Question about Kohler 20resa 20kw Home Emergency Backup Generator

1 Answer

GEN SET WILL NOT START /MAIN POWER OVERLOAD - Kohler 20resa 20kw Home Emergency Backup Generator

Posted by on

Ad

1 Answer

  • Level 1:

    An expert who has achieved level 1.

  • Contributor
  • 2 Answers

I have a Generator Kohler Res14 and its not crancking, and error of invald shutdown

Posted on Dec 18, 2013

×

Ad

1 Suggested Answer

6ya6ya
  • 2 Answers

SOURCE: I have freestanding Series 8 dishwasher. Lately during the filling cycle water hammer is occurring. How can this be resolved

Hi,
a 6ya expert can help you resolve that issue over the phone in a minute or two.
Best thing about this new service is that you are never placed on hold and get to talk to real repairmen in the US.
the service is completely free and covers almost anything you can think of.(from cars to computers, handyman, and even drones)
click here to download the app (for users in the US for now) and get all the help you need.
Goodluck!

Posted on Jan 02, 2017

Ad

Add Your Answer

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

1 Answer

Dometic AC B59516.711 15,000 BTU, while on generator power the AC works during day while it hot but once the sunsets and it cools down, compressor kicks on it drags the gen down and shuts it off.


something else besides the ac is stopping ( overloading) the genset
if it works well during the day, the compressor has to be working so the ac is not the problem
a 4000 watt gen set has a duty cycle load of around 3000 watts full time so any additional power requirement besides the ac will overload it
electric stoves , microwave ovens , hot water elements , anything that consumes power after dark will when combined with the ac will overload and shut down the gen-set

Jun 26, 2017 | Electrical Supplies

1 Answer

Onan diesel 8kw start by itself on off after a minute and start again 5 minutes later. is it a defective control box 2911442


if you have external utility power connected it could be the system controller that is faulty and trying to start the gen set which will come on line only to sense utility power and shut down
that action is shutting of the utility power and so the gen set starts again
if you are not connected to utility power, again it could be the controller that is faulty causing a problem
best have a electrician or gen set repair shop check it out

Nov 21, 2016 | Electrical Supplies

1 Answer

Using generator due to power outage plugged in coffee pot and no power coming from generator but generator still running . Briggs and Stratton G 1000M reset and nothing happening . OMGosh help


consider this
what is the wattage of the coffee pot and what is the wattage of the genset
if they are the same then the overload of the gen set has cut in
the gen set has to be at least twice any wattage of what is connected
other than that take it in for a proper diagnosis and quote

Sep 03, 2016 | Briggs Electrical Supplies

1 Answer

What connector is needed for a remote start?


talk with an accredited electrician as there will have to be a special relay/ breaker in the fuse board of the house
the problem is that your genset cannot be running when utility power comes back on as it will destroy the genset

the electrician can wire the board so that when utility power is available the gen set can be started but not connected to the house
when the utiltiy power fails the relay switches over to the gen set and allows it to start and power the house
when utiltiy power is restored the relay disconnects the gen set and reconnects to the utiltiy power supply
This is not a job for anyone except a fully qualified electrician

Oct 19, 2015 | Honda Generator Wireless Remote Starter...

1 Answer

How to clear a main power overload on a kohler gen


What is missing here is a couple of things, what size generator are we talking? a residential, commercial, what control is on the unit. They all reset in different ways. One sure way is disconnect the battery charger first (VERY IMPORTANT or control board can be damaged) disconnect the negative terminal off the battery. leave off for a minute they re conenct and re energize charger. Fault should clear unless you have done damage due to over load.

Mar 01, 2015 | Kohler Electrical Supplies

2 Answers

My power star w7 inverter charger wont charge off genset


there are things you would need to check
1, Does your inverter charge over any other power source?
if no, your inverter input power source has a problem
if yes , then
a, check the input voltage/frequency rating of your inverter then compare it to the output rating of your gen set
i believe there would be a difference between them
use a multimeter tester{ac}
inverters reject strange voltages or high voltage to protect itself from damage

May 29, 2014 | Electronics - Others

1 Answer

Have a SSR-EP100 air compressor that shows


Try to reset the main motor and fan motor over loads by pushing the reset on the overload it self, Then reset the controller. If the error resets, before starting. put a clamp on amp meter on to L1 or L3 motor lead which is located in the compressor electrical box . Then start and observe amps when unit is making air fully loaded. Once you know how many amps at full load the unit is pulling ,look at the overload setting on main motor overload and see if it is approxmately 10 amps above the max amps being pulled.If not set it about 10 amps above your max load amps.

Nov 26, 2011 | Ingersoll Rand Air Tools & Compressors

1 Answer

Start button doesn't work for all microwave functions--as well as timer--fuse is ok


Possible causes:

1. No power to outlet (overload or fault in microwave or other appliance).
2. Blown main fuse - likely due to other problems.
3. Open thermal protector or thermal fuse.
4. Defective controller or its power supply.
5. Clock needs to be set before other functions will operate (some models).

Dec 29, 2009 | GE Spacemaker JVM1640SJ Microwave Oven

1 Answer

I have a eu3000 overload safety shuts it down at about 1100 watts


Can you verify the amp draw on the output? This gen should handle 25 amps continuous. I wonder if you actually have a bit more that 9 amps? It would be nice to check the frequency and volts too...A Fluke multi-meter can read these values.

Jul 23, 2009 | Electrical Supplies

1 Answer

Honda eu 6500 gen overload indicator light will not shut off


Check the Ground Fault Indicator circuit breaker for triping, and look for the high limit on generator. Reset the main breaker by triping it full right and then back. Vitally

May 22, 2009 | Honda 6370C - Parallel Power Kit For ...

Not finding what you are looking for?
Kohler 20resa 20kw Home Emergency Backup Generator Logo

Related Topics:

578 people viewed this question

Ask a Question

Usually answered in minutes!

Top Kohler Electrical Supplies Experts

rjivaro

Level 2 Expert

153 Answers

John Trevino

Level 3 Expert

1388 Answers

Wayne McNeil

Level 2 Expert

168 Answers

Are you a Kohler Electrical Supply Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...