Smart UPS VT 10KVA fault "Mains Not Available. Input Freq/Volt Out of Range". All phases input and output giving the expected voltages 240V and frequency OK at 50Hz.

1 Answer

Gruber Power Services

Level 2:

An expert who has achieved level 2 by getting 100 points

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

Mentor:

An expert who has written 3 tips or uploaded 2 video tips.

  • Expert 176 Answers
  • Posted on Oct 09, 2013
Gruber Power Services
Expert
Level 2:

An expert who has achieved level 2 by getting 100 points

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

Mentor:

An expert who has written 3 tips or uploaded 2 video tips.

Joined: Aug 24, 2011
Answers
176
Questions
3
Helped
95508
Points
221

Sounds like you hooked up the input to the UPS on the bypass. Either way either way your input is not there. Also make sure you configure the UPS prior to placing online.

3 Related Answers

Anonymous

  • 1 Answer
  • Posted on Aug 26, 2010

SOURCE: smart apc ups error with all indicator flashing .

APC Smart-UPS 1500VA has an error. All it's pannel lights blinking. what is the best possible solution to this?

Ad

Anonymous

  • 64 Answers
  • Posted on Jun 30, 2009

SOURCE: insufficient Runtime Available on Agent

If the UPS display is indicating runtime at 6 mins, and software is saying insufficient, seems like a communications issue. I'd try downloading the latest communication software for the UPS and reseating the communications cable at both ends, making sure no bent pins, etc. could be causing a comm glitch.

Anonymous

  • 1 Answer
  • Posted on Feb 08, 2011

SOURCE: Silcon DP360, 3-phase 60kva, 400v,

#1. You should call APC Technical Support. It's free, and they will help you. You should get voltage even without a load on the unit.

#2. There is a Tripple-Slot unit for this device. It's specific for the Silcon based units. Read the manual, and there is a PN that you need for it. If it doesn't say SILCON, then it won't work. (I tried).

Paul
Data Centers Canada
www.datacenterscanada.com

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

0helpful
1answer

I have a Smart-UPS VT 10kVA that when goes to Mains out of range pass to bypass instead of battery, there is a way to setting the UPS to pass immediately to battery instead of passing to bypass first

The behavior of the Smart-UPS VT 10kVA in response to mains out of range can be configured using the PowerView software provided by APC (the manufacturer of the UPS). Here are the general steps to change the settings:
  1. Download and install the APC PowerView software from the APC website.
  2. Connect your computer to the UPS using a USB cable or network connection, depending on the interface available on your UPS model.
  3. Launch the PowerView software and establish communication with the UPS.
  4. Once connected, navigate to the UPS settings or configuration section within the software.
  5. Look for options related to the response to mains out of range or bypass operation.
  6. Adjust the settings to instruct the UPS to immediately switch to battery power when the mains voltage is out of range, instead of passing through bypass mode.
  7. Save the changes and exit the configuration settings.
  8. Disconnect your computer from the UPS.
It's important to note that the specific steps and options may vary depending on the version of the PowerView software and the firmware version of your UPS. Refer to the user manual or documentation provided by APC for detailed instructions and guidance on configuring the UPS settings.
If you are uncertain about making these changes yourself or require further assistance, it is recommended to contact APC's technical support or consult with a qualified APC technician who can guide you through the process and ensure the proper configuration of your UPS.
0helpful
1answer

AC Volts on Input when loaded

If you're saying that there is voltage output on the input wire when unplugged from the wall you should contact the manufactureer as this is a defect.
1helpful
2answers

NO VOLTAGE ON YELLOW PHASE

what caused the UPS to transfer to Bypass? could be inverter fault, would you please check your battery set, maybe the input power is outside the tolerance and causing UPS to discharge the battery set , as well when battery set reaches the end of discharge it is causing the UPS to transfer to bypass and there is something missing on the input yellow Phase.
if the above is not true check the load type that is connected to the UPS output that is causing UPS to switch off in 10 minutes time.
0helpful
1answer

Site wiring fault

Hi Viqtah, (<------ Clever!!)

If you hit the ESC key and get to the main menu there is a Setup submenu. In there you can change the line voltage values coming into the UPS. Sometimes a previous owner will change those values and cause the UPS to fault when properly connected. NOTE: A CERTIFIED ELECTRICIAN SHOULD VERIFY ALL CONNECTIONS ENSURE PROPER PHASE ROTATION.

Reply or call if you have any more questions -- 800.260.2259
0helpful
1answer

Case 1: 220 V, 50Hz applied to s 3000 measuring the output as follows: 1- phase to ground 220 2- Phase to neutral 219 3- ground to neutral 1 volt Case 2 disconnct the input 220 V we have 1- phase...

Did you measure with a true RMS meter?
If yes,the results are normal,but your ground connection is not very good.
The case has 110v potential (exactly half of the input&output 220v) because of the input and output capacitor filters (a capacitor is conectet from phase to casis and an other from neutral to chasis,thus resulting a 1/2 voltage divider). Because of this,the earthing is necessary.
0helpful
1answer

I have a UPS 1000 VA with 12 V X 2 Battery, Problems: when we on ups input 200 V without load, it gives output 210 V. when load it gives 230 V on electricity. When Electricity cut off it gives 250 V. When...

arif qc, Are you using a DMM that is or will make "true RMS" measurements or is it an "average responding" type of voltmeter? Is this APC ups designed for 120 vac input/output or is this unit a 220 vac input/output type? Use only a "TRUE RMS" type DMM to make your measurements!!! I believe if you visit Tripp-Lite site, you will find a tutorial video clip of why you should use a true-rms meter to make measurements of output voltages. 12fixlouie
0helpful
2answers

"On Battery" Alarm Sounds when Power Available.

if this comes sometimes and goes, this means that the power to ups is sometimes deviating from the specific ups input range, hence the ups is rejecting it. mesure the input voltagesand frequency with a multimeter and check whether they match the specified ones in the ups manual. aslo with some ups there are switches that you use to set the input voltages or number of phases in the ups input. check the manual to see whetther your ups has such.
0helpful
1answer

FAULTY MGE UPS

a 3 ph ups normally can work upto 450 volts because the normally its the transmisson range of voltage
220 to 250 is the voltage range of normal 1 ph line so check for proper line voltage or load voltage
Not finding what you are looking for?

1,648 views

Ask a Question

Usually answered in minutes!

Top APC Computers & Internet Experts

Cindy Wells

Level 3 Expert

6688 Answers

Grand Canyon Tech
Grand Canyon Tech

Level 3 Expert

3867 Answers

Rob Hill
Rob Hill

Level 3 Expert

1480 Answers

Are you an APC Computer and Internet Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...