On a call for heat, a heating element in the sequencer starts warming a small heating element which causes a small piece of bi-metal to warp. As it warps it pushes on relays which first light the burner and a short time later, start the fan.
Posted on Nov 23, 2013
We have royal red furnace to heat our home.The fan dose not stop.
Details.......does the furnace function normally otherwise? Might just be a stuck fan switch. Make sure the thermostat hasn't been set on Fan ON setting or summer air circ. on older furnaces.
Find the fan switch and tap it and see if fan quits. If it does,fan switch is bad.probably. Always make sure your air circ. filter(return air to furnace) is replaced every 3 mo. or so,too. don-ohio (:^)
Jan 03, 2017 | Royal Heating & Cooling
What is the tonnage of a carrier furnace model number 58gp100-2
It can handle five tons, or a 60000 btu ac. Tonnage is a measurment for the ac, 1 ton-12000 btus. The ac dose the cooling. the furnace simply blows the air, so if its a good furnace, and sized right, no need to replace it. Simply add the split system to the existing furnace. If you want the tonnage of the ac size, let me know your homes squarefootage, age, condition. Do NOT include the basement in the sq. ft.
Apr 07, 2015 | Heating & Cooling
Blower fan continually runs
It may be but the fan control may be set to turn off at to high a temp, or theres a short between ;r; and g at the stat or furnace or sequencer, IF it runs through it. A limit or rollout switch may have failed but this will keep the unit from firering. Check for a manual blower switch that may be on. At stat it should be at auto and alsso at the fan control. A stuck relay is always possible,
Mar 08, 2015 | Coleman Home Electric Furnace Eb15b/Eb15d
Heating elements keep coming on and off after blower turns off
Yes your sequencer is the switch to energize the elements & sometime the low speed on the blower motor. It completes the 240 volts going to the elements. The sequencer turns the elements on in stages as well as the blower, & most sequencers have numbers on the side to tell what thermal disk turns on first. The blower, & one element should be wired on the 1 & 2 terminals (this turns on first when the sequencer coil is energized & shuts off last when the coil is de-energized). If any of the thermal discs are stuck closed, this will constantly energize the element on that switch.
Dec 04, 2013 | Coleman Home Electric Furnace Eb15b/Eb15d
Electric Furnace heating coil stays on constantly
There are devices called heat sequencers that activate the heat strips and when get old they pop apart inside and don't keep the contacts open. You need a new triple heat sequencer, might get one from a mobile home supply house or call an HVAC co.
Sep 25, 2013 | Coleman Mobile Modular Home Electric...
Intertherm feh 015ha
either the heat strips, fusible links on elements or sequencers.
Sep 21, 2013 | Intertherm E3EB010H Electric Furnac
My furnace wont lite
Problem: Your furnace will not ignite the gas to produce heat for your home.The following is the sequence of operation and probable cause:
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch (or circuit breaker ) back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution:You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands (use gloves). If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Nov 29, 2010 | Heating & Cooling
Have a ruud achiever 90 plus furnace. the flame goes out after the igniter quits. any ideas
Problem: Your furnace will not ignite the gas to produce heat for your home. When a furnace has a bad ignitor what I see most of the time is the following sequence of operation:
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution: You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Nov 26, 2010 | Ruud UBHC Air Conditioner
Air pressure switch is closed before the ignition sequence causing the boiler not to ignite can you advise solution
Nov 26, 2010 | Heating & Cooling
Sometimes the furnace doesn't come on when it should
OK so its an all electric furnace no gas? I cant think of anything clicking on an electric furnace except the sequencers or the safety switches.
If this is whats your hearing then the fan should definitely be running.
Feel carefully around the fan motor (I assume this is in a mobile home). See if you detect any heat coming around the blower area close to the fan motor. If so the fan motor may be at fault or one sequencer may be out (the main one of course...) the thing is can you get the fan to come on by turning the auto switch on the thermostat (or if older model the Auto On switch on the furnace) to ON? If so you can "limp by and have heat til someone either checks it or you can go on deeper into it. but to go deeper you'll have to let me know you know where the elements are and that you have a volt meter. and feel comfortable using it especially on HOT wires.
Mar 03, 2009 | Heating & Cooling