Question about Honeywell Heating & Cooling
I have a Honeywell Ducted Heating at my home, the pilot seems on, gas seems to be flowing to the unit but when I switch it on nothing happens
    Top Expert:
  • Honeywell Master
  • 76,649 Answers
Do u hear the heaters gas valve turn on? if not replace it, they stick and cause this problem, also make sure control voltage is avail to the thermostat, this should be 24 volts, this also supplies power to the gas valve in the heater.
Posted on Apr 20, 2009
My Honeywell smartvalve stop opening the gas valve, inducer motor started, glow and pilot happen, just no fire...I replaced said smartvalve and upon installation, the inducer motor wouldnt run, no glo
Double check the wiring connections, maybe you have the pilot valve and the main valve wiring reversed. I had a call one time where the homeowner installed the gas valve backwards, so no flow and of course and the wiring on the three terminals was reversed.
The inducer should start whether or not the gas valve is wired wrong, unless it is wired in parallel with the pilot valve.
Jan 21, 2015 | Honeywell Heating & Cooling
My Honeywell smartvalve stop opening the gas valve, inducer motor started, glow and pilot happen, just no fire...I replaced said smartvalve and upon installation, the inducer motor wouldnt run, no glow or...
Smartvalves are tricky and a certain sequence must happen. Without going into this in depth, try this:
Install new smartvalve
Set thermostat to the off position
Kill the power to the unit
Restore power to the unit
Turn the heat on with the thermostat
In this order!
Aug 29, 2017 | Honeywell Heating & Cooling
I have a Brivis Buffalo 85, pilot light is on main burners will not ignite when turned on? It seems like gas isnt allowed to bar which turns on main burners
Usually a thermocouple or similar device is employed to allow fuel to flow once the unit sees that there is sufficient heat to ignite the fuel. Otherwise it can be a fuel valve that "sees" an unusual flow of gas which sets off the safety.
May 07, 2014 | Honeywell Programmable Thermostat Heater
Switch on wall fireplace with Honeywell control SV9403, pilot does not turn on even there is current flowing into the controller device.
Good Evening. Your fireplace is equipped with a smart valve (SV) to which the valve itself acts as the control. This unit has intermittent pilot or hot surface ignition. Can you clarify to me which ignition this unit has?
Dec 30, 2013 | Honeywell Programmable Thermostat Heater
Pilot lights up but would not fire up into heating, I have brivis buffalo 85
This is the proper cycle of a furnace and what should happen.
Inducer motor kicks on, it runs for a little bit, about 3-5 seconds, then you should see a bright yellow glow, this is the igniter, shortly after, you should hear a click and the gas should start to flow, almost immediately it turns to a blue flame. Then your igniter should turn off and the blower motor start up.
If the pilot turns on and the gas ignites, then shortly after the unit shuts off, chances are this is your blower motor. It is not starting up, then the heat limit is reached in your unit and the safety shuts it off.
Mar 02, 2011 | Honeywell Programmable Thermostat Heater
Burners on our Brivis Buffalo 52 Ducted heater aren't getting gas
test thermosat for proper operation ie-broken wire-power if good jump stat and check if unit goes on if it does than stat internal problem or wiring problem and needs replacement or repair --if stat good check fan safety/high limit sensor if good would need to check and test thermocouple thats the tube that the pilot flame burns on may be enough to keep pilot burning but not enough to open valve for heat demand
May 31, 2010 | Heating & Cooling
We have a Vulcan Ultra high efficiency gas ducted heating
Gas ducted central heater won't switch on all of a sudden
Nov 04, 2009 | Vulcan AUW230A Heater
Unable to get Braemar Spectrolink thermostate to switch to auto
I have exactly the same problem, did you ever get an answer to this issue?
Sep 08, 2009 | Honeywell Programmable Thermostat Heater
Ducted heating unit blows cold air and fan is always on..
that s correct the control is done by the thermostat stop the heating up to your set point and restart if the medium temp is under the set point
if this sequence fail means
- no power to the control element or is defective
thanks
Apr 27, 2009 | Heating & Cooling
Stadt Ducted Heater ignition problems
1 check power connection properly.
Mar 27, 2008 | Heating & Cooling
Heating & Cooling Logo
43 people viewed this question
Top Honeywell Heating & Cooling Experts
Bill Long
Paul Carew
Brandon Berry
Brandon Berry
Are you a Honeywell Heating and Cooling Expert? Answer questions, earn points and help others