Baxi boiler Baxi he 24 solo. Local Gas safe Engineer has replaced pcb, condensate trap, overheat and other thermostat, also igniter/sparker and flame failure sensor, Boiler still intermittently locking out (red light). He's scratching his head, suggest gas valve. Spending too much without resolution, any Ideas?
    Master:
  • 571 Answers
Make sure the gas inlet & outlet pressures are correct (manometer) & that the primary air mixture is adjusted correctly. Check to make sure you have 1 square inch of outside air for combustion per 2000 BTU's rating on the boiler.
Posted on Dec 12, 2013
I have a baxi combi boiler which wont start and trips the electric..plumber has changed fan,ignition and now pcb to no effect...help!
Start by diconnecting main supply to Boiler (at the boiler input) and see if it trips the electric. This would point to fault in wiring from board to boiler.
Then check several points with meter to find short-circuit.
If not, then you have to TURN OFF THE GAS SUPPLY and connect and disconnect items such as solenoids, switches, board etc; until you find what causes it to trip.
Nov 18, 2014 | Heating & Cooling
Baxi he 24 solo. Local Gas safe Engineer has replaced pcb, condensate trap, overheat and other thermostat, also igniter/sparker and flame failure sensor, Boiler still intermittently locking out (red...
Sounds like its an intermittent flame failure on trial for ignition. Look for the pilot flame drifting away from the sensor when the main valve opens.
Nov 24, 2013 | Heating & Cooling
Baxi duo-tec boiler - when water comes on flame roars up. When i put the heating on the flames roar for 5 minutes then die down.
is the boiler a combi if so have you checked the pressure. it needs to be at 1.5 bar 2 bar at the most . also check that the heat the boiler is producing is completeing the circuit on the heating if you have access to the pipe work there should be 2 or 3 22mm copper pipes. now turn the heating on and check which one is getting warm. the one that is is your flow and in about 2 to 3 min there should be one more pipe getting hot let me no if this is the case
Oct 27, 2012 | Universal 900MM Super Thermocouple Baxi...
I need a manual for a baxi solo he 15 Help !!!!!!!!!!!!!
http://www.plumbnation.co.uk/site/baxi-solo-24-he-boiler-natural-gas/Baxi%20Solo%20User%20Guide.pdf i hope this will help
Feb 09, 2011 | Heating & Cooling
Baxi solo pfl60 problem. the boiler has for some time been doing this - the fan starts normally when demand is present, then the pilot ignites, then it all shuts down. this happens repeatedly about 6 times...
One thing I would check is the flame sensor. Your boiler may not have this on it but I have seen them act like this before. If you have one I would replace it. Hope this is ofsome help. Thanks
Nov 26, 2010 | Heating & Cooling
How to light pilot light for baxi bermuda sp3
Go to this link.Bottom of page 15 on the manual
http://www.aroundtownflats.com/manuals/Boilers/Baxi/BAXI%20BERMUDA%20SP3%20GCNo.37-077-63.pdf
Basically it says (turn on the power first) Turn the knob to the the star/flame marking. Push the knob in, hold it for approximately 10 seconds. Release and check the small flame is lit. Now turn it to your desired heat setting.
Jul 21, 2010 | Heating & Cooling
Baxi solo340p overheating no control
the gas valve is just a valve that open and shuts which lets the gas in,
the cylinber stat controls the hotwater
there must be a thermsat on the boilet that controls the water temp and a overheatstat thats controls the boile which should shut dow in the event of overheating if you go to the baxi wedsite you can down load the info for your boiler
Jan 15, 2010 | Heating & Cooling
Baxi solo 3 70pf boiler problem
This happened to me and it was a rubber pipe inside had perished so it was detecting a loss of pressure. You can see it if you take the main cover off and also the front clipped on cover. Its at the top on the right. You need to replace it with heatproof pipe. Good luck!
Dec 31, 2009 | M20 X-Treme Radar Detector
Baxi 3 Solo Boiler will not ignite
it could just be the presure switch try bridging it out and see if burner lights
Sep 10, 2009 | M20 X-Treme Radar Detector
Baxi solo 2 30pf will not fire up.. please help!
first off ensure water is getting to boiler, next, No pilot = pressure switch. On my baxi solo 40 pf pressure switch is replaced 8-10 times a year cures your problems,,,,,,,, momentarily , and have had all your other parts,but with no effect to speak of,.......sorry............ solution = [ change boiler ].sounds like gas pressure or lack of water to system or **** boiler like mine .........good luck.
May 15, 2009 | Water Heaters
Heating & Cooling Logo
113 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Donni Steen