Goodman Model GMP050-3 Rev B Solid flashing light. Draft motor turns freely by hand, but did have one wire unhooked. Reattached wire, checked all connections. Set thermostat at highest setting. Powered unit and Draft motor started, ran for very few seconds, then constant flash. Furnace worked fine this past season. Board or motor? Thanks, Nick
  • 5 more comments
  • carl garno Oct 17, 2013
    how long does it take to get a response? I posted this 2 days ago, anybody looking at this?
  • Charles Chapman
    Charles Chapman Oct 20, 2013
    carl, first there were 5872 request that I got alone .
  • Charles Chapman
    How many time shave you put this post up. I know I gave you a suggestion
  • carl garno Oct 22, 2013
    This was my first & last post. The ONLY suggestion I received was "I would contact Goodman that would be the best place for info" Well, DUH, I sure didn't need a Fixya "PRO" to tell me this! I thought this would be faster, but was wrong. I used my common sense & done my own trouble shooting. Thanks for all your help! LOL
  • Charles Chapman
    Charles Chapman Oct 22, 2013
    Carl, someone else did respond and wrote out what looked like a four page letter from Goodman to you
  • Charles Chapman
    Add a Comment I said go to goodman because most mfg have a troubleshooting page and teck support
  • Charles Chapman
    THta would have been a lot faster than me going there or trying to write it all out to you
    Cheetah:
    An expert who has answered 20 or more questions within one hour.
  • 83 Answers
I would contact goodman that would probably be the best place for info
Posted on Oct 20, 2013
Therinnaiguy
  • 1420 Answers
SOURCE: Goodman furnace I think
Ok, a flashing 3 on a Goodman control board usually means that the pressure switch is tripping. A few things will cause this. One being a restriction in the exhaust or combustion air inlet. The second could indicate a faulty inducer blower motor and the third would be a blocked or bad pressure switch.
With the front cover off and door switch taped down, Have a helper turn the thermostat up to 75. You will be watching the circuit board for flashing lights and in a few seconds the inducer motor (the small fan hooked to the exhaust) will start. If this does not happen, we either have a bad circuit board or blower motor. If the fan starts rotating, inspect the hoses going to the small circular pressure switch. Sometimes they may get either water or debris in the hose and not allow the switch to sense pressure. If the hoses look OK, the igniter will glow an orange color and you will see this if you look thru the small viewing port. IF no glow, you could have a bad pressure switch, a bad ignition relay (found on the circuit board) or a bad igniter. OK so if the igniter glows, a few seconds later the gas valve should click open and send gas to the burners. The orange will turn to blue. If this does not happen, you have either a bad gas valve or bad circuit board. Finally if you get flame but it will not stay lit more than a few seconds, you may have a restriction in the burner gas train, a bad gas valve, a dirty or bad flame sensor or not enough gas pressure.
Knowing the sequence of operation will give you the needed information to talk with a service technician and cut down on diagnostic costs.
Try looking on the back of the furnace access panel for both model number and a diagnostic schematic. This will confirm what the flashing 3 code means for your unit.
Sorry, without knowing the model number, this is the best I can do for you. Good Luck!
Posted on Oct 29, 2007
Therinnaiguy
  • 1420 Answers
SOURCE: furnace won't stay running
1 FLASH
Furnace fails to operate.
• Integrated control module
diagnostic LED is
flashing ONE (1) flash.
• Furnace lockout due
to an excessive
number of ignition
“retries” (3 total)1.
• Failure to establish flame.
Cause may be no gas to
burners, front cover
pressure switch stuck open,
bad igniter or igniter
alignment, improper orifices,
or coated/oxidized or
improperly connected flame
sensor.
• Loss of flame after establishment.
Cause may be
interrupted gas supply, lazy
burner flames (improper gas
pressure or restriction in flue
and/or combustion air
piping), front cover pressure
switch opening, or improper
induced draft blower
performance.
• Locate and correct gas
interruption.
• Check front cover
pressure switch
operation (hose, wiring,
contact operation).
Correct if necessary.
• Replace or realign
igniter.
• Check flame sense
signal. Sand sensor if
coated and/or oxidized.
• Check flue piping for
blockage, proper
length, elbows, and
termination.
• Verify proper induced
draft blower performance.
Posted on Nov 25, 2008
  • 6 Answers
SOURCE: Goodman GMP075-3 ignition problem
bad board,i have had several board failures on goodman
Posted on Dec 31, 2008
machtcl1
  • 61 Answers
SOURCE: furnace starts properly, then shuts down, led flashes 8 times
The first thing to look at is the flame sense rod.
Shut off power to the furnace, remove, clean sensor with steel wool or sandpaper then reinstall the sensor. Reapply power and it should run properly.
Posted on Jan 10, 2009
SOURCE: Goodman GDS8 Furnace Won't Cycle
I had the same issue as zippygaloo with the harness plug. By lifting up the connector, the furnace would go out of it's current fail mode and start operating normal again. I have temporarily resolved my issue, by tying up the wires (looped under them with tie raps) and secured them to the vented furnace housing directly above, thus alleviating any stress pulling down on the connector plug by the weight of the wires. Since doing this my furnace has been running flawlessly and stays right at the temp on the Tstat. No more fault modes with blinking lights! Hope this helps you guys. I don't know if it's related to bad design flaw, or there is a weak connection on the board, but it worked for me.
Posted on Mar 01, 2009
I have a goodman furnace GMP100-4 REV B..about a year ago it was not working. The fan would start but it would not ignite. We found out we need a new ignitor and it was a good quick easy fix. Now a ye
Any light flashin on the control board? If not then look for a small fuse blown on the board. See lights a flashing count them flashes
A sampling of various failure codes on a furnace:
Read one LED flash that stays on continuously to mean your furnace has no signal coming from the thermostat and will not operate. Turn the power off and check the thermostat for improper settings or connections.
Interpret one LED flash that blinks on and off to mean your furnace has locked out because it could not ignite after three tries, and must be reset. Interrupt power to your furnace for 20 seconds or lower the thermostat so your furnace does not try to heat, then reset the thermostat to the previous setting. After one hour of lockout, your furnace will automatically reset itself and try to operate as usual.
Decipher two LED flashes to mean the draft blower is not working, or your furnace has a short in the pressure switch circuit. Turn off the furnace power and repair a short or replace the pressure switch.
Read three LED flashes to mean your furnace has an open pressure switch circuit or it has an induced draft blower operating. Check the pressure switch hose of your furnace for blocks or an improper connection. Also, look for blockages in the flue, and tighten any loose wiring.
Translate four LED flashes to mean your furnace has a primary limit circuit open, possibly from loose wiring or blocked filters. Check and clean filters, tighten wiring and check the flue for blockages.
Interpret five LED flashes to mean your furnace senses a flame without a call for heat. This could be from a gas valve closing slowly or a burner flame lingering.
Read seven LED flashes as a warning of a low flame sense microamp signal. This could happen with a coated flame sensor or a lazy flame from poor gas pressure. Turn off the power and adjust the gas pressure according to the information on the rating plate.
See eight LED flashes as meaning an igniter circuit problem due to a bad igniter or an igniter connected improperly. Replace the bad igniter or check the ground wiring, making necessary corrections.
Decipher nine LED flashes to mean the high-stage pressure switch circuit will not close during a high-stage-induced draft blower operation. Your furnace may have a pinched or blocked pressure switch hose, a blocked flue or loose wiring.
Read continuous flashing on the LED to mean your furnace has a reversed polarity of 115 volts. Turn off the power and correct the wiring polarity after reviewing the wiring diagram.
Nov 29, 2011 | Goodman Heating & Cooling
I turn my thermostat to the HEAT position, I hear the Thermostat click and the Furnace begins to hum but no air comes out of the vents. Also if i turn the fan to the ON position air will come out of the...
need to go to furnace and watch it...if your hearing a hum the enducer draft motor may have failed...it should start first if there is no fault codes...reset unit by unplugging furnace or in some cases turning power switch off...turn thermostat on heat and watch unit ..the small enducer draft motor should start first the a ignitor glows and the should light...goodman units have a control board with a light on control board when it fails should flash a code and on the door or inside on lable should give you what that code is...hope this helps good luck
Jan 07, 2011 | Goodman GMS90703BXA Heater
Goodman 95 %furnace keeps saying low pressure is stuck. changed out low pressure switch and high pressure switch and still have same problem.
That thang might be sensing a lazy flame. In other words the flames took too long in the board's opinion to quit sensing the flame. Yall probably need to do pressure tap on the gas valve.
Here is a realistic look at goodman fault codes and what to check fer and I am assuming you are not a tech and don't know this already and am hoping it helps:
Now here is how it should all go down:
Bottom dollar: it all goes back to type of gas, the initial setup, the pressure tap. and how it is wired up to begin with.
This will give you an idea where to start I hope.
Dec 10, 2010 | Goodman GMS80903BNA Heater
Air not coming out full force
Check the circuit breaker for the indoor unit. Also make sure the fan rotates freely by hand, then check the capacitor for the fan motor and replace it if bad. If the capacitor is good then check the fan motor windings to see if the fan is bad.
Jul 20, 2010 | Goodman Heating & Cooling
What is the model number for the Draft Inducer Motor Goodman GNP075-2REVB Furnace
I think you must mean GMP075-2rev8 check this link for parts listing:
http://site.famousparts.com/goodman/PDF/RP-169C.pdf
Johnstone supply which has many locations in many cities sells Goodman and stocks parts, and available mailorder http://www.johnstonesupply.com/corp/Default.aspx
Feb 18, 2010 | Goodman Furnace Draft Inducer Blower ...
Furnace lights fan comes on then fan goes off furnace stays light until overtemp takes it out code flashes 4
Have some one hold the bottom door safety switch, turn furnace on wait until heating fan relay clicks, and check at terminal (Heat) & terminal (neutral or where all the white wires are located on the control board) for 115 volts to 120 volts. If voltage is present replace blower motor, if voltage drops out while running then replace control board.Turn power off to furnace, open bottom door and feel blower motor with hand, if motor is real hot replace motor. you can not oil this type of motor, it has to be replaced along with the compacitor. Good luck.
Jan 22, 2010 | Goodman Furnace Draft Inducer Blower ...
Need help with a goodman gmt070 furnace...error code flashes three times, i have replaced pressure switch, still flashed, replaced board, still flashes three times...flue is clear, draft inducer motor is...
it may be clogged at the barbed fitting on the induced draft motor where the pressuer switch tubing connects. take a paper clip and **** it out make sure you can stick it thru freely till you can feel the Inducer wheel then reconnect and try again.
Nov 04, 2009 | Heating & Cooling
Goodman GMP075-3 Random Incomplete startup
If the draft motor starts then shuts right off and then a red light comes on usually means that there is a blockage somewhere. Check the pressure switch line, make sure that it is clear and the hole in the heater that the pressure switch vaccum line runs to is open. If that checks out then make sure that your flue vent cap is on and that it is not pressed down on the flue vent and that the gases can vent properly
Feb 13, 2009 | Goodman GMS90703BXA Heater
My heater is not running no ignition
your polarity wires need to be reversed the main wires coming into the unit are either black going to black white going to white changed the wires around to black going to white and white going to black that should solve your problem
Nov 04, 2008 | Goodman GMS90703BXA Heater