Need to no if it runs on 115 or 230 and what size breaker
I need to no if the bryant 462ajc018ba or the bryant 462ajc021ba run on a 115 or 230 watts and what size breaker to use this is a window unit
  • 358 Answers
The power info tha you need should in the same tag wher you find the model nubber ,if not lok for another tag behind the front panneland if still is not there lok at the one on top of the compresor,if it less than 12000 BTU should be for 115 and a braker of 20 amps .
Posted on Apr 21, 2009
Will goodman outdoor ac work with bryant indoor unit
This is true as long as it is not a heat pump. Make sure they replace the piston (metering device to match the outdoor units required piston size. Or if the indoor coil is metered via TXV, it will automatically meter the refrigerant flow. If you are mismatching a system, make sure an acid test is performed on the old refrigerant and take appropriate measures with the new system if the test shows positive acid. They need to definitely install a liquid line drier.
Apr 12, 2013 | Bryant 462AJC021BA Air Conditioner
I have a new furnace and the breaker keeps tripping (20/30). It is a bryant westinghouse box. I think 200 amphes
1) You got a FIRE truck coming.
2) Wire is too small.
Problem is NOT circuit breaker.
3) Both 240Volt appliances on same breaker is a hazard, especially if space available in 200 amp service panel for more breakers.
4) Usually each 240V appliance has separate breaker.
5) Circuit breaker trips because of High heat on the wire.
If wire gets hot, it will start a fire inside the wall.
Electric code requires wire-size match breaker-size.
6) If you put larger amp breaker on same wire that is getting hot, then wire will get hotter.
Result: FIRE truck middle of night with folks jumping out window in glass-cut bare run across yard.
7) Each appliance has volts and watt rating on label.
EVERY appliance has label.
8) For example stove might be rated 8000 watts and 240Volt.
8000 watts divided by 240 volts = 33.3 amps
Stove would require 40 amp breaker and 8 gauge wire.
9) How to figure it out:
http://waterheatertimer.org/Color-codewire.html
http://waterheatertimer.org/How-to-install-a-subpanel.html
10) Do same calculation for new furnace.
12000 watt furnace divided by 240 volts = 50 amps.
Use 60 amp breaker and 6 gauge wire.
11) Summary: fixya wants you to be safe, and buy stuff showing in the ads.
Use a bigger breaker ONLY when bigger wire is also installed.
Call furnace installer, the installer should know to check safe wiring before installing.
Nov 04, 2012 | Bryant Westinghouse Bqc Quad Circuit...
Ac compressor runs, no blower fan. fan and capacitor ok. bryant
so the outside compressor and fan are working good ? If the fan and capacitor check out good then check that the wire from the thermostat for the fan (usually green and tied to grey on a bryant) has voltage and if it does the control board needs replaced because it contains the fan relay
Aug 19, 2010 | Bryant 462AJC021BA Air Conditioner
Fan wont turn t humms
Might need a little more information, but here goes. If the fan won't turn at all, you need to oil it, if you can spin the fan and then it slowly beguns to run ful speed, replace the run capacitor.
Jun 24, 2009 | Bryant 462AJC021BA Air Conditioner
Air conditioned not running
compressor problem that clicking is a relay for the compressor check your breaker.
Jun 21, 2009 | Bryant 462AJC021BA Air Conditioner
Bryant Legacy Air Conditioner doesn't blow out cold air
Unplug the unit with all controls off, then plug back in and wait 5 minutes before turning on switct at unit. Good luck
May 27, 2009 | Bryant 462AJC021BA Air Conditioner
Furnace is not working, digital thermostat does not register
sounds as if your low voltage transformer might have bit the bullet will need replacing all of the devices you mention are powered by this one low voltage t-stat
Dec 09, 2008 | Bryant 462AJC021BA Air Conditioner
Heating & Cooling Logo
41 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Donni Steen