Once temperature is reached the burner still trys to re lite causing the fan to run and won't shut off it is a trane furnace. we have changed the fan limit and cleaned the sensor. Sometimes the fan will run for 3 or 4 hours and drops the temp in the house causing the cycle to start all over again. We have chnaged the t-stat 2 times.
  • mbkingrea Apr 15, 2009
    thermostat on heater doesnt kick off when temperature is reached...what could cause this?
  • 34 Answers
Need a thermocouple it sounds like to me.
Posted on Apr 17, 2009
Furnace reaches temperature set then shuts down and restarts 8 times before final shutdown.
When you say the the furnace re-starts 8 times before shut down, what is cycling 8 times? just the indoor blower or is the main burner re-firing 8 times? If it's only the fan it sounds like the fan control.
Mar 07, 2018 | Coleman Heating & Cooling
Gas furnace short cycles 2 minutes or less. Multiple troubleshoot steps and replaced components - no help. Any advice?
I did not see that your indoor fan motor started. Near your indoor fan motor there is a temperature switch that is called the fan delay relay. On a temperature rise the relay shuts a contact that turns on the indoor fan motor. If the contact does not close the high temperature limit will shut the gas controls off like your getting. A fan delay relay also allows the fan to run a minute or so to carry away the remaining heat in the furnace and help cool the furnace down. The fan delay relay is normally mounted in a recessed area in the fire wall of the furnace plate. I have also seen them on the top of the furnace heat exchanger. Anyway, the fan delay relay will probably not be available on a sunday, so temporarily until parts are available, try turning the thermostat fan from auto to on and try the furnace again. By turning on the fan to on the high temp limit will not shut you down again.
I have had high temp limit change there trip points, but you said you bypassed it and did the same thing.
Another cause could be using the wrong type of air filter. The new pleated filters sold block to much air flow. If air mass flow rate drops the difference in temperatur go up and when the difference in temperature go up, it gets nearer the high limit and causes it to trip. All pleated filters drop normal air flow through ducts by at least 35%. To make your air duct system work properly use the what is called throw away filters which cost about 1/3 the cost of the pleated filter. Remember to either clean or change the throw away filter monthly to reduce dirt being drawn into your duct system.
Hope this helps.
Feb 13, 2015 | Heating & Cooling
I install 2 new honeywell non programmable thermostats. The temp never reaches the setting temp. Always 5 to 8 degrees off. I can not get the furnace to heat the home over 70 degrees. Even set at 80. Any...
If the furnace is cycling on and off and not reaching temp there is a problem in the control circuit. If the thermostat is not satisfied the furnace should be running without shutting off in which case the capacity of the furnace is inadequate because of size or problems reducing the capacity. This could be caused by an increase in home size, poor air flow (dirty filter, loose fan belts, fan running slow, obstructions in the duct), dirty heat exchanger or burner, reduced gas flow, over temperature switch bad causing the burner to shut off early, or a few more technical reasons. You may do well to call a technician to troubleshoot this problem.
Feb 09, 2015 | Heating & Cooling
Is it normal for my furnace to have burner cycle once or twice
That sounds normal. When the bonnet reaches a preset temperature the burner turns off then when it cools down a bit the burner turns back on. Clean filters etc will help to keep the burner on longer in a cycle.
Aug 24, 2014 | Heating & Cooling
Fan runs long after room reaches desired temp. heat goes off and fan continues to blow cold air, have a protech 520 thermostat
Is your 'Heater' you are talking about-- A furnace-- with a burner and a blower?
Either way-- We need to adjust a control that determines WHEN THE FAN RUNS--
Most furnaces have a section where the heated air collects, and there has to be a sensor in that chamber, that senses when that air is warm enough to circulate around--- and when the burner shuts off, the air in that area cools down, and the sensor should shut off the fan-
Can you find the Heated air area?-- and can you find a temperature control in that area?-- Can you adjust the control, so that it shuts off the fan when the air temp drops to 100- to 120 degrees F...
Tell us more about the type of furnace/heater we are workig with, so I can better help you-
Tell us more
Mack B
Jan 18, 2011 | Heating & Cooling
1994 trane furnace fan will not shut off xl 1200
Hello there:
please contact a certified trane dealer i think that you are having a thermostat problem they may be able to assist you on setting the thermostat the correct way . ok?
best regards
mike
Aug 15, 2009 | Heating & Cooling
Central heater will not heat up to set temp on thermostac
pressure port is plugged pull hose off draft motor and clean port with a paper clip