Blower comes on but no gas ignition, so no heat. What's the problem?
    Problem Solver:
  • 23 Answers
That sounds like the limit look for a little round thing with two wires with a button between the wires push it to reset it but there could be several of them even one buy the blower motor there is also a high limit in the center of the furnace all you see is two wires if that one is out you have to remove it two screws then just drop it on the floor it will free the numeral bymetal inside put it back on and you should begood
Posted on Dec 08, 2013
No ignition
Many have a small 3A fuse similar to a car type push in fuse on the main board.
Feb 26, 2014 | Modine Effinity93 - 260,000 BTU - High...
Fan on with gas or with hot exchanger
how do i know it the starter is bad on 2004 gmc envoy
Nov 08, 2013 | Montgomery Ward (223600UP) Heater
SR333LP turns on but does not heat
hot surface igniter may not be getting hot enough to ignite the gas
Jun 05, 2013 | Sta Rite Starite 333 Btu Propane Gas...
Laars LX 250 AGS Service error. Burners ignite the go out.
if connected 120 volt switch red and black wires its not rectification
Nov 17, 2012 | Jandy Laars Lt 250,000 Btu Heater
The pole buiding 24 in hanging Dayton sometimes the blower comes on like after 5 minutes after everything else kicks in and sometimes like when its supposed to and sometimes not at all?? All the electric...
I'm not sure whether this is a gas unit or not. With many gas heaters, the blower comes on when the heat exchanger gets hot enough and goes off once the heat exchanger cools. Other things are happening before the blower goes on. The blower is normally controlled by a "fan control thermostat". This stat actuates the blower when the furnace is hot enough so that cold air is not being blown around and allows the blower to run until the furnace cools enough to get out the remaining heat after the flame shuts off but not so long to again allow cool air to blow around. If this fan control is malfunctioning, you will get erratic runs from the blower or the blower may not run at all or run long or continuously. The fan control is the first thing to check.
Gary
Jan 31, 2011 | Dayton Gas Furnace Heater
Furnace does not come hot surface ignitor does not come on
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Dec 29, 2009 | Goodman GMS90703BXA Heater
Have a Goodman GMT070-3B which the vent motor seems to be sticking. I took apart and cleaned the brushes and reassembled. The furnace will come on only after what seems like the vent motor comes up to...
The whole assembly must be replaced.
The sequence of operation is -
Combustion fan purges the heat exchanger. A pressure switch verifies combustion air fan is running. Usually a 30-45 second purge before the hot surface ignitor glows, or the spark ignition starts.
Gas valve opens after 10-15 seconds and main burners light. Control board monitors for flame and shuts gas valve after 2-3 seconds if main burner does not light.
If burner does not light, some boards repeat this for 3 tries, then locks out and is reset by cycling power.
Air blower comes on after another 30-45 seconds after main burner ignition.
Times may vary based on the specific controller board. A flow chart and timing sequence should be located somewhere on the unit, usually in the fan compartment.
Dec 16, 2009 | Goodman GMS90703BXA Heater
Won't ignite
make sure wiring is correct for 220 vs 110 wired for 220 from factory if 110 see inside panel move wires ignitor is not getting hot enough
Jun 02, 2009 | Jandy LXI 400 NATURAL GAS POOL HEATER -
Modine Hot Dawg Heater Model HDS - Natural Gas 30 BTU - HDS30AS0111 Logo
186 people viewed this question
Top Modine Heating & Cooling Experts
scott bailey
scott bailey
joe creger
joe creger
Level 1 Expert
Mark Lanasa
Mark Lanasa
Level 1 Expert
Are you a Modine Heating and Cooling Expert? Answer questions, earn points and help others