I have a Carrier 38APD030 unit with Comfort Link, I keep getting an A120 code for low SST, the air handler is running at 35 hertz and is rated for 8200 CFM at 60hertz. I have return air reset in program to try to keep second stage compressor from coming on. Unit is lightly loaded at this time of year so we have BAS shut OA dampers to minimum whenever unit called for DX cooling. Unit was charged by the book during startup and no loss of charge has accured. 1st stage compressor is a compland with the disc unloading. Thanks
4 Suggested Answers
ACTECH
  • 80 Answers
SOURCE: is ruud heat pump model upka-042jaz a single or multiple stage pump?
I NEED THE MAKE AND MODEL OF THE T-STAT TO HELP YOU
DID HE CHANGE ANY WIRING?
Posted on Jan 17, 2008
  • 588 Answers
SOURCE: when charging central air unit r-22......
It sounds like you have your gages hooked up wrong. Blue goes to the Suction line (the big line) it should be cold when the units running.
Red goes to the liquid line (the little line).
Posted on Apr 27, 2009
SOURCE: Copleland scroll compressor failure
I have scroll chiller contains scroll compressor tandom circuit. One of the compressor failure from it due to unbalance of the winding. Previously compressor thermistor opens two to three times. Also one phase open in contactor of the compressor. Can you guide me regarding the reason of compressor failure and what is the next step for the replacement of compressor. Also give guide line for the points take care.
Posted on Mar 27, 2010
My(38ycc030340)carrier heat Pump ac unit blows 5 amp fuse on board in handler in attic when switch stat to heat.
Miss wired or shorted low voltage wiring. Have you changed stat? Animal chewed wires at foundation wall or in attic?
Oct 10, 2016 | Carrier Heating & Cooling
Is there a reset switch on Carrier airconditioner
No turn you termalsate to the off pos. Then to fan on. Them see if it goes off and then switch to cooling on the coldest sting if the fan in air handler shuts off before. The stat tells it to it might be kicking out on thermal overload bad motor. Check the condnsor fan for this to fans don't turn on unless they are told to by power going to a board or a relay low voltage control wires may be damaged clean the units pay a tension
Jul 31, 2016 | Carrier Heating & Cooling
Heat pump problems
Some heat pumps have high and low pressure swiches installed to keep compressor from running when unsafe conditions occur that can damage the compressor. If the outside fan is not turing on, the unit is cycling on high pressure, if you see ice forming on the big refrigerant line coming from the air handler, then the compressor is shutting down on low pressure. Low pressure can be cause by lack of air flow through air handler or from a low refrigerant charge.
Feb 13, 2014 | Intertherm Heating & Cooling
My airhandler keeps burning out the transformer and i cant get it to come on
You need to check the low voltage wires to the out door unit, disconnect the two wires labeled Y and C from the air handler. Most of the time the low voltage wire are the problem or the circuit board is bad.
Jun 07, 2011 | Carrier Heating & Cooling
I want to find the transformer for the 36 volt inside unit. Is it in the inside unit or outside unit .I have no power to the inside unit however the outside unit has power,and the inside unit appears to be...
It's a 24v transformer. Your indoor unit houses the transformer for the outdoor unit. The outdoor has a low voltage (24v) supply running to it to push in the contactor for the outdoor unit to run. If your air handler inside has no power then it will kill your LOW VOLTAGE power to the outdoor unit. You will still have the high voltage power to the outdoor unit. You may have a fuse on the switch for your air handler blown if there is one. On the disconnect switch mounted to your air handler, you will have a door to open and a fuse in there. If not, check your main breaker at the panel. If you don't know what a transformer looks like, you may want to have someone familiar with electrical of HVAC help you. To check the transformer for power, you first need power to your air handler, which you don't have. I would say that is not your problem. I would assume your air conditioner is not running outside, correct? Your problem is the power (HIGH VOLTAGE) to your air handler. Loose wires, blown fuse, tripped breaker etc...
Aug 06, 2009 | Comfort-Aire HMC36AT-1 Air Conditioner
Carrier Comfort 13 Puron model 24ACA3 / FV4NB006 installed 3/18/08 no longer cooling. Carrier AC1-100 Thermostat checked per manual - all default settings intact. Test override did not turn unit on though....
Verify 24 volts at the low voltage transformer inside the air handler. If it is OK, jump out the red/green and yellow thermostat wires. If everything comes on, replace the thermostat.
Jun 07, 2009 | Carrier 38CKC036 Air Conditioner
The Infinity Comfort Control code
Call your local Carrier dealer. They have code to get into system. Rusty Good system
May 21, 2009 | Heating & Cooling
3 amp fuse blows on a carrier 58mcb furnace board
Hi!!! Does your ac unit work fine?If not check your low voltage problem..You have a low voltage problem check the wire going out to your condensor make sure that they are not touching..Good luck..Check low voltage wires..short in progress..
Jan 04, 2009 | Carrier 52CQ-312-4 Comfort Series Heat...
My Heat will not work on my upstairs unit. I am getting an E2 error code on my carrier thermostat. what does that mean?
the e2 code on a carrier comfort zone thermostat is indicitive of the external safety sensors which are located on your units ductwork in the attic. the e2 code are the hpt/ and lat sensor codes. the hpt is the heat pump temperature sensor and the lat is the leaving air temperature sensor. you can pull off the cover of the panel and behind it will actually give you all the fault codes associated with you carrier tsat.each sensor has a certain ohm rating and if its out of the range it will fail. now as to the reasons for failure, the indoor coil could be dirty, filters dirty, refrigerant charge incorrect.
Dec 03, 2008 | Carrier Heating & Cooling
Heating & Cooling Logo
32 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Donni Steen