Question about Hayward H Series Induced Draft Abg 100,000 Heater
No spark to ignite propane gas. No power at purple wire at gas valve. All limits and switches checkout. Power to NEW (replaced) control module card. Good flow, gas and water. Ignighter new, blower clean and working . Should I keep buying parts or just trash it and replace complete heater..Ron in Pa.
4 Suggested Answers
  • 61 Answers
SOURCE: Hayward Spa Heater ignites for 2 seconds and shuts off.
Sounds like this is a flame sensor issue. It is not detecting the flame.
Posted on Apr 04, 2009
SOURCE: Hayward Spa Heater H100ID blower will not stay on.
I had a similar problem and it turned out to be the solder connections on the control module. The connector that is soldered to this board (comes from the gas valve) needed to be re-soldered.
Posted on Jun 14, 2009
thepool
  • 78 Answers
SOURCE: Hayward H250K gas pool heater error code
Low Flow errors are not necessarily real. They can be caused by improper adjustment or a defect of the pressure switch. Locate the pressure switch. Verify that the "switch" makes contact. Adjust the dial, reducing the distance the switch has to travel to engage. This will effectively lower the operating pressure required to operate. Keep adjusting until the unit stays on.
Posted on Apr 23, 2010
Single wire igniter that sparks the oven on but flame goes out after a few seconds. Does the igniter control gas valve?
Its the other way around the valve controls the igniter so to speak
GAS OVENS 1)The spark igniter tip is dirty (can clean it with either a little wire brush or a piece of fine sandpaper).
2) The Pilot flame is too low, and the tip of the igniter is not in the flame good enough. (the flame acts as a circuit when it touches the tip & completes the circuit).
3) The spark module is no good and needs to be replaced.(But 1 & 2 are your best bet).
spark module does not sense the flame when it's on. The spark igniter is also the flame sensor which provides feedback to the spark module.
Make sure the igniter is properly aligned with the burner lighting holes and it is clean. All lighting holes must be clean too. You can enlarge them using a drill bit one size bigger.
If it would not fix the problem, replace the bake burner and the igniter.
There is a small chance for the spark module itself to be bad as well.
ELECTRIC OVENS:
CHECK THE OVEN RELAY CONTROL BOARD Aclicking sound could be something wrong with a relay. Check for any loose connections around the main control board on your oven. The click you hear is a relay losing power and switching back on. If the clock resets then something is causing power interruptions to the board.
Mar 23, 2015 | Ovens
Power cuts out 5 minutes after oven is lit
Gas ovens / stovetop that use gas and not electricity. These work by igniting gas and use actual flame on the the stovetop.
Newest cook top styles, such as the induction or halogen cook tops combine the same style to produce more even heating. Some of these ovens feature thermal limiters or thermostats that regulate the burner system.
GAS OVENS
ELECTRIC OVENS:
The oven safety valve
(also called the gas valve) is the part that ensures that gas is not released until the igniter has reached the correct temperature needed to ignite the gas. While this part can fail, it is uncommon. If the hot surface igniter does not glow you should first verify that you have voltage to the circuit. This is a live voltage check and should be performed by a qualified person. If voltage is lost at the valve terminals then you should verify the continuity of the bi-metal in the valve using a multi-meter.
Mar 10, 2015 | Ovens
Kenmore gas range when no clicking when turning the oven on
Get FREE Standard Shipping on orders of $100 or more. Details
Range: Gas burner won't spark or ignite A surface burner igniter switch and a spark module activate the spark electrode when a burner is turned to the "Lite" position on a gas range's cooktop. If the surface burner switch, spark module or wiring in that circuit fails, the spark electrode won't work, and as a result the gas burner won't light. If those components work but the electrode won't spark, the problem could be that the spark electrode is coated with spilled food of is bent or broken. In addition, the electrode won't spark or ignite the burner properly if the ceramic insulation sleeve below the tip of the electrode is cracked or broken. If the gas burner isn't lighting, these repairs may help.
Range 101
See all articles These repairs may help solve your problem:
Replace the spark igniter electrode
1396454293470.jpg The spark igniter electrode-also called the surface burner igniter-is an insulated electrode that provides an ignition spark to light a surface gas burner. It sparks and makes a ticking sound when the burner switch is turned to the Lite position. Replace the spark ignition electrode if it fails to spark or if the ceramic insulation sleeve is cracked or chipped. How to Replace a Spark Igniter Electrode in a Gas Range Find This Part
Replace the surface spark module
1377098014986.jpg The surface spark module is in the ignition circuit for the gas surface burners. When a surface burner control knob is turned to the "Lite" position, it provides voltage to the spark electrodes on the gas surface burners. If the surface spark module fails to provide the electrodes with voltage, then it should be replaced. Find This Part
Replace the spark igniter switch
1396454315355.jpg The igniter switch is an electrical switch on the stem of the gas surface burner control valve. This switch completes a circuit to the surface burner spark module, causing the burner igniters to spark when the burner switch is turned to the Lite position. Replace the burner igniter switch if the burners don't spark when you turn the burner control knob to the Lite position or if igniters spark constantly even when the burner knobs are in the Off position.
May 27, 2014 | Kenmore 79012 / 79014 / 79019 Gas Kitchen...
My maytag mgr5729adw gas range oven omits a strong gas smell when attempting to preheat. Sometimes it heats sometimes it doesn't but use to get a small boom when igniting. Ignitor still glows oran
see the next steps and proceed with common sense: God bless you
Main Control / Oven Switch
The main control or oven switch may have failed. You will need to identify the wires from the switch/control that lead to the igniter that is clicking. These wires may pass through the spark module and change colors. Refer to the wiring diagram or tech sheet. If you have power leaving the switch/ control when in the off position replace the switch /control. Manual switches can be tested with an ohmeter.
Spark Module / Igniter Module
If your oven igniter keeps clicking the igniter module or spark module is the likely problem. First be sure the igniter is clean and the surrounding contact points are clean. Make sure power is off when cleaning. If the oven keeps clicking after it's cleaned and the oven switch / control checks good replace the spark module.
Jul 26, 2012 | Kitchen Ranges
The water heater red light keeps flashing rapidly on my Powervent 2 model 41VRP40N. It is not producing hot water and when I read the manual it says it needs more heat. What does this mean. How do I fix...
There are many things to check. The single most important test is for 24V at the gas valve after the ignitor is supposed tp be on. 19 V or less and there is either a bad ground or the ingition control board has failed. (Wire ground problems are a high probablilty)
Here is what the book says:
PROBLEM #1 - HOT SURFACE IGNITOR DOES NOT GLOW RED
(Remember to wait for purge time, 17/34 seconds, on models so equipped).
Possible causes
A. No main power
B. Faulty transformer
C. Faulty thermostat
D. Faulty limit switch
E. Faulty blower interlock switch
F. Faulty hot surface ignitor
G. Faulty ignition control
Solution
Step #1
Perform normal system checks of main power, transformer, thermostat, limit
switch, blower interlock switch, and replace faulty component.
Step #2
With power on and thermostat set at its highest position, check voltage
between "TH" and "TR" on HS780 ignition control. If 24 volts is not present
check output at transformer. If no, replace transformer. If transformer
checks out OK look at other controls in the 24 volt circuit I.E.: thermostat,
limit switch, blower interlock switch. Check for 120 volts between "neut"
(L2) and "120" (L1). Check for 120 volts at the ignitor across "IGN" and
"IGN" terminals on the HS780 ignition module. If 120 volts is present,
replace ignitor. If no, replace the 780 series module
PROBLEM #2 - IGNITOR GLOWS RED BUT MAIN BURNER
WOULDN'T LIGHT
Possible causes
A. Improper ignitor alignment
B. Faulty ignition control
C. Faulty gas valve
D. High inlet gas pressure
E. Polarity reversed
F. No earth ground
Solution
Step #1
Check for availability of gas at gas valve. Make sure the manual valve
upstream of the gas valve and the gas valve are in the full on position. Also
make sure gas is being supplied to the system at the proper pressure, too
high will lock-up the valve.
Step #2
Check proper polarity of "NEUT" and "120" on the ignition control by reversing
the wires, if reversed gas valve will not open. If this does not solve the
problem, replace wires as they were.
Step #3
Check for proper ignitor position.
Step #4
Check for a good earth ground by using a meter connected between L1
and furnace chassis. Should read 120 volts, if no, check and/or repair ignition
ground wire or ignition control mounting screws.
CAUTION POLARITY MUST BE OBSERVED
Step #5
Check for 24 volts at the gas valve terminals; "1" and "2" on a 7200 series,
"M" and "C" on a 7100 series, "TH" and "TR" on a 7000 series. If yes,
check wire integrity or change the gas valve. If no, change the 780 series
ignition module.
That is pretty much all of the troubleshooting required.
Thanks for choosing FixYa,
Kelly
Feb 14, 2011 | Rheem 40 Gallon FVR NATGAS Low WATER...
Vulcan convection oven model SG4d-1 will not ignite burners
Gas does not ignite. No spark. No Ignition light is not ON.
1. Shorted electrode on igniter/flame sense.
2. Igniter cable (high voltage) OPEN.
3. Heat relay malfunction.
4. Centrifugal switch in blower motor inoperative.
5. Transformer inoperative.
6. High limit thermostat open.
7. Interconnecting wiring malfunction.
8. Ignition module malfunction.
Sparks but gas does not ignite.
1. Gas solenoid valve off or inoperative.
2. Manual gas valve closed.
3. Gas supply OFF or insufficient gas pressure.
4. Inerconnecting wiring malfunction.
5. Igniton module malfunction.
Feb 23, 2010 | Vulcan Convection Oven - VC44EC-208-1
Turn Thermostat to call for heat (here click)from the t-stat calling. I do not here the multiple click (ignitor)and then the flow of gas. I have a Honeywell VR8204M electronic gas valve. I have votage...
Wiggle wires, it could be something as simple as a loos connection. If your getting power to valve and it's not opening your valve is bad. Also check your limits somethimes all limits are connected and one broken one will throw the system off.
Dec 01, 2008 | Honeywell Heating & Cooling
Goodman GMP075-3 ignition problem
OK, if the furnace is not lighting for even a few seconds, you have either a bad gas valve, bad wire, bad control module or no gas. The pressure switch is not the issue. Check all wires to the gas valve and look for 24 volts across them when the ignitor glows and you hear the click. Then test for 24 volts to ground. It could be a bad ground wire.
Sep 28, 2008 | Goodman GMS90703BXA Heater
Coleman furnace blower runs continuously
You should be seeing 120 volts to the igniter. Anything less requires either a replacement of the transformer, start relay or control module.
Dec 19, 2007 | Coleman Propane Forced Air Heater...
Hayward H Series Induced Draft Abg 100,000 Heater Logo
56 people viewed this question
Top Hayward Pool & Spa Experts
Jay Finke
Jay Finke
Bill Jordan
john h
Are you a Hayward Pool and Spa Expert? Answer questions, earn points and help others