I have a Carries AC unit (model FK4CNF002). Heat pump in the outside works but blower doesn't (tried both heat and cool). Power load (240V) on the blower is there and I also measured the voltage on control board terminals and they seem to have 26V voltages. The transformer feels hot. Any help and suggestion on what I should be looking next will be greatly appreciated.
    Top Expert:
  • Carrier Master
  • 12,962 Answers
If you have determined that the line voltage is getting to the blower motor then the unit is defective and needs to be replaced. Check for the presence of the voltage at the wires going directly into the motor to make sure. It is not the compactor relay because it supplies power to both the compressor and condenser fan. If your air handler is inside the house, the housing also has circuit breakers for the fan motor - check that also.
Posted on Nov 24, 2013
SOURCE: Reverse Cycle not cooling!
I had a service man come out and he said the compressor was not coming on so he installed a hard start in parallel with capacitor solving the problem and is working normal now.
Posted on Dec 01, 2008
  • 56 Answers
SOURCE: problem with my AC unit
Hi Phillip,
Check your thermostat wires to see if you have any of them which are bare and touching. If any are touching separate them and tape em up and try unit again. You have a direst short in your cooling portion of the unit.
Posted on Feb 12, 2009
  • 26 Answers
SOURCE: I have a goodman furnace and ac unit the fan and
Look at the contactor on the condensing unit, remove the low voltage wires to the contactor and turn on the system. If the low voltage fuse doesn't blow, replace the contactor.
Posted on Jul 07, 2009
t1m130
  • 86 Answers
SOURCE: Blown Transformer heat pump
blown transformers are usually from a low voltage short the first thing i would do is wire a automotive or resetable 3amp fuse in line with the transformer so you dont blow transformer after transformer the wire coming off the transformer that say 24v take that wire a couple of inches down and cut it and install the fuse in series there
24v----------------
24v----------x----------
24v--------{3ampfuse}----------
now you can go through your low voltage wires one by one and test them unhook all the wires to your outdoor condenser at your indoor unit(furnace or airhandler) and try turning it to cool now if you blow the fuse the short is between the tstat and the indoor unit if the fuse is still good leave it on cool and hook up one wire at a time to your outdoor unit starting with R a lot of times your contactor or your defrost board will short out on you also look for pinches in wires wires with cracks in the insulation and wires touching metal this situation can be a real pain sometimes i would recommend calling a hvac company if you start to get stumped
hope this will help you
Posted on Jul 26, 2009
hvac1960
  • 2133 Answers
SOURCE: Amana PTAC unit will not
Compressor working ?
Please follow this tips:
To get proper cool, keep the tips as follows:
1. Check air filter is cleaned. 2. Check indoor coil is cleaned. 3. Checkindoor blower motor is working. 4. Keep in cool mode. 5. Set temp minimum 3degrees less than room temp.6.Check compressor is working with correctpressure.
Please specify, if any error code..........
Thanks. Helpful?
Posted on Jan 19, 2011
Fan doesn't work in heat mode it works on all other functions. Heat does come out but fan doesn't kick in. Outside unit is operating
AC inside fan doesn't come on AUTO - DoItYourself.com Community Forums
www.doityourself.com > ... > Air Conditioning and Cooling Systems
Jul 21, 2004 - The inside FAN doesn't run when in AUTO mode. If I leave ... Is the thermostat not working correctly or something in the AC unit causing it to do this? Thanx ... The unit is electric central air-conditioning(heat and cool). It made ... Carrier A/C condenser fan not working
Jul 27, 2012
Heater Fan Doesn't Work on AUTO
Jan 23, 2006
Blower doesn't work in ON position after repair
Mar 25, 2005
Central AC/Heat, Blower Doesn't work on Auto
Nov 30, 2004
More results from www.doityourself.com
Nov 01, 2015 | Heating & Cooling
Replaced Thermostat and now Blower Motor will not run
Sounds like a set up issue on the tstat. You say this is a packaged unit, inside the machine you should find where the tstat wires hook up. Typically red is power yellow is compressor orange is reversing valve white is emergency heat green is blower. Put red and green together, test blower. Then red green and yellow, make sure blower works again. If blower runs both ways it's either the tstat wire or tstat itself. Make sure you are landing wires on dedicated heat pump terminals, make sure in settings you are set up for heat pump with back up electric heat and TSTAT CONTROLS THE FAN. Good Luck. Also if there is a switch on the tstat for gas or electric on the back you want electric.
May 12, 2017 | Heating & Cooling
My Ruud heat pump/AC blower does not come on for cooling or heating. Both units work as does the outside fan unit. Blower is only thing that does not work. I noticed my KWH usage was more than double in a...
The blower/fan motor may be shot. The fan ON/OFF circuit switch, may be locked up or has totally failed. The only way to test it, is with a circuit tester to see if the fan is in fact getting power.
Hope this helps you troubleshoot the problem.
Mar 29, 2011 | Heating & Cooling
Outside ac unit operates but no blower. Fan "on" does not operate from thermostat. However "heat" works fine furnace and blower. ???
Go to furnace and shut off power, remove blower door compartment. Inside you will find a control board where thermostat wires are connected. Should look something like this:
R-Red Wire= Power
G-Green Wire= Fan
W-White Wire=Heat
Y=Yellow or Blue Wire=Cooling.
It sounds like you have a bad motor speed. So try this:
With Power Still Off, on the same control board there is a terminal usually marked Cool and Heat. There should also be a couple of terminals that are named park. The wires hooked to these are the fan wires..
Exchange the Heat and Cool wires on the terminal board. Put everything back together and try cooling again, if the fan comes on
then you have a burnt out motor speed. Go back to furnace and change
the heat and cool wires around, next if Cooling had the black wire hooked to it, put yellow or blue on Cooling and black to park.
Note: The reason why you put the blower door back on is because it
has a door switch that if not properly seated, you wont be able to power
up anything
Jun 22, 2010 | Heating & Cooling
I tring to change thermosat I can not remeber what color go where
Typical Thermostat Wiring for 4 or 5 wire Heat/Cool Thermostat (not heat pumps)
4 Wire Termostat
R = Red One Side of 24 volt Transformer
G = Green Blower
Y = Yellow Cool
W = White Heat
5 Wire Thermostat
with one transformer for both units
Rc One Side of 24 volt Transformer
Rh Jumper Rc to Rh
G = Green Blower
Y = Yellow Cool
W = White Heat
5 Wire Thermostat
With 2 transformers one for indoor unit
And one for outdoor unit
Rc = Red One Side of (outside) 24 volt (outside transformer)
G = Green Blower (outside transformer)
Y = Yellow Cool (outside transformer)
Rh = Blue One side of (inside) 24 volt (inside transformer)
W = White Heat (inside transformer)
COOLING ONLY Thermostat
G = Green Blower
Y = Yellow Cool
HEATING ONLY
R or Rh One Side of 24 volt Transformer
W = White Heat
Feb 09, 2010 | Heating & Cooling
How do you wire a honeywell round mechanical thermostat
What are you trying to wire up?
4 Wire Termostat
G = Green Blower
Y = Yellow Cool
W = White Heat
5 Wire Thermostat
Rh Jumper Rc to Rh
G = Green Blower
Y = Yellow Cool
W = White Heat
5 Wire Thermostat
G = Green Blower
Y = Yellow Cool
HEATING ONLY
W = White Heat
Feb 09, 2010 | Honeywell CT87B ROUND HEATING&COOLING...
I have a coleman Evcon model AH16-0 . I am
4 Wire Termostat
G = Green Blower
Y = Yellow Cool
W = White Heat
5 Wire Thermostat
Rh Jumper Rc to Rh
G = Green Blower
Y = Yellow Cool
W = White Heat
5 Wire Thermostat
G = Green Blower
Y = Yellow Cool
HEATING ONLY
W = White Heat
Jan 06, 2010 | Heating & Cooling
Trying to figure out thermostat wiring diagham on a split system
4 Wire Termostat
G = Green Blower
Y = Yellow Cool
W = White Heat
5 Wire Thermostat
Rh Jumper Rc to Rh
G = Green Blower
Y = Yellow Cool
W = White Heat
5 Wire Thermostat
G = Green Blower
Y = Yellow Cool
HEATING ONLY
W = White Heat
Jan 05, 2010 | Heating & Cooling
Hi- Can not tell if my unites are straight cool / heat or a heat pump.
if you look inside the condenser unit outside,see if you see the big reversing valve,if not it is a straight cool,heat, the heat strip ins in the air handler so you would have to take the side panel off and look for the heat stripe,my the way heat pumps also have a aux.heat stripe just in case it does not get cold enough outside,hope this helps you-mike