Question about Mr Steam MS225EB1X eTempo MS225E 7.5 KW 208V 1 Phase Steambath Generat
7.5KW 1963 JB GEN 200 VOLTS ON ONE PHASE 40 VOLTS ON THE OTHER UNDER LOAD
    Prodigy:
    An expert who has answered 500 questions.
  • Mr Steam Expert
  • 573 Answers
Check the reaactor, and also diodes
Posted on Nov 21, 2013
I have a Kohler 7.3 ECD generator with error code UVunder frequency. Restarted gen and it ran for one hour so I shut it off. What's the problem?
check the operating rpms
the rpms determine the voltage and frequency and can be adjusted at the governor spring setting
adjust it until the voltmeter reads the required voltage
set slightly above to allow for rpms drop under load
for example if 240 volts set around 250 volts and that will drop back to 240 volts under load
if 110 set around 115 and that will drop back under full load
both frequency and volts are dependant on rpms
Sep 20, 2016 | Kohler Electrical Supplies
The wire in my house for an elec. garage heater is 14 gauge wire with a 15 amp breaker. I assume i need at least 10 gauge wire with 20 amp .The heater is 20.9 amps and 3000-5000 watts, with 17500 BTUs
Curt, a 20 amp breaker will blow if you pull 10.9 amps from it. I suggest having a licensed electrician do your wiring. Likely, you need a permit anyway.
Oct 22, 2015 | Water Heaters
What size generator do I need to run a 10 hp motor
on the plate attached to the motor you will find several important items
one is the wattage of the motor
this is the maximum wattage that the motor uses when under load
the gen set will need to be at least 30% bigger than that figure
next there will the number of phases that the motor is
it will read as 1 ph or 3ph
If it is 1ph that is a single phase motor and will ru from a single phase gen set
however if it is 3ph you will need a 3ph gen set to run the motor
As most single phase motors are limited to around 5hp I would be very sure that the motor is not 3ph
specialist advice from an accredited electrician or electrical motor shop is recommended before buying a gen set. as if you need 3ph the gen sets become expensive.
Aug 07, 2015 | Electrical Supplies
The generator puts out too many volts. The control knob doesn't help it. Any info appreciated. Thanks, RP
volts on a gen set are controlled by the engine prms
adjust the screw on the governor arm to set at the correct out put volts
remember that unloaded set volts ( rpms ) will drop under load so set about 10 volts over out put voltage so that under load the correct volts will be supplied.
May 05, 2015 | Electrical Supplies
1963 ONAN SPEC#705JB 3R/1G GEN DATA #705 JB3N1B HAVING PROBLEM WITH VOLTAGE OUTPUT UNDER LOAD ONLY.200 VOLTS ONE PHASE 40 VOLTS ON THE OTHER.FOUR LEAD GEN 120/240 VOLTS.ANY THOUTS,BRUSHES LOOK FINE.
First remove any loads, is the voltage still unbalanced? If not check the grounding of the load, if yes check generator N/G leads are tight. Check the stator windings to make sure they are in tolerance for L1 L2. If you need help let me know. This unit probably has a reactor, so check for any loose connections. Also check the diodes, you may have to lift one end out of circuit to test properly, or else your meter will not read correctly
Oct 19, 2013 | Electrical Supplies
I have a 12RES showing 114 volts on phase and 124 volts on phase 2. 240 v between phases. Is this typical?
No it is not typical, you never indicated if you are measuring it under load or not. Repeat that test under 1/4 load and see if they even out.
Feb 03, 2013 | Kohler 12 kW Emergency Power System -...
Honda EU3000is. 2 year old unit used by electric start at least 5 days a week. My gen has recently stopped staring by the electric start, it turns over but just not as strong as when new, what i mean by...
I have a 5 year old EU300is that would not start with or without the battery. I went through all the usual such as gas, plug, oil, etc. The battery showed 12 volts, however, when tested further it would not hold a load. I bought a new American made battery and now the unit runs fine.
Jan 29, 2011 | Honda 6370C - Parallel Power Kit For ...
The coleman voltage generator for 250 kva gen set
Well I assume that this generator is NOT three Phase, and delivering 440 Volts? in that case, that reading is what is called and "Open Circuit" reading, with a full load, that reading will/should come down to the nominal voltage of 250 V (+/- 10%) This generator is a 250 V AC unit? If this is so then it is operating correctly? It is 5kw UNIT. using a digital multimeter due to it's large input impedance it will often give erroneous readings if NOT loaded down with the correct.any. load.?
Mar 02, 2010 | Coleman Powermate Powermate 5000W...
How to install a 208v outlet for a stove
if its a single phase panel you will only have 120/240 v.a.c. you can wire it for 240 volts and it will heat faster anyway the only way you could have 208 volts would be if you had 3 phase delta or open delta 3 phase or buy a special "dry-type" transformer for 240 volt to 208 volt step-down,otherwise it will be red-& black will be your 2 hot phases of 120 volts each/white-neutral/and green or green-yellow will be the case safety ground
Nov 14, 2009 | General Electric Profile PP945 30 in....
Mr Steam MS225EB1X eTempo MS225E 7.5 KW 208V 1 Phase Steambath Generat Logo
41 people viewed this question
Top Mr Steam Electrical Supplies Experts
BJ Russell
Hippy_dd
Are you a Mr Steam Electrical Supply Expert? Answer questions, earn points and help others