Need wiring diagram for a ac060x1022b air conditioning unit. i installed a relay breaker on the unit outside and need to know that i wired it correctly. took a couple of weeks to get the right part and now i forgot how it was wired
  • 306 Answers
Should be three wires coming out of your box. Take the ground and connect it to the ground stud inside the unit. And then take the black and connect it to the contactor on the L1 side and then the white and connect it to the L2 side. Just match the black to black and white to white. Across the contactor.
So just to make sure I expained it good. Contactor sits just inside your case you have two small wires that are from the t-stat. Only 18 gauge. then the bottom of the contactor has two connections so power comes to the bottom side that is what you are hooking up. Now on the top you should have maybe 5 or 6 wires coming from that. But those are there already.
Posted on Apr 21, 2009
Carrier model 38tdb air conditioning unit kicks out the 40 amp breaker. Also moisture under compressor unit outside. What is problem?
What breaker? The breaker for the condenser? Likely have a compressor shorted to ground or drawing locked rotor amps. Easiest way to tell is make sure breaker off, unhook compressor wires from contactor. Turn on breaker and turn on machine. If the breaker does not trip, obviously problem with compressor
Jul 14, 2016 | Carrier Heating & Cooling
Why did the air handler on my 1999 Trane heat pump stop working? Could it be a fuse in outside unit
The fan is controlled by a relay that is operated by the thermostat. There is usually a wiring diagram inside the unit that will show the location of the relay.
Feb 08, 2015 | Heating & Cooling
Keeps blowing 3 amp fuses when i turn the air conditioning on.
Ok, If 3 amp fuse is blowing in the air handler unit when switch is turned to cool check to see if outside unit jump starts and stops when this happens. If this is the case wiring is fine check main relay in outdoor unit. There will be a spring contact on main relay (Black relay close to where wires come into unit), check for corrosion or carbon build-up on little round contacts. If you can clean contacts with a small piece of sand paper. Make sure all breakers are off before removing cover! You might have to remove relay in order to clean it. Make sure you write down exact locations of any wires you remove. This should fix the problem.
Jun 20, 2012 | Heating & Cooling
Yes I turned all switches off but the motor is still running, what should i do i cant afford a technician today
the thermostat operates a relay (usually in the outside unit) .. sounds like your relay has stuck contacts. you can trip the air conditioning circuit breakers to shut it down for now .. you can try tapping the relay with a screwdriver handle to see if you can break loose the contacts .. or better, you can replace the relay .. its also possible that the thermostat has a shorted contact .. disconnect (or unplug) the thermostat and see if the motor stops .. if it doesn't then suspect the outside relay .. if it does then replace the thermostat .. make sure the wiring to the stat is ok ..
Sep 26, 2010 | Heating & Cooling
I purchased a 60-Amp Cutler-Hammer Fusible Pullout Air Conditioner Disconnect to replace my older (over 20 years) one for my AC/Heating unit inside the house. Looking for a wiring diagram as I have 2-wires...
The two wires coming from the breaker box go to the terminals marked "LINE". The two wires going to your AC unit go to the terminals marked "LOAD".
Hope you find this to be very helpful. :-)
Mar 22, 2010 | Heating & Cooling
Installation manual required for teco split aircondtioner. Reverse cycle LS0909Y. I have operation manual but not sure how to install and wire up. Many thanks.
Is the unit an AC only or a heat pump?
Wiring to the units should in the manual or online.
Both units proper house voltage to inside unit and outside unit.There will also be a two wire low voltage cable between thr two.This is so the inside unit can turn on the higher current draw of the compressor in the outside condenser unit thru it's relay.If you have a heat pump there will also be a set of two wires to the 4 way gas valve in the condenser unit to change from heating to cooling mode,a set of two wires to control the on/off function of the fan in the condenser unit when it needs to defrost and mayby a two wire set to a themal sensor in the condenser to sense if it is frosting up when system is in heat mode.
Try to get a wiring diagram and if you can't get to the point where you understand how to wire the unit don't guess! Call someone who knows wiring or call a pro, he can you money over the cost of replacing parts if unit is miswired.
Oct 06, 2009 | Heating & Cooling
RUUD Central Air/Heat Pump
you may have lost your refrigerant and the unit is shut off on low pressure.
You can check the unit's charge by turning on the indoor fan and pushing the ourtdoor contactor down(the relay with heavy wires going in). With the unit runnig for a couple minuits does the large copper line coming into the outdoor unit from the indoor coil get cold to the touch?
If not you have lost your refrigerant
May 31, 2009 | Ruud UBHC Air Conditioner
Panasonic cs-pw9gke i need wiring diagram
Split A/C-Cold:
You need four wires(two #10 and two #12) to the outdoor unit, leaving you house, and three wires(#10) coming from the breaker to tye indoor unit inside your house.
Split A/C-Cold and Hot:
You need five wires(two #10 and three #12) to the outdoor unit, leaving your house, and thee wires(#10) coming from the breaker to your indoor unit inside your house.
This ypical arrangment(all of them use three wires fro the breaker), yet there are other units which may require 6-7 wires connected to the the outdoor unit depends on the added features to the unit.
Regards,
Gulftecheng
Dec 05, 2008 | GE Quiet-Aire Ductless Split System Air...
Outside fan motor with relay and two capacitors, one capicitor has three prongs and the other has two. need wiring diagram to help ensure hook up is right and also need to know how to test relay and caps...
are you looking to wire up the fan or rewire the whole outdoor unit? The fan capacitor is the one with two prongs and you should have two brown wires coming off the fan. One brown wire per terminal