A carrier furnace model 58dla110---10122 won't start
I turn on thermostat a no response from furnace. Ignitor doesn't light on no inducer motor action please advise
    New Friend:
    Cheetah:
    An expert who has answered 20 or more questions within one hour.
  • 46 Answers
Make sure the kill switch on the blower door is closed, or furnace won't do anything. Then remove power from furnace for a few seconds, then try again. Still no go? Take a jumper wire and jump the "r" terminal to the "w" terminal on the furnace's board. This bypasses the thermostat. This is only for testing. If it still wont run, call service guy. Gas furnaces are not good things to tinker with.
Posted on Nov 27, 2013
4 Suggested Answers
  • 582 Answers
SOURCE: I have a Ruud 90 Plus Model UGRA furnace and blower starts immedi
NO BECAUSE THE BOARD IS TELLING THE FANS TO STARTARE THE CONTACTS FUSED TOGETHER OR STUCK IN THE CLOSED POSISTION CHECK THIS FIRST
Posted on Aug 10, 2009
milten1
  • 1304 Answers
SOURCE: goodman gmpn100-4 ignitor lights, burners don't ignite
1 blink is ignition failure
without being able to do voltage checks
i would reccomend checking your igniotor, if you can put an amp meter on it, it should read 2.6-3.4 amps
if you cannot do that, Or check voltages I woudl repalce the igniotor, gas valves do go bad but very few and far between....
at the risk of a bad rating you deserve at least an answer...
if i were called to your house with this complaint I woul not bother comming with out the ignitor
just because the igniotr looks likes its hot,, it may not be hot enough to safely open the gas valve
Posted on Oct 25, 2009
shastalaker7
  • 1515 Answers
SOURCE: no heat coming from furnace,
Hi, this unit if you say hot surface ignitor has no standing pilot for you to light. Yes, the fan will run in the on position. Turn it back to auto. Leave it off. You will need 2 people, this will be easier for you. Go to the furnace and see if you have a round inspection hole to look through. If so, see if you see a red led light. Yes or know. Remove the panel to where you can see the circuit board, burners lined up and so on. Some units have a panel switch on them so when you remove the panel, it kills power to everything. It would be around the perimeter and you will need to tape it down real good. Now, have someone turn the thermostat to auto/heat and turn the heat up high. I know this is a Carrier with a hot surface ignitor, so you should be hearing the small inducer motor start running. If you did have a red led light and it is flashing, you will have a code sheet glued to the panel, a error sheet to tell you what is wrong, like if its flashing 3 times fast and 1 time long and slow you would look at chart and it will say what to look for. Some units have them and some don't.Anyway, the inducer motor comes on first, it has a clear plastic tube coming from it going to a pressure switch. If the motor is on and the tube is clean, no water, condensation in it, it goes to the switch and closes the switch.When it closes, it will send a command to the main controller, circuit board or a module to send power to the hot surface ignitor, which will glow and send a signal back to open the pilot valve(PV). There is a porcelin flame sensor next to the ignitor that has a metal tip which heats up and tells the main gas valve the pilot is on to open up and send gas from the 1st burner over to the 2nd and so on. This is the sequence of operation. We know the stat is good, and the blower motor is also good, so all we need to do is find out why the furnace wont light and run. It may have a flame roll out switch on it that has tripped. It has a reset button on it. Make sure the gas valve and gas is on before you do this test I am walking you through. Try to have a helper. Remember the door switch if it has one. This should be a easy fix, so get back to me and keep me posted on what is going on. I will wait to hear from you. You can do this.
The best to you,
Shastalaker7
Posted on Apr 11, 2010
Changed inducer motor, now furnace will not ignite and gives code 31
since there is no model number to go by, let's go generic. Most inducer motors have some way of "proving" it is running to the control board. It may have a centrifugal switch in it or it may have use some type of air pressure switch. The centrifugal switch will usually have 2 wires other than the power wires and most of the time, go to the rear of the motor. The air switch usually has a small rubber hose that pushes onto it and is connected to the fan housing.
Aug 06, 2017 | Carrier Heating & Cooling
Heater does not come on gms80703an
There are too many reasons for this to happen so we would have to narrow it down. The sequence of operation on a Goodman furnace is usually:
1: Inducer draft motor comes on
2: Hot surface ignitor comes on and glows
3: Gas valve opens, lights burners
4: Flame sensor detects flames
5: Blower comes on
If the inducer motor never came on, then you start looking at power to the unit, thermostat issues, or inducer motor issues. Just a few places to start. Hope this helps!
Dec 05, 2013 | Goodman Heating & Cooling
Carrier Furnace won't start up
Sequence of events: call for heat at T-stat, inducer motor turns on, negative pressure created in heat exchanger closes pressure switch, pressure switch control wire runs through all safety's (these must all be in closed/safe position) if ok then glow plug lights. Time delay then gas valve opens, flame verified by "flame rod" t-stat = :)
Apr 22, 2013 | Heating & Cooling
Furnace was working fine and just stopped working...it reacts to raising the thermostat but doesnt actually flame on
This is probably a ignitor.
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution:You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks.Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. Please see "limits, rollout switches & furnace control boards" further down on this page. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Please leave feedback... Thanks...
Jan 28, 2011 | Goodman GMS90703BXA Heater
Induction fan motor cycles on and off , with no call for heat
Problem: Your furnace will not ignite the gas to produce heat for your home. When a furnace has a bad ignitor what I see most of the time is the following sequence of operation:
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution: You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Nov 26, 2010 | Heating & Cooling
Rheem 3204-80D furance. Turns on and fan starts. Then in about a minute the fan shuts off.
I AM WORKING ON A CARRIER 90% FURNACE. IT WILL NOT FIRE UP. IT SHOWS A 34 CODE. THE IGNITOR DOES NOT ENERGIZE FROM THE BOARD. NO POWER COMING FROM THE BOARD. I HERE A CLICK AS IF IT IS TRYING BUT NO...
4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution: You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. Please see "limits, rollout switches & furnace control boards" further down on this page. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Nov 25, 2010 | Heating & Cooling
Carrier 58sxc120 won't ignite and I get a fault code blinking light of short long short don't know what it means.
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution: You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. Please see "limits, rollout switches & furnace control boards" further down on this page. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Nov 24, 2010 | General Heating & Cooling
Hot surface ignitor won't ignite,I replaced the igniter and it still won't.
Oct 25, 2010 | Heating & Cooling
Gas Furnace will not start when outside temperature rises to 50F
There is a pressure switch near your draft inducer motor that needs to close when draft inducer motor is running. Verify that the switch is closing. If it is not closing, you might have a problem with either the switch itself, or there could be some sort of blockage in your flue. I would start with the switch first. This switch has to "prove" before it will allow anything else to happen. The loud click could be from your switch or your gas valve. If the switch is closing and nothing else is happening, it could be a problem with your gas valve or HSI.
Mar 12, 2010 | Carrier XHB123D X/Y Series Heat/Cool Air...
Heating & Cooling Logo
133 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Tim Whalen