Question about Goodman GMS90703BXA Heater
Goodman code problem three blinks
I have two newly installed (one month ago) 92% direct vent heating systems. I have turned on the thermostat for the first time after the hot summer and neither unit worked. My installer returned and bled the gas line and sucked on some hoses and determined that one unit has a blocked exhaust. he's returned during daylight and charging me to fix the blockage which is ok if it really a blockage --act of nature or God like leaves or a pest in the pipe---but now the other unit is also blinking 3 blinks and will not pump heat. what else could be wrong --ie an installation problem?
Re: goodman code problem three blinks
Same problem with 1 yr old Goodman. Checked entire exhaust and pressure switch. Inside fan, pressure switch hose clogged with crusty white gunk. Cleaned it & furnace fixed. I have no furnace repair experience, but love to "play MacGyver". Hopefully this could save someone a service call.
Posted on Nov 12, 2009
I just had the problem with my new Goodman Furnace. The diagnostic code was flashing three fast blinks. I thought I had a problem with my exhaust being clogged as just a few days prior in a windstorm I had my chimney cap blow off and I thought I had a pest or something blocking the exhaust. I got to looking around and the combustion/exhaust fan had an orange wire behind it. The fan can easily be turned by hand and I had noticed a rough sound when it spun. I soon found out that this orange wire that had been behind the outside of the fan had been cut and this wire apparently supplied some sort of signal or power to a pressure switch. (judging that the three blinks meant a pressure switch stuck open from the inside of the bottow panel) I spliced the wire back in with itself (with the power the ther furnace off) and the furnace immediatly fired up and worked fine. This is probably just an installation error that the furnace installer made, but I was able to fix the problem myself and I have no prior furnace maintenance experience. Just a possible thing to check.
Posted on Mar 07, 2008
  • 1,420 Answers
If you remove the access panel on the unit and flip the back toward you, you will notice the diagnostic error codes. 3 Blinks represent a problem with the combustion fan, pressure switch or a vent blockage. Here are some things you can do to test it. With a piece of electrical tape holding the door switch, the unit will attempt to start up if the thermostat is calling for heat. The ignition sequence will be that there will be a light blinking on the control board and the combustion/exhaust fan will start turning. Then if there are no restrictions in the venting or combustion chamber, a pressure switch will close allowing the ignition to turn on and get hot. You may notice a viewing port where an orange glow will be seen. After about 15 seconds, you should hear a click and notice the orange turned to blue. If the unit does not light up, you will need to make sure the combustion/exhaust fan is blowing out enough air. Go outside and see if there is a good flow of air coming out of the exhaust vent pipe (if you can get to it). If you are able to temporarily remove the fresh air inlet (supply air) to the furnace to test for a blockage in it, do so but always remember to reinstall it prior to using the furnace. Cycle the furnace again and see if it lights with the supply air vent off (not the exhaust vent). Restriction in intake vent? Now if you did not discover blockage, you may be looking at a weak pressure switch, bad igniter or even misadjusted gas pressure. All these should be covered under warranty from your installer if the furnace is new. Let me know what you found!
Posted on Sep 18, 2007
Where is the pressure switch and how can I clear the hoses to it??? I think this is my problem.
Posted on Nov 25, 2012
0 characters
3 Points
Just installed Mr Heater Big Max 45 btu. Ran for two hours then exhaust fan made a high pitched noise and shut off. I turned unit off via thermostat and now all I get is three blinking lights and no...
with the unit unplugged try to turn the fan blade. If its hard to turn than this is a problem. You can try to oil the fan if it is hard to turn.
Dec 30, 2011 | Heaters
I turn my thermostat to the HEAT position, I hear the Thermostat click and the Furnace begins to hum but no air comes out of the vents. Also if i turn the fan to the ON position air will come out of the...
need to go to furnace and watch it...if your hearing a hum the enducer draft motor may have should start first if there is no fault codes...reset unit by unplugging furnace or in some cases turning power switch off...turn thermostat on heat and watch unit ..the small enducer draft motor should start first the a ignitor glows and the should light...goodman units have a control board with a light on control board when it fails should flash a code and on the door or inside on lable should give you what that code is...hope this helps good luck
Jan 07, 2011 | Goodman GMS90703BXA Heater
I installed a new goodman unit this past spring. It seems to work ok to good in the day time but the tempature is warmer so we do not need as much heat. At night I know the thermostat is coming on. I...
Heating Mode (Goodman Service Manual)
· The furnace control checks for an open main limit (this
limit is normally closed). If the limit is open, the furnace
will remain inoperable until the limit is closed. During
an open limit the circulating air blower will be
energized. The status light will blink four (4) times.
· The room thermostat reacts to a demand for heat.
· The control will then check to insure that the vent
pressure switch is open. If, at this point, the vent
pressure switch is closed the control will blink two (2)
times and will remain inoperable until this situation is
· The venter blower is energized.· The vent pressure switch will close when it detects a
pressure in excess of its setting. If the pressure switch
fails to close the status light will flash three (3) times.
The sequence cannot continue until the pressure switch
· After a pre-purge of about ten (10) seconds the electronic
ignition device will be energized.
· After a slight delay the gas valve will open.
· The burners will ignite and the flame sensor will detect
the presence of flame. The ignition device will
deenergize. If the sensor does not detect the burner
flame, the gas valve will close and the ignition cycle
will be repeated for a total of three attempts. If, after
the third attempt, the presence of flame is not detected,
the furnace will go into a lockout condition for one (1)
hour. It will then repeat the ignition cycle. This one (1)
hour lockout and retry will occur indefinitely.
· Thirty (30) seconds after the main valve is energized
the circulating air blower will be activated.
· The furnace will remain in operation until the demand
for heat is satisfied.
· Once the demand is satisfied the venter will shut off,
and the circulating air blower will shut off after the field
selectable time off is attained.
· The furnace will remain dormant until the next demand
for heat.
Dec 03, 2010 | Goodman GMS80903BNA Heater
I have a Lennox elite series furnace. The vents are just blow out cold air, not heat. The theromstat is now working strange. I set the digital theromstat at 75 deg. and then place the thermostat on hold....
You did great! Yes you have a heating system error not a thermostat issue. The 2 blinking lights is an indication something is wrong. Now what you need to do is to remove one of the panels on the heating system and look for a wiring diagram pasted on the reverse. On this diagram there will be a diagnostic chart explaining where to start looking for an issue based on 2 blinks. Because each model is different, a 2 blink error code could indicate a bad pressure switch, plugged air filter or any other thing.
Mar 21, 2010 | Heaters
It will only cycle once and then it shuts off.. i have to turn off and then back on through the thermostat to get it it through another cycle , the system is three years old. i have tried two other...
Your furnace has a diagnostic light in the unit. Look for a small see-thru window either on the top panel or the bottom panel. Look for a blinking light. Record the number of blinks. Now remove the bottom panel and look at the wiring diagram. There will be a error code list explaining what the blinks represent. If you open the panel prior to looking thru the window, you will erase the code. Changing the thermostat is not the solution. Good Luck.
Sep 07, 2009 | Goodman GMS90703BXA Heater
Goodman GMS90904CXA Wont ignite, light blinks 3 times
Ok, you either have a inducer fan issue or a pressure switch issue or a plugged vent pipe. The inducer turns on to establish a draft for the exhaust. If it is not working you will get this error code. If the pressure switch does not sense pressure caused by the inducer, it will give this code. If either the intake pipe or exhaust pipe is blocked (even y just a little) it will give you the same error code. If the condensate hose or receptical is plugged, again it will give you this error code. Good Luck!
Oct 20, 2008 | Goodman GMS90703BXA Heater
Goodman HVAC Package Unit
Cycling the external switch on the GMS series will not help you. That switch is for A/C only. At the unit found inside the house, remove the front cover. If there is a door switch, tape it closed. Now if the thermostat is calling for heat, the unit will cycle as you mentioned. When the unit does not start, check for a blinking light on the circuit board. After three unsuccessful tries, the light will blink a code (2 blinks then a pause up to 9 blinks than a pause). Make a note of how many blinks you see. On the reverse side of the access panel you will find a diagnostic schematic. It should tell you a fault code corresponding with your blinking. This will give you a starting point where to look. If the codes are not found there, check inside your owner's manual. Or you can call Goodman at 713-861-250.
Get back to us with those codes and maybe we can help you further.