Air condition freezing up

I have a bryant ac that is freezing up.The filters are clean the evap is clean. It does not freeze consistently. Also it was pouring water over about 1 month ago. that has stopped and it is discharging outside. It is 110 during the day and about 90 at the ev ening. This happens every year- we have had it serviced and they find nothing wrong- any ideas

Posted by on

  • kentlong Jun 10, 2008

    Unit is freezing up. Had a tech. check the unit - all o.k. Worked fine for about 4 days, still the same issue. fan (blower) will not run during this. Is the fan shutting down and causing the freeze or does it shut down when it freezes. Since the serv. Tech gave it the O.K. what would be some solutions. Again inside filter clean and no obstructions.

×

Ad

2 Answers

  • Level 3:

    An expert who has achieved level 3 by getting 1000 points

    Superstar:

    An expert that got 20 achievements.

    All-Star:

    An expert that got 10 achievements.

    MVP:

    An expert that got 5 achievements.

  • Master
  • 1,420 Answers

Make sure the condensate drain is clean and clear of any debris. With the indoor unit off, Remove the inspection panel and pour a gallon mixture of 10% Bleach to Water solution in the drain pan. Do not overflow the pan but check to make sure there is flow to the outside or drain. Clean out the drain hose if you have to. A freezing coil is a sign of either not enough air going across it or not enough charge in the system. Check to make sure all of the return air vents as well as supply vents are in full open and unrestricted. If they are, you will need to have the charge checked. If this turns out good, have your technician install an anti-freeze kit. This kit will temporarly turn off the compressor unit for a short period when the sensor in the kit experiences a freezing condition. Then after a bit, it will turn on the compressor. It may not cool as much as it was, but it may get you thru. Good Luck!

Posted on Sep 14, 2007

Ad
  • Level 2:

    An expert who has achieved level 2 by getting 100 points

    MVP:

    An expert that got 5 achievements.

    Governor:

    An expert whose answer got voted for 20 times.

    Scholar:

    An expert who has written 20 answers of more than 400 characters.

  • Expert
  • 80 Answers

Have an HVAC tech recover the refrigerant from the unit an recyle it during the recovery. Remove any old filter dryers installed on the unit and replace with a new one! YES! Braze in new ones! Pull a triple vacume on this sytem down to 500 microns to insure all non-condensables are evacuated from the system. Weight the charge of refrigerant back in and set by superheat readings from the evaporator coil to the compressor! majic number is 40f evap outlet plus 12f to make it around 52-55 at the compressor inlet. Your problem has been restrictions in the refrigeration cycle either in capillary tube with orfice for metering device or a TXV getting cloged with ****! Hope this gets it solved for you!

Posted on Aug 22, 2010

Ad

1 Suggested Answer

6ya6ya
  • 2 Answers

SOURCE: I have freestanding Series 8 dishwasher. Lately during the filling cycle water hammer is occurring. How can this be resolved

Hi,
A 6ya expert can help you resolve that issue over the phone in a minute or two.
Best thing about this new service is that you are never placed on hold and get to talk to real repairmen in the US.
The service is completely free and covers almost anything you can think of (from cars to computers, handyman, and even drones).
click here to download the app (for users in the US for now) and get all the help you need.
Good luck!

Posted on Jan 02, 2017

Add Your Answer

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

1 Answer

I stored my FH50220 in my storage unit over the winter and now it will not spray water


If your storage unit got below freezing it may have frozen and damaged something. It's hard to drain all of the water from pumps, tubes, valves, heaters etc. inside a carpet cleaning machine. If a machine must be stored where it may freeze one way to keep it from freezing up is to pour automobile windshield washing solution into the fresh water tank and run it through the machine until it comes out all of the Jets and cleaning attachments. Remove the fresh water tank and continue to run the solution through the machine to flush the windshield cleaner out of the machine. Be sure to use a cleaner with the proper anti-freeze rating and run fresh water through the machine before using it to clean carpets.

Apr 01, 2016 | Hoover FH50220 Vacuum

2 Answers

The coils are freezing overnight


Dirty filter,undercharged, evap. coil plugged.These are some possibilities, also tstat may be set to low adjust to reasonable temp

Apr 01, 2015 | Heating & Cooling

1 Answer

Why is suction and discharge lines of Goodman WMC24-1A split ac system freezing up.?


Low on freon, dirty evap, dirty filter or maybe restricted at the metering device

Jul 20, 2014 | Goodman Heating & Cooling

1 Answer

Armana APN14K-E portable AC freezes up


Lack of air flow or a lack of refrigerant are the two primary reasons why coils freeze. Clean the filter and the coil, if frost continues it is likely low on refrigerant.

Jun 30, 2017 | Haier Amana Apn14ke-E 14 000 Btu Portable...

1 Answer

Freezing up on goodman air condition cple36-1


Hello, freezing up is either a airflow problem such as dirty filter, dirty evap coil, dirty blower wheel, wewk blower motor ot a low refrigerant charge.

Jul 24, 2012 | Heating & Cooling

1 Answer

Suction line and evaporator coil freezing up


Hello, a air conditioning unit will freeze from lack of airflow or low refrigerant charge. Check filters, make sure blower wheel is clean and running at full speed and that evaporator coil is clean. If that checks out good then you will need a technician to come out and attach guages to the unit to check the operatimg preesures, fimd the leak, amd recharge with refrigerant. Many times the ac will leak at the schreader valves.

Jul 12, 2012 | Carrier Heating & Cooling

1 Answer

Hoshizaki M# DCM-270BAH-OS runs for days then freezes up evap coil and stops water inlet to evap.


There is a thermostat probe sat on the front of the evaporator to tell the control board when to harvest. Check it is tight in it's holder. Check the condenser is absolutely clean and filters clear. You can adjust the thickness of the cube. set it on the thinnest setting and see if it harvests before freezing solid.

Jun 15, 2012 | Hoshizaki Freezer Commercial Ice Machines...

1 Answer

If i set the temp to low on my window air conditioner can it cause the unit to freeze up


Under some conditions, it could freeze up. High humidity levels can cause the coils to freeze. Not cleaning the air intake filter regularly, can also cause the coils to freeze. However, most window units can not be set below 65 degrees. But, in high humidity, it could freeze at that temp.

If you want to avoid the possibility of the coils freezing, operate a ceiling fan or other small fan as fast as comfortable. This keeps the cool air moving a generates a wind chill that fools your body into thinking it's cooler than it really is. Doing this will keep you from having to turn the AC way down and thus, save on energy cost.

I hope this has helped you and thanks for choosing FixYa.

Sep 08, 2011 | Heating & Cooling

1 Answer

My air conditioner cooling coils get frozen approx\.after 2 hrs of running i have showed it to the service boy they first serviced filled gas and even changed the fan motor. but still the problem...


Hello, the evap coil will freeze from either low airflow or low charge. I would clean the coils, check air filter and replace or clean if dirty. If you have a thermometer measure the air entering the ac and the air leaving the ac, the differance should be 15-20 degrees, measure this after cleaning the coils. If it still is below 15 degrees the unit is underchraged.

May 26, 2011 | LG Heat cool Window Air Conditioner

1 Answer

Intertherm ac with heater for clayton mobile homes. water is leaking on floor from ac unit in house. the outside drain is dripping good so it does not appear to be a clogged drain.


Sounds like you may have freezing coil. Clean your filters and the inside of your coils. Also blow out the drain (just in case). Many people pour a cup of bleach in the drain pain once a month to keep the slime from growing.

Jul 23, 2010 | Heating & Cooling

Not finding what you are looking for?
Heating & Cooling Logo

Related Topics:

2,135 people viewed this question

Ask a Question

Usually answered in minutes!

Top Heating & Cooling Experts

Paul Carew

Level 3 Expert

3238 Answers

Dan Webster
Dan Webster

Level 3 Expert

8220 Answers

Tim Whalen

Level 3 Expert

3074 Answers

Are you a Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...