Furnance lights and then burner goes out
Just replaced Ruud corsair furnace control board. Now igniter lights and burner lights but does not stay on. cleaned flame sensor but problem persists. can anything else be causing this?
    Master:
  • 571 Answers
I'm assuming this is a remote sensor... if so, you need to read the MicroAmps that the flame is generating. If it is anything less than 4, then either the flame is not hitting the sensor enough, or the sensor needs replaced.
Posted on Dec 06, 2013
No power
you have a low amp fuse protecting transformer. could be thermostat issues.
Dec 12, 2013 | Ruud Rheem Corsaire Control Circuit Board...
Rheem corsair. Just replaced control board and now igniter come on , burner lights but doesn't stay lit. Took out flame sensor and sanded and replaced. Still same issue . Is the sensor bad or can i
If the sensor does not I.D. a pilot, the furnace would not fire, so your OK to this point. The sensor needs to stay in a flame constantly once the main burners light. Sometimes the draft will cause the flame to waver and cause a shutdown. Also, if the blower fan does not start on time, the furnace will shut down. I would check for wavering first.
Nov 22, 2013 | Heating & Cooling
I have a RUUD Furnance with a piolet light. There
If you have a pilot, then this is an older furnace. Most of them use a 2 wire thermostat. Allot of the new digital, programmable thermostats require a 3rd wire - a common to the thermostat. Allot of old furnaces do not have a common terminal on the furnace board. It can be done, but takes a good technician. The way around this is to use a digital, programmable thermostat that will operate on straight battery. It will be stated on the thermostat package, saying it will operate with a common wire from the furnace or with only the use of the batteries.
Then make sure that you hook up the 2 wires to the "R" terminal and one wire to the "W" terminal, it doesn't matter which thermostat wire goes to which terminal.
Note: If you have a air conditioner installed, it will be a different story.
Sincerely,
Good Luck,
Paul Gibson
Mar 31, 2010 | Heating & Cooling
Ruud Silhouette II Gas Furnace, the furnace lights but will only stay on for a few seconds?? What could be the problem??
Bad or dirty flame rod.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Jan 09, 2010 | Ruud Heating & Cooling
Ruud IFC Furnace Blower comes on and stays running, never lites
Check on the circuit board for an automotive type fuse that is probably blown. These fuses blow because of a short in the control wiring. If the fuse is blown a lot of furnaces run the fan all the time as a diagnostic. You will have to find the short or it will just blow again.
Oct 04, 2009 | Heating & Cooling
Ruud Silhouette II Fails to Ignite
sounds like you have bad flame sensor or the sensor is in a bad postition. To get eliminate the lockout turn the power off to the unit and back on again. Look at the circuit board light and see what the troubleshooting code is.
Jan 13, 2009 | Heating & Cooling
I am working on an older reehm furnace a corsaire.
either the sensor is dirty or bad,clean the sensor first if that doesn'y work replace it
Nov 21, 2008 | Heating & Cooling
Heater lights for about 5 sec and then goes out
One flash on a Ruud furnace indicates failure to ignite. There is a viewing port on the furnace where you can watch the flame. If the ignitor is igniting the burner and then 2 or 3 seconds later, the flame goes out; you most likely have a flame sensor that is dirty or not working. Check to make sure you are getting gas. Check the connections of all wires to the control board. If the sensor is not part of the ignitor, see if you can get to it to clean it with a small wire brush. Make sure there is a good ground connection between the board and furnace frame. If the flame is not traveling all the way to the flame sensor, clean your burners. If the flame burns inside the burners, you may have weak gas pressure. Good Luck.
Sep 29, 2007 | Heating & Cooling
Heating & Cooling Logo
112 people viewed this question
Top Heating & Cooling Experts
paulcarew
Dan Webster
Dan Webster
Donni Steen