Question about Goodman GMS90703BXA Heater
Goodman furnace gmt090-4a ,blower to chimney goes on,igniter lights up,I hear gas valve pressure trying to send gas to burners for few seconds and flame will not light up and furnace shuts down with 1 blinking red light.can you please give solution to make it ignite,do i need a new gas valve.
  • 148 Answers
Clean your flame sensor first before you change that gas valve
Posted on Feb 06, 2014
5 Suggested Answers
WebTeligent
  • 42 Answers
SOURCE: No heat, trouble shooting light has continious flash.
There is a vacuum sensor on most units tied from the exhaust gas fan to the sensor. Does the unit try to start? If the unit's exhaust fails to pull the switch it will turn off after about 30-45 sec after starting. "IT" thinks it's not exhausting and stops to keep from overheating. Do you have this exhaust fan and rubber hose to sensor? Can you see if that fan is turning on start?
Posted on Nov 10, 2007
gear001
  • 59 Answers
SOURCE: Goodman GMNT 60 Furnace. Burners shut off after a
No, the board isnt out. The board has a code telling you that its out. Its your flame sensor. You wouldn't have gotten any heat if the gas valve was out. check if that flame sensor goes to another sensor on the same circuit , if it does check that. If it just a one wire sensor make sure its in the right position. If its a one rod flame senor with one wire I would sand it down with sandpaper. if its a two wire senor ohm it out to see if you ger current going through it.
www.fastacservice.com
Posted on Oct 16, 2009
  • 26 Answers
SOURCE: goodman furnace, inducer blower comes on, but
In the burner compartment opposite of the ignitor is the flame sensor. seems to be dirty. one screw holds it in. Remove and clean with a wire brush.
Posted on Nov 21, 2009
heatman101
  • 43501 Answers
SOURCE: Burner ignites and goes out (Goodman Gas-fired furnace)
The problem you have is water in the exhaust pipe.
Check to see if the pipe has sagged anywhere or if there is a trap in the line.
If you hear gurgling then it is definetly water....
Some times can be hard to find, even a pipe 1/4 full will cause problems. They are very sensitive to flue problems.
Make sure that the flue pipe either runs back to the furnace or out to the outside, a continuos slope either way witha high spot in the middle.
Also check the bottom drain of the blower if it has one, have had them plug and trap water also..
I hope that this will help you to solve your problem!
Thanks for using Fixya!!
Heatman101
Posted on Dec 24, 2009
Fan turns on, pilot on left side turns on red light at bottom stays solid during entire time then pilot goes out and blower stops no heat please help
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remaing solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Oct 05, 2010 | Goodman GMS90703BXA Heater
Furnace tries to light but misfires
Check the air filter.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
Feb 26, 2010 | Goodman Heating & Cooling
Goodman unit. when i turn it on the blower fan and the exhaust fan comes on butit does not lite no flames at all. i don't even hear the gas click in.
Feb 15, 2010 | Intertherm P3RA-048K Air Conditioner
Thermostat calls and from time to time won't ignite
I would first look at any wire connections both at the furnace and the thermostat. Then I would replace the thermostat. Check the units control board when it does not start for an error code. There should be a small viewing port to look into the furnace cabinet to see the control board.
Feb 12, 2010 | Goodman Heating & Cooling
Fan comes one, should hear whooshing of ignition,
Jan 27, 2010 | Goodman Heating & Cooling
Goodman model gms8 will not light fan comes on then turns off
Jan 26, 2010 | Goodman GMS80453ANA Open Flame Mid-Size...
I have a goodman furnace model#GMT045-3A. when I turn it on the electronic pilot works fine and the furnace will start and run about 30-45seconds then shut off. I followed the insructions for restart but...
Jan 26, 2010 | Goodman Heating & Cooling
New furnace, installed last October - has run approximately 3 months at the most. Have had to replace pressure switches, and again it is not working....will not ignite, but blower fan runs a pushes cold...
It's possible that the pressure switch is doing what it was designed to do, shut the burner off if there is a restriction in the vent system. Your problem may be intermittent, and is caused by wind blowing across your roof in a specific direction. Rarely, but on occasion I have seen this happen, the wind creates pressure on your vent pipe and prevents the pressure switch from closing. A directional cap (similar to  a wind rotating chimney cap) may be required. Good luck and let me know if this helps.
Jan 02, 2010 | Goodman GMS90703BXA Heater
When I turn my furnace on, the purge blower starts as normal, then after 15 seconds the ignitor starts to glow but when the gas valve should turn on it only turns on for a split second and then you can...
Nov 19, 2009 | Goodman GMS90703BXA Heater
Goodman GMP 125-4 one blinking light code. Gas valve has been replaced (at cost of $443). Didn't fix problem. Same co wanted $415 to replace circuit board. I did it myself for $99 part. Still same problem!...
One blink means it didn't light after a number of attempts. You replaced the circuit board and gas valve. Read on for some suggestions. On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
Nov 18, 2009 | Goodman GDS80904BNA Open Flame Heater
Goodman GMS90703BXA Heater Logo
183 people viewed this question
Top Goodman Heating & Cooling Experts
Dan Webster
Dan Webster
paulcarew
Brandon Berry
Brandon Berry
Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others