Question about Generac Guardian RTSE200A3 200 Amp 120/240-Volt Service Disconnect Transfer
My 200 amp transfer switch is not transfering into generator power when power goes out, i have to do it manually, but id does transfer back when power is restored
CarlGehrke
  • 169 Answers
SOURCE: Generac Guardian 15kW Generator
That sounds just about right, if the relay contacts get welded together it sometimes takes out the driver on the printed circuit board. As you found out, 12vdc from 23 to 194 makes the transfer switch move to the Generator position, relay not energized makes the ATS move to the Normal position.
You can make a nice test function by installing a 10 amp contact switch in series with either the N1 or N2 terminals. When the switch is open the generator thinks the Normal power has failed.
Regards,
Carl
Posted on Jan 26, 2009
  • 26 Answers
SOURCE: Generac 4456 does not start on power loss
I install and work on these everyday. If you hooked up the transfer switch you probable have a control wire wrong. check the utility power sense wire. That lets it no when to start in auto. it could be a relay or fuses. or a control board.
Posted on Jul 09, 2009
SOURCE: When utility power goes out, the transfer switch doesn't transfer
Call an electrician.
Posted on Jan 23, 2010
  • 760 Answers
SOURCE: I bought a Generac 17kw with automatic transfer
If you are using a Manual transfer switch, then you should manually operate the system. Why don't you use the switch it came with? Why would you use a 200a manual transfer switch on a 17kw generator? The idea is to move your critical circuits into the transfer switch panel. Then it would operate in auto.
Posted on Jul 03, 2010
  • 85 Answers
SOURCE: I Am installing a Generac 20Kw air cooled unit
It is always good to install a large enough wire where the maximum load can be drawn plus a little extra for safety. 7 gauge wire will do, if it was mine I would use 6 gauge wire. If the length is over 20 feet but not longer than 80 feet go to the next larger size wire.
Posted on Dec 18, 2010
Why wont my transfer switch change back to utilities position when the power is restored?
It depends on the brand of switch and generator. A Generac has its brains in the generator control board, others in the switch, what brand of switch please?
Aug 20, 2014 | Electrical Supplies
Automatic transfer switch not transfering power to home
YOU MAY WANT TO CHECK THE RELAYS THAT ARE IN THE TRANSFER BOX
Dec 15, 2013 | Generac Guardian 200-Amp Automatic...
Coils on transfer switch got fried when utility came back what could have caused this
possible failure of a relay. contact generac,sometimes they will accomodate you with new parts
Oct 08, 2012 | Generac Guardian 200 Amp Transfer Switch...
Just finished installing a 20 KW Generac generator (fueled with natural gas). The included transfer switch will not automatically transfer to the generator, but transfers back to the utility without...
Check the connections on the tranfer relay and two coils. The two coils have blue wires. I have seen them come off from assembly or shipping its common. Each coil has two blue wires #8 and E1 with crimp steak ons and limit switches make sure there all pushed on all the way. Hope this helps
Mar 09, 2011 | Generac Guardian RTSE200A3 200 Amp...
I have a Briggs & Stratton Automatic Home Generator 7 kW, Model# 40301. I had it installed by an electrician. Who also installed Briggs & Stratton Transfer Switch 50 Amp. The problem is the...
It sounds like the mains sense wire is disconected from the control panel or the run wire is not being cut by the aux contact on the transfer switch.
Is the transfer switch manual or motorised?
Feb 15, 2011 | Briggs Stratton 7,000 Watt Automatic Home...
I bought a Generac 17kw with automatic transfer switch. I would like to use a 200 Amp manual throw transfer switch. The generator came with a pre wired sealtite pig tale and junction box. Inside the...
Jul 02, 2010 | Generac Guardian 200 Amp Transfer Switch...
I have a new Generac 20KW Propane generator with a rtse 200A3 automatic switch. I had an electrician install the switch and make the connections from to the generator. The generator is blowing the 7.5 amp...
Sounds like the electritian wired something wrong. Control wiring for that generator should be:
N1 and N2 = 240 vac utility input
Wire 0 = ground
Wire 194 (15B) = + battery
wire 23 = transfer signal
Sep 02, 2009 | Generac Guardian 200 Amp Transfer Switch...
Jul 01, 2009 | Generac Guardian 200 Amp Transfer Switch...
Generac Guardian RTSE200A3  200 Amp 120/240-Volt Service Disconnect Transfer Logo
Top Generac Electrical Supplies Experts
Craig Butler
Craig Butler
dennys23601
Don  Farrell
Don Farrell
Are you a Generac Electrical Supply Expert? Answer questions, earn points and help others