor? With the label in the middle like that, I can't tell what's what. Sorry, I am a duffus when it comes to reading electrical diagrams. I did see this diagram on another thread about capacitors, but it is unclear how it relates to my issue.
  • Carrier Master
  • 17,099 Answers
What is the model number of the heat pump? What is the voltage that you are dealing with?
Posted on Nov 27, 2013
  • 7 more comments
  • Chip Walsh
    Chip Walsh Nov 27, 2013
    The model number is 38YC024310 and the motors are marked 208-230v.
  • Brad Brown Nov 28, 2013
    That new motor should have a diagram on it. The wiring for the heat pump ishttp://www.docs.hvacpartners.com/idc/gro...
    you should look at the first example
  • Chip Walsh
    Brad, having the wiring diagram doesn't help me that much since I need to add a capacitor that is not in the wiring diagram.
  • Chip Walsh
    Berzerko, thanks for the wiring schematic, but I can't ID a three terminal capacitor or a fan motor in the diagram.
  • Chip Walsh
    B Carson, I haven't monkeyed with the compressor wiring so I'm not sure how your solution helps me wire the fan motor.
  • Brad Brown Nov 29, 2013
    Chip,
    Add a Comment What was the link to the diagram that berzerko listed, I dont see those comments.
  • Chip Walsh
    Chip Walsh Nov 30, 2013
    Crazy, but I don't see it either. I did see the same diagram in another thread here, and the fellas name is birzerko. Sorry for the confusion.
When the heater is on, should the fan outside on top of the unit also be working along with the blower from the heater ? When the heater is off, cold air is comming from the vent's, can I cover the
No. This is strictly a gas package unit, not a heat pump. the condenser fan motor should NOT run when their is a call for heat from the thermostat. The condenser fan only runs with the compressor on a call for cooling. Hopefully the compressor is not running @ the same time, but if it is, it would make sense that the contactor for the compressor & condenser fan motor is stuck closed OR the low voltage cooling wires are shorted straight to a 24Volt control wire.
Jan 15, 2015 | Carrier Heating & Cooling
Condenser fan on heat pump does not turn off
If it is just the condenser fan that means you have a fan relay that has welded shut. Turn power off to your unit and trace the wires from your condenser fan back into the control panel at the unit. You'll have 3 wires going to it. 2 go to the run capacitor and one goes to the fan relay. The one that goes to the fan relay is the part that needs to be replaced. If you have no fan relay and it goes to the main contractor, half of your main contractor is welded shut and will need to be replaced.
Sep 18, 2014 | Carrier 52PQ-515---3 Premier Series Heat...
Need the motor size on a carrier 38SQ940311
Carriers usually have a 1/4 HP condenser fan motor.
Jul 19, 2012 | Carrier Heating & Cooling
Carrier 48NMX042 IFM wont stop, condenser fan motor and compressor wont run
Ok first thing is it sounds like a wiring problem. So first step is to make sure the thermostat is properly connected. Which... the main thing here is there needs to be 24v dc power coming from your control board (transformer) going to the thermostat..generally that is the red wire. All the thermostat does is connect that "red" wire (power) to one of the other wires to complete a circuit. So make sure you have 24 volts... (generally about .5amps) . if you have power than switch thermostat to fan only should energize the green wire only. then switch to ac and move temp low enough that the ac should turn on and that should energize the yellow wire. for sure one of those wires is incorrect now or the fan wouldn't be on OR THE THERMOSTAT IS NOT CONNECTING THEM AND IT IS BAD. Now about the compressor and fan.... those same wires run out to the compressor unit... ok the yellow for ac.. greeen does not go to compressor unit that is for fan only (vent).. red carries the same 24 volts... one difference here is that most carrier units only have the one transformer....so you run the red wire is the +pos 24 volt..and then a "common " wire is needed which is the Ground or neg... that wire on a carrier is brown usually but could be different depending installer. The orange wire goes to the pump reversing valve it is always energized when on ac mode...when heater is on in the winter it is heat pump and is not energized so just connect the orange and yellow together... tell me more specifics if this doesn't help and i'm sure I can help you... thanks Chuck
Jun 22, 2012 | Carrier Heating & Cooling
My fan motor on a carrier 38ycc024310 has been changed two times should i replace the heat pump or is there an electrical problem
Most Carrier units use smaller horsepower motors with less rpm.
If a universal motor was used that may be your problem.
Check the specs listed on the unit and replace with the correct motor.
Also replace the capacitor.
Dec 18, 2010 | Carrier 38CKC042 Air Conditioner
Condenser Fan and Compressor not turning on.
Are you sure you have high voltage going to the unit? One wire from fan lands on top left of contactor, the other two go to C and Fan on capacitor. Manually push in contactor, if no fan than no high voltage.
Jun 05, 2017 | Carrier 38CKC060 Air Conditioner
When the unit is in heat mode is the fan on the outside supose to run? Capacitor on outside and inside have been replace fan was running when capacitor was first replaced.
Hi, and the outdoor condenser fan should not be on at all in the heat mode unless this is a heat-pump!! So, I can see that this is a 3-ton Carrier split system and I haven't pulled up any information on it, only if I need to. But if the indoor unit runs on natural gas/propane, this would not be a heat-pump and the outdoor fan would run only in the cooling cycle. So, if it is not gas fired it is a heat-pump, and yes the outdoor unit should be up and running all year around. On a heat-pump you will have what is called a reversing valve in the refrigerant system that directs the flow of freon in the right direction for the season you are in. Most all heat-pumps will have a heat strip package installed in unit for emergency and aux. heat if compressor lets say fails. You're thermostat will have on it a selector switch, you will see on it these labels, Aux., emergency heat, auto/on/off/heat/cool. You will know from what I have just went through with you what you have. Forgive me for such a long explanation as I like my customers to understand more about there units in question. I could have just said yes or no and thanks? Doesn't work like that for me. I hope this has helped you out. One thing, If you determine this is a heat-pump and the fan is not on when in heat, you may have lost this condenser fan motor? You say both run caps. were replaced, and normally when you loose a run cap for a motor they will open internally, leak, buldge ect. So if this is taking place, if you can yourself take a look at the run cap. Also, make sure you have 220 volts to condensing unit. If not, check breaker probably a 30 amp double pole to see if it has tripped. You will have a disconnect box at the unit and inside there will also be 2 fuses. If you see only a pull out square connect, the fuses are still there but in behind the cover. If you have power and can hear the compressor come on but fan does not, I am positive you will have A faulty run cap, or faulty motor. Kill power to unit and try and slide a metal coat hanger down to prop or blade to see if it spins freely. If it is hard to turn bearings are froze up. If the capacitor seems to look ok, and the motor does spin free, It still may have open windings. Do these checks I have asked of you on power to the outdoor unit. If all is good, Stand in front of the unit and have someone turn the stat on for what season you are in. Lower or raise temp a ways above or below room temp. You should her the contactor close and compressor will start along with the condenser motor.If compressor starts and motor does not, then I would say it has failed and or cap again. When a motor is replaced, the run cap must always be replaced to!! Please get back to me and keep me posted. I will wait to hear what has happened. Good Luck.
Sincerely,
Shastalaker7
Jan 13, 2010 | Carrier 38CKC036 Air Conditioner
Air on heat pump not cool outside unit humming but not kicking on
This could be an inoperative condenser fan.System will kick off on high pressure without proper air flow.The hum indicates voltage is present. Providing the fan motor is not locked up and will spin,Check your run capacitor which helps boost the motor voltage initially and will get it turning.If the cap is good,you may be faced with motor replacement....good luck
Aug 19, 2009 | Carrier 38CKC042 Air Conditioner
Motor good and not running possibly bad relay
hey there, it seems you know a little about the troubleshootig. The first thing you need to do is see if the rela is trying to energize by checking for 24v accross the coil while it should be running. I am guessing that with a 1/8 hp this is the condenser fan motor (outside). If you are not getting 24v at the coil is your compressor coming on? You may have a safety switch with a manual reset (usually red button) on the piping under the fan motor or just a broken wire. If this is a heat pump and the relay is located on the circuit board and the compressor is coming on,chances are the board is bad. If you only have 2 stat wires coming into the unit, check for 24v on them wait for any time delays. If it is there and at the coil replace the relay. If the 24v is not outside at all, check iside or try different collor wires, one may be broken. If still no 24v, take the tstat off the wall, turn off both units to kill power, twist the wires from terminals G, Y and R together. This should bring it on. If this is the only way to bring it on, replace the tstat. Also, there may be a float switch in a condensate pan somewhere on the indoor unit. If the pan is filled with water, it will either kill the whole 24v circuit or just keep the outdoor from coming on. Let me know what you find
seth
Jul 31, 2009 | Carrier 38BRC048 Air Conditioner
Heating & Cooling Logo
154 people viewed this question
Top Carrier Heating & Cooling Experts
Dan Webster
Dan Webster
Bill Long
Are you a Carrier Heating and Cooling Expert? Answer questions, earn points and help others