Question about Eaton Powerware 9130 UPS (700465461) UPS System
Powerware 9130 service manual - Eaton Powerware 9130 UPS (700465461) UPS System
Pawerware 9130 alarm 191
need to change batteries.
cannot hold charge
Nov 09, 2013 | Eaton Powerware 9130 UPS Battery
Alarm #191 open cell voltage powerware 9130
Remove the front panel plastic cover where the batteries are located, then plug the two connectors together, restart the UPS, and it should be fine.
Aug 13, 2013 | Powerware Series 9 9170 UPS System
Bc bus fault of 9120 2KVA
Suspect charger board failure. Replace with new model 9130. 9120 is obselete
Mar 21, 2013 | Powerware 9120 UPS System
Alarm error #191 comes from a battery test, where batteries are put under load for 25 seconds. (If the alarm is unexpected, you might have enabled the periodic 30-day battery test.)
#191 is test failure for battery internal resistance. So, need to locate and replace the bad battery, then run the battery test manually. If batteries are good, make sure no battery connector is corroded or loose.
Feb 04, 2013 | Powerware Series 9 9170 UPS System
Donde puedo conseguir el manual del equipo powerware pwi-9130 3000R
Try www.eaton.com/powerquality. Choose Mexico as your country and then 9130 rackmount as your prouduct. Documentacion tab.
Nov 27, 2010 | Powerware Eaton PW9130 3000VA Tower UPS ...
Short backup time
Suspect battery failure/faulty cell in a batt
Remove batts and check outside unit
charge up to around 2.27V/cell then check discharge on each batt (12V car lamp is good dummy load)
faulty one will be obvious.
MAKE SURE YOU ARE VERY CAREFUL WITH BATTERIES, THEY ARE VERY DANGEROUS, AND ALWAYS LIVE!
Check you manual for safety procedures, BEFORE working on Batteries.
hope this helps
thanks for using Fixya
Jul 06, 2010 | Powerware 9120 UPS System
I need qty:10 from ups poweware9120
The Powerware 9120 UPS has been replaced by the Eaton 9130 (www.eaton.com/powerquality). You may be able to get some 9120 models from www.powersupersite.com. Just do a search for 9120.
May 18, 2010 | Powerware 9120 UPS System
Eaton Powerware 9130 UPS (700465461) UPS System Logo
73 people viewed this question
Top Eaton Computers & Internet Experts
Lawrence Oravetz
Danny Kuhlmann
Are you an Eaton Computer and Internet Expert? Answer questions, earn points and help others